    High super heat , high sub cool

    Recently I attended a complaint that only room is getting 26°C only. ThenI checked a Ac Lennox 2Ton R22 SYSTEM FIXED Orfice
    Liquid line pressure - 305Psi
    Suction line Pressure - 78Psi
    Liquid line Temperature - 119°F (Near Condenser)
    Suction line Temperature -83°F(Near Condenser)
    From Eveprator Air flow Temp -67°F
    Return Airflow to Eveprator Temp -79°F
    Compressor Ampere little high
    Outside Temperature - 108°F

    Can anyone tell what is the issue?
    .
    I Changed orfice piston 059 , I flushed evaporator Unit

  2. #2
    Join Date
    Jan 2010
    Posts
    45,373
    Post Likes
    Paul
    I moved your thread to the
    ( Tech to Tech Chat- Residential )since you stated you're a technician.in your profile.
    This is where you should ask your questions.

  3. #3
    Join Date
    Jan 2010
    Posts
    45,373
    Post Likes
    System could be working outside of it's design condition.
    Did you clean the condenser ?

  4. #4
    Join Date
    Aug 2021
    Posts
    15
    Post Likes
    Thread Starter
    No , I didn't flush condenser

  5. #5
    Join Date
    Aug 2021
    Posts
    15
    Post Likes
    Thread Starter
    But I cleaned condenser unit and changed fan motor

  6. #6
    Join Date
    Apr 2020
    Location
    va
    Posts
    10,300
    Post Likes
    Test for noncondensables.

  7. #7
    Join Date
    Jan 2012
    Location
    Missouri, USA
    Posts
    3,963
    Post Likes
    Lower indoor blower speed and retest.

  8. #8
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    14,048
    Post Likes
    Quote Originally Posted by Paul4131 View Post
    Outside Temperature - 108°F
    I know what I would do ..... I'd go home and start packing
    Tell your Cat I said "Psst Psst Psst"

    It seems like everywhere I go the AC is broken

  9. Likes VTP99, BBeerme, Achso017 liked this post.
  10. #9
    Join Date
    Aug 2021
    Posts
    15
    Post Likes
    Thread Starter
    I changed new orginal blower and blower motor

  11. #10
    Join Date
    Aug 2021
    Posts
    15
    Post Likes
    Thread Starter
    How to make noncondensables test?

  12. #11
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    14,048
    Post Likes
    Quote Originally Posted by Paul4131 View Post
    I changed new orginal blower and blower motor
    I think almost all blower motors have 3 speeds ....
    Tell your Cat I said "Psst Psst Psst"

    It seems like everywhere I go the AC is broken

  13. #12
    Join Date
    Apr 2020
    Location
    va
    Posts
    10,300
    Post Likes
    Quote Originally Posted by Paul4131 View Post
    How to make noncondensables test?
    Close ll service valve, pumpdown if possible, manually run condenser fan motor till pressure stabilizes, compare saturated temp to ambient. Should match.

  14. Likes takoateli liked this post.
  15. #13
    Join Date
    Aug 2021
    Posts
    15
    Post Likes
    Thread Starter
    Ok I will check

  16. #14
    Join Date
    Sep 2010
    Location
    Indiana
    Posts
    1,005
    Post Likes
    Low charge.

    108 outside? 79db inside. Wet bulb id take a guess at 63...

    Should be about 1 degree superheated not 30

  17. #15
    Join Date
    Aug 2021
    Posts
    15
    Post Likes
    Thread Starter
    I released gas and vacuuming, recharged gas . Still Ac is working same as before. Could it be due to excessive heat load?

  18. #16
    Join Date
    Aug 2021
    Posts
    15
    Post Likes
    Thread Starter
    And could it be due to scroll compressor failure?

  19. #17
    Join Date
    Sep 2010
    Location
    Indiana
    Posts
    1,005
    Post Likes
    I wouldn't expect "a little high" amps if it wasn't pumping. If you block off the condenser does the suction climb?

  20. #18
    Join Date
    Dec 2016
    Location
    East Meadow, N.Y.
    Posts
    1,815
    Post Likes
    Quote Originally Posted by Paul4131 View Post
    And could it be due to scroll compressor failure?
    You have a very high compressor ratio, so the compressor is working well for now. As Ksefan mentioned, you could try lowering the fan speed till you get 18 to 21 degrees difference between supply and return.

    Sincerely,

    Willliam McCormick

  21. #19
    Join Date
    Dec 2016
    Location
    East Meadow, N.Y.
    Posts
    1,815
    Post Likes
    Quote Originally Posted by Snapperhead View Post
    I think almost all blower motors have 3 speeds ....
    Some Rheem Rudd, split air handlers have single-speed blower motors, that burns my biscuits.

    Sincerely,

    William McCormick

  22. #20
    Join Date
    Jan 2012
    Location
    Missouri, USA
    Posts
    3,963
    Post Likes
    Quote Originally Posted by Bill mcC View Post
    Some Rheem Rudd, split air handlers have single-speed blower motors, that burns my biscuits.

    Sincerely,

    William McCormick
    Or blower motors with 5 cfm difference between high and low speed.

+ Reply to Thread
Page 1 of 3 123 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •