Thread: BO AND AO

  1. #1
    Join Date
    Jan 2009
    Location
    Not in Iran
    Posts
    1,111

    BO AND AO

    What is the difference between binary outputs and analog outputs?
    Binary is on and off I am thinking,
    Analog outputs is the same but it is more like for a drive?
    I'm doing some reading and was wondering.
    Also binary and analog variables?
    Last edited by milkyway; 09-09-2012 at 11:14 PM. Reason: Adding
    no signature blast'em man blast'em
    !!!KILL THE TERRORIST!!!

  2. #2
    Join Date
    May 2002
    Location
    Baton Rouge, Louisiana
    Posts
    3,959
    binary is on/off
    analog-varies, usually a signal that modifies voltage or ma based on settings
    Quote Originally Posted by MatrixTransform View Post
    very soon it is you that will be pwned

  3. #3
    Join Date
    Jan 2008
    Location
    Near Philly
    Posts
    525
    Really? Please don't tell me you are actually billing somebody for your time.

  4. #4
    Join Date
    Jan 2009
    Location
    Not in Iran
    Posts
    1,111
    Quote Originally Posted by mechdorn View Post
    Really? Please don't tell me you are actually billing somebody for your time.
    Nope, just like my post said, doing some reading,. What makes u think I am billing for my time??
    Pay attention

  5. #5
    Join Date
    Aug 2012
    Location
    Silver Creek, Ny
    Posts
    94
    I was interviewing for a local DDC control company here in Buffalo, I didn't have any prior DDC experience but I am versed in HVAC and telecom so I gave it a try!
    so I found online a DDC tutorial site that pretty much gives a grass roots explaination of DDC and networks all the way up through BACnet and LON.

    Check it out...
    http://www.ddc-online.org/Digital-Co...l-Systems.html

    BTW...I didn't get the job
    Perfect Practice Makes Perfect

  6. #6
    Join Date
    Nov 2006
    Location
    Desert Southwest
    Posts
    719
    A commonly used analog output signal is 4-20 milli amps or 0-10VDC with the lower end of the signal being scaled as 0% and the upper end as 100% of the signal.
    A common use is a signal going to a variable frequency drive to an electric motor.
    If you can't fix it with JB Weld, Duct Tape, and Ty Wire it has to be replaced.
    No good deed goes unpunished.
    If you want to take off friday to go fishing then make sure you train your helper right.

  7. #7
    Join Date
    Aug 2006
    Location
    Ohio
    Posts
    2,090
    Binary Output (AKA: Digital) is simply on or off. Example: A control board telling a relay to turn on a fan motor.

    Analog output is a variable signal used as a control signal. Example: 0-10vdc from a control board used to tell a VFD how fast or slow to drive a motor. 0vdc = 0Hz, 5vdc = 30Hz, 10vdc = 60Hz, or anything in between.

    Now I want you to study up and give me examples of what a BINARY INPUT and a ANALOG INPUT could be used for.

  8. #8
    Join Date
    Sep 2012
    Location
    Central Florida
    Posts
    892
    Quote Originally Posted by zw17 View Post
    Binary Output (AKA: Digital) is simply on or off. Example: A control board telling a relay to turn on a fan motor.

    Analog output is a variable signal used as a control signal. Example: 0-10vdc from a control board used to tell a VFD how fast or slow to drive a motor. 0vdc = 0Hz, 5vdc = 30Hz, 10vdc = 60Hz, or anything in between.

    Now I want you to study up and give me examples of what a BINARY INPUT and a ANALOG INPUT could be used for.

    Can anyone answer??

  9. #9
    Join Date
    Mar 2003
    Posts
    7,326
    Binary input typically used for status. typical bo's include airflow switch, safety devices, relay aux contacts. fan proof=binary input closed, ie airflow switch closed.

    analog input is a control variable, could be an output off of a tempereature sensor, humidity snesor, airflow station, and other controls that give a variable response. example--an airflow station on an air handler delivering a 4-20ma output based upon differential pressure across the fan inlet cone.

  10. #10
    Join Date
    Aug 2006
    Location
    Ohio
    Posts
    2,090
    Flange!!!!

    I wanted him to answer so he could learn something ya dolt!

  11. #11
    Join Date
    Sep 2012
    Location
    Central Florida
    Posts
    892
    Quote Originally Posted by zw17 View Post
    Flange!!!!

    I wanted him to answer so he could learn something ya dolt!

    Which is why I asked before starting to list stuff.

  12. #12
    Join Date
    Mar 2003
    Posts
    7,326
    ooppsie, thought we were doing training. my bad for sure.

  13. #13
    Join Date
    Mar 2003
    Posts
    7,326
    ok, well he still needs to learn some things. how do you deal with having a 2-10 volt sensor, but need a 4-20ma input??

Page 1 of 3 123 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event