Page 2 of 2 FirstFirst 12
Results 14 to 19 of 19
  1. #14
    Join Date
    Apr 2010
    Location
    NC Sandhills
    Posts
    468
    Post Likes
    A goodman defaults to heat on RV. Sounds like they tied the 24v to RV with 24v to Contactor/compressor and when the cooling call ends the RV defaults/changes over to heat. Have them come back and wire it so it is always energized. Did you request a Heatpump for future dual fuel or going away from gas. I think it gives you better options down the road depending on your location.

  2. #15
    Join Date
    Mar 2009
    Location
    Mount Holly, NC
    Posts
    6,964
    Post Likes
    I was taught that reversing valve problems arise when they sit in a single position for extended periods, so the energize to cool option was enacted so during the summer the valve would switch often, preventing any oil or sediment from accumulating in the valve blocking changeover.
    in heat mode, each time the defrost cycle is called for, it reverses, so the only issue is in summer when the thermostat will stay in cool mode for months straight.
    I vote that it is ok for it to switch to heat between cycles.
    The TRUE highest cost system is the system not installed properly...

    Find a HVAC-Talk Contractor by clicking here

    Do you go to a boat repairman with a sinking boat, and tell him to put in a bigger motor when he tells you to fix the holes?

    I am yourmrfixit

  3. #16
    Join Date
    Jul 2006
    Location
    Virginia
    Posts
    7,065
    Post Likes
    Quote Originally Posted by Cincy_Ron View Post
    That's a sharp looking thermostat catman, but yikes! I can feel my wallet tingling.

    Edit - The Prestige IAQ 2.0 System that is. I see there are less expensive options
    In some cases its cheaper to get the iaq thermstat than it is to fish a new wire
    From the thermostsat to the furnace.
    Go Trump

  4. #17
    Join Date
    Jan 2004
    Location
    PA
    Posts
    74,872
    Post Likes
    Quote Originally Posted by vstech View Post
    I was taught that reversing valve problems arise when they sit in a single position for extended periods, so the energize to cool option was enacted so during the summer the valve would switch often, preventing any oil or sediment from accumulating in the valve blocking changeover.
    in heat mode, each time the defrost cycle is called for, it reverses, so the only issue is in summer when the thermostat will stay in cool mode for months straight.
    I vote that it is ok for it to switch to heat between cycles.
    Rheem energizes the RV in heat mode. So all summer long it stays in the cool mode and never switches until heating season.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  5. #18
    Join Date
    Mar 2009
    Location
    Mount Holly, NC
    Posts
    6,964
    Post Likes
    yup. GE units used to be energized to heat also, but in the 80's when heil and Janitrol had training classes, this was the reason they gave for why they chose to energize in cooling.
    also, many thermostats energize the cooling mode the entire time the tstat is set to cool, not each time the stat calls.
    The TRUE highest cost system is the system not installed properly...

    Find a HVAC-Talk Contractor by clicking here

    Do you go to a boat repairman with a sinking boat, and tell him to put in a bigger motor when he tells you to fix the holes?

    I am yourmrfixit

  6. #19
    Join Date
    Sep 2012
    Posts
    6
    Post Likes
    Thread Starter
    Quote Originally Posted by vstech View Post
    I was taught that reversing valve problems arise when they sit in a single position for extended periods, so the energize to cool option was enacted so during the summer the valve would switch often, preventing any oil or sediment from accumulating in the valve blocking changeover.
    in heat mode, each time the defrost cycle is called for, it reverses, so the only issue is in summer when the thermostat will stay in cool mode for months straight.
    I vote that it is ok for it to switch to heat between cycles.
    Good point. I'm not in the trade but I'd think with the newer programmable thermostats they could be set to cycle the RV every X number of cycles/days.

Page 2 of 2 FirstFirst 12

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.