    Should reversing valve cycle every time a/c turns off?

    Hey folks, new to the site. I had my a/c unit replaced under a home warranty when I bought my house years ago and the original Carrier unit (a/c only) was replaced with a Goodman split system heat pump unit. It's never been wired to use for heat, just for a/c, and every time the outdoor unit shuts off after a cooling cycle there is a loud "whoosh" as the reversing valve is de-energized. Is that normal? I'm including a link to a mp3 I just made of it shutting off. Thanks!

    Ron

    Reversing valve audio

  2. #2
    Join Date
    Apr 2006
    Location
    Barrie Ontario
    Posts
    318
    Post Likes
    Depends on equipment and I don't install goodman but not uncommon for a manufacture to set it up to energize the valve for cooling.

  3. #3
    Join Date
    Dec 2005
    Posts
    2,032
    Post Likes
    Quote Originally Posted by Cincy_Ron View Post
    Hey folks, new to the site. I had my a/c unit replaced under a home warranty when I bought my house years ago and the original Carrier unit (a/c only) was replaced with a Goodman split system heat pump unit. It's never been wired to use for heat, just for a/c, and every time the outdoor unit shuts off after a cooling cycle there is a loud "whoosh" as the reversing valve is de-energized. Is that normal? I'm including a link to a mp3 I just made of it shutting off. Thanks!

    Ron

    Reversing valve audio
    NO.
    Unless, it is poorly installed.

  4. #4
    Join Date
    Jul 2005
    Posts
    7,834
    Post Likes
    Quote Originally Posted by Cincy_Ron View Post
    Hey folks, new to the site. I had my a/c unit replaced under a home warranty when I bought my house years ago and the original Carrier unit (a/c only) was replaced with a Goodman split system heat pump unit. It's never been wired to use for heat, just for a/c, and every time the outdoor unit shuts off after a cooling cycle there is a loud "whoosh" as the reversing valve is de-energized. Is that normal? I'm including a link to a mp3 I just made of it shutting off. Thanks!

    Ron

    Reversing valve audio
    Have an HVAC contractor come out and run continous power to the RV. Sounds like they used a two-wire connection and have the contactor and RV wired in parallel.

  5. #5
    Join Date
    Jul 2006
    Location
    Prata di Pordenone Italy
    Posts
    8,069
    Post Likes
    That is the problem with home warranty you never get the good work .do you have a gas furnace or electric heat

  6. #6
    Join Date
    Sep 2012
    Posts
    6
    Post Likes
    Thread Starter
    Thanks for the replies guys, I appreciate it. Yeah, it seems to me like whenever the thermostat is on auto/fan AND cool the reversing valve solenoid should be energized then. It might have been a case of not enough wires running out to the unit since the original wasn't a heat pump.

    Catmanacman, I have a Carrier Weathermaker SX gas furnace that I use for heat. If I remember right it's around 90% efficient.

    Having said that, I have another question. I live in the Northern KY area just across the river from Cincinnati. Would it be worthwhile to have a new thermostat, outside sensor, etc. installed and use the Goodman in heat pump mode for heat? Would I see any noticeable savings on my bill?

    I just installed new high efficiency windows and I'm adding an extra R-30 of insulation to the attic, so I'm kind of looking for anything else I can do to save energy. If it helps, I pulled up my bill from last Feb and I paid $1.01 per CCF for gas, and 8.75 cents per kilowatt hour for electricity.

  7. #7
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    It can save about 2 bucks per 1,000,000 BTUs of delivered heat at outdoor temps where its COP is 3. Break even is at about a COP of 2.5

  8. #8
    Join Date
    Jun 2001
    Location
    Moore, Oklahoma, United States
    Posts
    4,648
    Post Likes
    If somebody "hacked in" a heat pump I have to question the rest of the installation. In particular the choice of indoor coil.

  9. #9
    Join Date
    Sep 2012
    Posts
    6
    Post Likes
    Thread Starter
    54regcab, the evaporator coil is the matching unit to the compressor unit outside. They were both replaced under a home warranty when I bought my house and the combo is what was supplied to the installer by the insurance company. The install was nicely done appearance wise, it doesn't look "hacked in" as you put it. It wasn't replacing a heat pump, or installed as a heat pump, and I think hvacrmedic nailed it. The contactor and reversing valve solenoid are wired in parallel. Yeah, it should have been done right during the install and the extra wires run out to the unit. Should be an easy fix. I'm having a guy come out this week that my brother and I used on a house rehab a couple of years ago to take care of it.

  10. #10
    Join Date
    Jun 2001
    Location
    Moore, Oklahoma, United States
    Posts
    4,648
    Post Likes
    Not sure why they would have installed the heat pump and matching coil when a less costly straight A/C would have done the job. it must have been what they had in stock, glad to hear the job at least looks professionally installed. Since you already have the heat pump, might as well make it functional.

  11. #11
    Join Date
    Jul 2006
    Location
    Prata di Pordenone Italy
    Posts
    8,069
    Post Likes
    If you use a honeywell iaq thermostat you will need only 3 wires from the stat to the furnace then you will only need to run a new wire from the furnace to the outdoor unit and a seperate wire from the furnace to the outdoor sensor

  12. #12
    Join Date
    Sep 2012
    Posts
    6
    Post Likes
    Thread Starter
    Quote Originally Posted by 54regcab View Post
    Not sure why they would have installed the heat pump and matching coil when a less costly straight A/C would have done the job. it must have been what they had in stock, glad to hear the job at least looks professionally installed. Since you already have the heat pump, might as well make it functional.
    Yeah, I'm pretty sure it was all they had in stock at the time and if I remember right I was being a little vocal to the home warranty folks about how long the whole thing was taking. ;-)

    I think I am going to invest in the right thermostat and outdoor sensor and give the heat pump option a try.

  13. #13
    Join Date
    Sep 2012
    Posts
    6
    Post Likes
    Thread Starter
    Quote Originally Posted by catmanacman View Post
    If you use a honeywell iaq thermostat you will need only 3 wires from the stat to the furnace then you will only need to run a new wire from the furnace to the outdoor unit and a seperate wire from the furnace to the outdoor sensor
    That's a sharp looking thermostat catman, but yikes! I can feel my wallet tingling.

    Edit - The Prestige IAQ 2.0 System that is. I see there are less expensive options

  14. #14
    Join Date
    Apr 2010
    Location
    NC Sandhills
    Posts
    468
    Post Likes
    A goodman defaults to heat on RV. Sounds like they tied the 24v to RV with 24v to Contactor/compressor and when the cooling call ends the RV defaults/changes over to heat. Have them come back and wire it so it is always energized. Did you request a Heatpump for future dual fuel or going away from gas. I think it gives you better options down the road depending on your location.

  15. #15
    Join Date
    Mar 2009
    Location
    Mount Holly, NC
    Posts
    9,064
    Post Likes
    I was taught that reversing valve problems arise when they sit in a single position for extended periods, so the energize to cool option was enacted so during the summer the valve would switch often, preventing any oil or sediment from accumulating in the valve blocking changeover.
    in heat mode, each time the defrost cycle is called for, it reverses, so the only issue is in summer when the thermostat will stay in cool mode for months straight.
    I vote that it is ok for it to switch to heat between cycles.
    The TRUE highest cost system is the system not installed properly...

    Find a HVAC-Talk Contractor by clicking here

    Click below to BECOME a pro member
    https://hvac-talk.com/vbb/forumdispl...ip-Information

    Do you go to a boat repairman with a sinking boat, and tell him to put in a bigger motor when he tells you to fix the holes?

    I am yourmrfixit

  16. #16
    Join Date
    Jul 2006
    Location
    Prata di Pordenone Italy
    Posts
    8,069
    Post Likes
    Quote Originally Posted by Cincy_Ron View Post
    That's a sharp looking thermostat catman, but yikes! I can feel my wallet tingling.

    Edit - The Prestige IAQ 2.0 System that is. I see there are less expensive options
    In some cases its cheaper to get the iaq thermstat than it is to fish a new wire
    From the thermostsat to the furnace.

  17. #17
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Quote Originally Posted by vstech View Post
    I was taught that reversing valve problems arise when they sit in a single position for extended periods, so the energize to cool option was enacted so during the summer the valve would switch often, preventing any oil or sediment from accumulating in the valve blocking changeover.
    in heat mode, each time the defrost cycle is called for, it reverses, so the only issue is in summer when the thermostat will stay in cool mode for months straight.
    I vote that it is ok for it to switch to heat between cycles.
    Rheem energizes the RV in heat mode. So all summer long it stays in the cool mode and never switches until heating season.

  18. #18
    Join Date
    Mar 2009
    Location
    Mount Holly, NC
    Posts
    9,064
    Post Likes
    yup. GE units used to be energized to heat also, but in the 80's when heil and Janitrol had training classes, this was the reason they gave for why they chose to energize in cooling.
    also, many thermostats energize the cooling mode the entire time the tstat is set to cool, not each time the stat calls.
    The TRUE highest cost system is the system not installed properly...

    Find a HVAC-Talk Contractor by clicking here

    Click below to BECOME a pro member
    https://hvac-talk.com/vbb/forumdispl...ip-Information

    Do you go to a boat repairman with a sinking boat, and tell him to put in a bigger motor when he tells you to fix the holes?

    I am yourmrfixit

  19. #19
    Join Date
    Sep 2012
    Posts
    6
    Post Likes
    Thread Starter
    Quote Originally Posted by vstech View Post
    I was taught that reversing valve problems arise when they sit in a single position for extended periods, so the energize to cool option was enacted so during the summer the valve would switch often, preventing any oil or sediment from accumulating in the valve blocking changeover.
    in heat mode, each time the defrost cycle is called for, it reverses, so the only issue is in summer when the thermostat will stay in cool mode for months straight.
    I vote that it is ok for it to switch to heat between cycles.
    Good point. I'm not in the trade but I'd think with the newer programmable thermostats they could be set to cycle the RV every X number of cycles/days.

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •