+ Reply to Thread
Results 1 to 10 of 10

Thread: Siemens TEC Point

  1. #1
    Join Date
    Aug 2008
    Posts
    1,104
    Post Likes

    Siemens TEC Point

    i have a hot water valve on a TEC that is set up invertly. 0% fully open, 100% fully closed. without physically switching wiring on controller can i change action via insight??

  2. #2
    Join Date
    Feb 2007
    Location
    Sacramento, CA
    Posts
    87
    Post Likes

    Depends on the TEC Application

    What application is the TEC using? Check the application point list. If you can change the action there will be a binary point to change the action. You should then be able to change the action from the Insight. You will need to back up the TEC to the panel and the panel to the Insight to make sure the changes are backed up and won't be reversed if the TEC loses power, this will cause a reload of the TEC point list in the panel.

  3. #3
    Join Date
    Aug 2008
    Posts
    1,104
    Post Likes
    Thread Starter
    app 2023. i think point 58 has something to do with this change. not sure.

  4. #4
    Join Date
    Mar 2008
    Location
    Indy
    Posts
    378
    Post Likes
    Quote Originally Posted by gazoo View Post
    app 2023. i think point 58 has something to do with this change. not sure.
    What is the current value for point 58? This will help me find the value you want.

  5. #5
    Join Date
    Aug 2008
    Posts
    1,104
    Post Likes
    Thread Starter
    5

  6. #6
    Join Date
    Feb 2007
    Location
    Sacramento, CA
    Posts
    87
    Post Likes

    Post Can't find my old CD's

    I can't find my old Insight CD's , I haven't worked for Siemens in a quite a while, but I was able to look up the application guide for VAV TEC's on the internet & point 58 is the point to change the action of the motors. Just remember it affects all 3 motors (VAV damper & both hot water valves). Unfortunately what I found on line didn't have the table for how the value works. Check your Insight CD's, I believe there should be a copy of all the application guides with the values for point 58 & how each value affects the motors.

  7. #7
    Join Date
    Nov 2006
    Location
    NW Florida
    Posts
    711
    Post Likes
    It has been a few years for me but I think the DO Direct should be a value of four to accomplish your goal.

    Don't hold my feet to the fire but I'm about 66% confident on this.

    Ken

  8. #8
    Join Date
    Nov 2006
    Location
    NW Florida
    Posts
    711
    Post Likes
    Thinking about this in the morning, I may have been thinking of the 2070 application, not the 2023.

    Don't want to steer you wrong if I can help it.

    Ken

  9. #9
    Join Date
    Feb 2006
    Location
    Float'N Vally, MS
    Posts
    3,521
    Post Likes
    You may have to do a wire reversal.
    Hope this helps....


    https://www.hqs.sbt.siemens.com/gip/...8412_us-en.pdf
    Life is too short, Behappy!
    TFMM

  10. #10
    Join Date
    Mar 2008
    Location
    Indy
    Posts
    378
    Post Likes
    Quote Originally Posted by gazoo View Post
    5
    5 equals motor 1 is enabled, motor 2 is enabled and motor 3 is not used.
    13 equals motor 1 is enabled, motor 2 is enabled and reversed, and motor 3 is not used.

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •