Results 1 to 6 of 6
-
09-10-2012, 03:40 AM #1
New Guest
- Join Date
- Sep 2012
- Posts
- 4
Mcquay AGS160CS27-ER10 oil filter and oil change
Hello everyone,
Can someone help me in obtaining information about replacing an oil filter and oil in this machine? It uses a screw compressor, and I cant seem to find any information on doing this repair work. Thank you very much in advance!!
-
09-10-2012, 03:51 AM #2
New Guest
- Join Date
- Sep 2012
- Posts
- 4
Forgot to add, the compressor model number is HSA179QY11YB
-
09-10-2012, 07:24 AM #3
This is a fairly in depth procedure and should be done by someone with the appropriate experience. You need to get your post count up to to 15 and apply for pro membership, that way we can assist you.
-
09-10-2012, 10:57 AM #4
New Guest
- Join Date
- Sep 2012
- Posts
- 4
Ok Ryan, will do.
-
10-19-2012, 04:49 PM #5
New Guest
- Join Date
- Oct 2012
- Location
- Israel
- Posts
- 4
oil filter access
If the comp is compact without external oil seperator the cover plate of the oil filter is
in the center of the upper side of the comp. near the oil seperator.
If the comp. is equiped with an external oil seperator than the cover plate is located
on the side of the comp. next to the inlet of the oil return hose from the oil seperator.
You can"t miss it. It has 6 screws on it, it's round about 4" in diameter.
The oil for r134a is any 68 synthetic. The volume is indicated on the nameplate of the chiller.
Cheers
-
02-23-2013, 01:20 PM #6
New Guest
- Join Date
- Sep 2008
- Location
- ARIZONA
- Posts
- 2
This unit has frame 3200 Compressors, internal oil sep. as you are facing the discharge end of comp its on the lower right side oppisite side as slide valve indicator 4-5" diam. you will need to pump comp down if suc shut off valve was installed as a option. if not pump comp and evap down to cond remove cover change filter. oil is a grade 68 but only use the brand that Mcquay supplies