    York YK Centrifugal Chiller

    We have 3 YK series york chillers R134a cooling capacity 1500 Tons.One of the chiller is surging too much condenser Sub cooling is around 10 Deg F.Its motor is 3.3Kv,Ampares are are fluctuating between 70 to 95.Any body can tell what is possible cause.Thanks.

  2. #2
    Join Date
    Sep 2007
    Location
    Somewhere in the world.
    Posts
    1,643
    Post Likes
    Post all the operating data for the Chiller without it we would all be guessing as to the cause !
    A mind is like a parachute. It doesn't work if it is not open.

    The best part of going to work is coming back home at the end of the day.

    Hard work spotlights the character of people: some turn up their sleeves, some turn up their noses, and some don't turn up at all.

  3. #3
    Join Date
    May 2007
    Posts
    202
    Post Likes
    will you tell me what Data points you required.Thanks.

  4. #4
    Join Date
    Jan 2011
    Posts
    1,396
    Post Likes
    All the data you would normally take during an operating inspection. Entering and leaving CHW temps, same for condenser, evaporator pressure, discharge pressure, saturated suction, saturated condenser, discharge temp, liquid level in the condenser...you get the idea.

  5. #5
    Join Date
    Sep 2007
    Location
    Somewhere in the world.
    Posts
    1,643
    Post Likes
    Name:  printers.jpg
Views: 382
Size:  28.4 KBName:  printer set up.jpg
Views: 343
Size:  39.5 KBName:  printer set up a.jpg
Views: 318
Size:  39.8 KBName:  printer set up b.jpg
Views: 327
Size:  35.6 KBName:  printer set up c.jpg
Views: 333
Size:  30.5 KBName:  York Sales Order.jpg
Views: 452
Size:  41.2 KBName:  History.jpg
Views: 371
Size:  35.7 KB
    A mind is like a parachute. It doesn't work if it is not open.

    The best part of going to work is coming back home at the end of the day.

    Hard work spotlights the character of people: some turn up their sleeves, some turn up their noses, and some don't turn up at all.

  6. #6
    Join Date
    Aug 2003
    Location
    Fort Worth, TX
    Posts
    11,444
    Post Likes
    What chiller surging basically is: when there is too high of a pressure difference between the condenser and the evaporator for the non-positive displacement compressor to overcome. As a result, gas flow reverses across the impeller wheel, attempting to stall it. This happens in spurts and is why amp draw fluctuates wildly during surging events...the impeller is working against gas flowing in the wrong direction.

    Basic causes:

    Fouled cooling tower

    Fouled tower sump and/or condenser pump strainers

    Fouled condenser tubes

    Failure to lower entering condenser water supply setpoint when chiller load is low

    Charge not trimmed correctly
    Building Physics Rule #1: Hot flows to cold.


    Building Physics Rule #2:
    Higher air pressure moves toward lower air pressure


    Building Physics Rule #3:
    Higher moisture concentration moves toward lower moisture concentration.