Results 1 to 10 of 10
  1. #1
    Join Date
    Sep 2012
    Posts
    373
    Post Likes

    Basement HVAC system not heating one of the rooms very well- what to do?

    Hello. I am a new member here.

    I live in a 5700 sq ft home (including the basement which is about 2200 sq ft) right outside of Atlanta, Georgia. The house has three HVAC systems - one for each floor. A 2 ton system serves the upstairs which is about 1400 sq ft, a 3.5 ton for the main level which is about 2200 sq ft, and a 1.5 ton for the finished basement. The main level and upstairs systems are fine, nothing wrong with them. One of the rooms in the basement never gets warm in the winter, and that's the game room where my teenagers are hanging out in all the time. The basement system is a Trane XR11 heat pump which was installed back in late 2003. Three of the rooms in the basement have 7 foot ceilings and the main theater room has an 8 inch supply duct going in to it from the air handler. There's only two returns in the whole basement, one 10 inch return in the theater room, and one 6 inch return in the man cave. The thermostat is located in the theater room. The man cave has a 6 inch supply going into there. There's also an unfinished workshop which has a 6 inch supply and also an unfinished bathroom that has a 4 inch supply. Both of those rooms will be finished in the future. One finished storage room has a 6 inch supply. There's a 6 inch supply going in to the game room. Air flow is very week in there, and my teenagers are always complaining that it is cold in there all the time in the winter when the heat's on. The other rooms get OK heating in them.

    My question is, what can help the game room get good heating? What changes can happen in the future to improve the heating in there? What would you recommend? Sorry about the long post.

    Thanks.
    Susan

  2. #2
    Join Date
    Jan 2004
    Location
    PA
    Posts
    73,800
    Post Likes
    A return added to the game room, and probably another supply.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  3. #3
    Join Date
    Sep 2012
    Posts
    373
    Post Likes
    Thread Starter
    Thanks. I agree that a return should be added. We are thinking about having the system replaced next year, so when that happens I will have the HVAC company check that out. Would you think that the system for the basement is undersized? I would think not because basements don't need much heat or cool.

  4. #4
    Join Date
    Sep 2012
    Posts
    373
    Post Likes
    Thread Starter
    Here's what the register in the game room looks like. (if this helps)
    Attached Images Attached Images   

  5. #5
    Join Date
    Jan 2004
    Location
    PA
    Posts
    73,800
    Post Likes
    Just sounds like not enough return. Typical less then adequate duct design.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  6. #6
    Join Date
    Sep 2012
    Posts
    373
    Post Likes
    Thread Starter
    Thanks beenthere. So, I will look into that when we have the system replaced.

  7. #7
    Join Date
    Sep 2012
    Posts
    373
    Post Likes
    Thread Starter
    One last question, If we do end up having a return added, what size will it have to be?

  8. #8
    Join Date
    Jan 2004
    Location
    PA
    Posts
    73,800
    Post Likes
    What ever size is needed to return the same amount of air your supplying to that room. Might need an 8" round.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  9. #9
    Join Date
    Sep 2012
    Posts
    373
    Post Likes
    Thread Starter
    OK. Thanks for the input. We are having our heating tune up done on Oct 1, and I'll ask the service tech then to look at the system.

  10. #10
    Join Date
    Sep 2012
    Posts
    373
    Post Likes
    Thread Starter
    It has been a few weeks since I've visited this thread. I need to make a correction about the size of the return in the theater room. That return is 12 inch NOT 10 inch like a previously said. Hope this helps.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.