    Should reversing valve cycle every time a/c turns off?

    Hey folks, new to the site. I had my a/c unit replaced under a home warranty when I bought my house years ago and the original Carrier unit (a/c only) was replaced with a Goodman split system heat pump unit. It's never been wired to use for heat, just for a/c, and every time the outdoor unit shuts off after a cooling cycle there is a loud "whoosh" as the reversing valve is de-energized. Is that normal? I'm including a link to a mp3 I just made of it shutting off. Thanks!

    Ron

    Reversing valve audio

  2. #2
    Join Date
    Apr 2006
    Location
    Barrie Ontario
    Posts
    318
    Depends on equipment and I don't install goodman but not uncommon for a manufacture to set it up to energize the valve for cooling.

  3. #3
    Join Date
    Dec 2005
    Posts
    1,913
    Quote Originally Posted by Cincy_Ron View Post
    Hey folks, new to the site. I had my a/c unit replaced under a home warranty when I bought my house years ago and the original Carrier unit (a/c only) was replaced with a Goodman split system heat pump unit. It's never been wired to use for heat, just for a/c, and every time the outdoor unit shuts off after a cooling cycle there is a loud "whoosh" as the reversing valve is de-energized. Is that normal? I'm including a link to a mp3 I just made of it shutting off. Thanks!

    Ron

    Reversing valve audio
    NO.
    Unless, it is poorly installed.

  4. #4
    Join Date
    Jul 2005
    Posts
    5,491
    Quote Originally Posted by Cincy_Ron View Post
    Hey folks, new to the site. I had my a/c unit replaced under a home warranty when I bought my house years ago and the original Carrier unit (a/c only) was replaced with a Goodman split system heat pump unit. It's never been wired to use for heat, just for a/c, and every time the outdoor unit shuts off after a cooling cycle there is a loud "whoosh" as the reversing valve is de-energized. Is that normal? I'm including a link to a mp3 I just made of it shutting off. Thanks!

    Ron

    Reversing valve audio
    Have an HVAC contractor come out and run continous power to the RV. Sounds like they used a two-wire connection and have the contactor and RV wired in parallel.

  5. #5
    Join Date
    Jul 2006
    Location
    Virginia
    Posts
    4,619
    That is the problem with home warranty you never get the good work .do you have a gas furnace or electric heat
    We really need change now

  6. #6
    Thanks for the replies guys, I appreciate it. Yeah, it seems to me like whenever the thermostat is on auto/fan AND cool the reversing valve solenoid should be energized then. It might have been a case of not enough wires running out to the unit since the original wasn't a heat pump.

    Catmanacman, I have a Carrier Weathermaker SX gas furnace that I use for heat. If I remember right it's around 90% efficient.

    Having said that, I have another question. I live in the Northern KY area just across the river from Cincinnati. Would it be worthwhile to have a new thermostat, outside sensor, etc. installed and use the Goodman in heat pump mode for heat? Would I see any noticeable savings on my bill?

    I just installed new high efficiency windows and I'm adding an extra R-30 of insulation to the attic, so I'm kind of looking for anything else I can do to save energy. If it helps, I pulled up my bill from last Feb and I paid $1.01 per CCF for gas, and 8.75 cents per kilowatt hour for electricity.

  7. #7
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    67,880
    It can save about 2 bucks per 1,000,000 BTUs of delivered heat at outdoor temps where its COP is 3. Break even is at about a COP of 2.5
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  8. #8
    Join Date
    Jun 2001
    Location
    Moore, Oklahoma, United States
    Posts
    4,190
    If somebody "hacked in" a heat pump I have to question the rest of the installation. In particular the choice of indoor coil.

  9. #9
    54regcab, the evaporator coil is the matching unit to the compressor unit outside. They were both replaced under a home warranty when I bought my house and the combo is what was supplied to the installer by the insurance company. The install was nicely done appearance wise, it doesn't look "hacked in" as you put it. It wasn't replacing a heat pump, or installed as a heat pump, and I think hvacrmedic nailed it. The contactor and reversing valve solenoid are wired in parallel. Yeah, it should have been done right during the install and the extra wires run out to the unit. Should be an easy fix. I'm having a guy come out this week that my brother and I used on a house rehab a couple of years ago to take care of it.

  10. #10
    Join Date
    Jun 2001
    Location
    Moore, Oklahoma, United States
    Posts
    4,190
    Not sure why they would have installed the heat pump and matching coil when a less costly straight A/C would have done the job. it must have been what they had in stock, glad to hear the job at least looks professionally installed. Since you already have the heat pump, might as well make it functional.

  11. #11
    Join Date
    Jul 2006
    Location
    Virginia
    Posts
    4,619
    If you use a honeywell iaq thermostat you will need only 3 wires from the stat to the furnace then you will only need to run a new wire from the furnace to the outdoor unit and a seperate wire from the furnace to the outdoor sensor
    We really need change now

  12. #12
    Quote Originally Posted by 54regcab View Post
    Not sure why they would have installed the heat pump and matching coil when a less costly straight A/C would have done the job. it must have been what they had in stock, glad to hear the job at least looks professionally installed. Since you already have the heat pump, might as well make it functional.
    Yeah, I'm pretty sure it was all they had in stock at the time and if I remember right I was being a little vocal to the home warranty folks about how long the whole thing was taking. ;-)

    I think I am going to invest in the right thermostat and outdoor sensor and give the heat pump option a try.

  13. #13
    Quote Originally Posted by catmanacman View Post
    If you use a honeywell iaq thermostat you will need only 3 wires from the stat to the furnace then you will only need to run a new wire from the furnace to the outdoor unit and a seperate wire from the furnace to the outdoor sensor
    That's a sharp looking thermostat catman, but yikes! I can feel my wallet tingling.

    Edit - The Prestige IAQ 2.0 System that is. I see there are less expensive options

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event