Thread: TXV Question

  1. #21
    Join Date
    Feb 2009
    Location
    Tallahassee, FL
    Posts
    6,217
    Post Likes
    Go where you purchased the valve and have a look at the eq tube fitting. If it has no schrader depressor go back and remove tube. Add service tee with schrader depressor with eq tube connected to port with no schrader.

    Or just pump it down and remove it.

  2. #22
    Join Date
    Feb 2006
    Location
    Phoenix,AZ
    Posts
    4,021
    Post Likes
    Quote Originally Posted by millertime77 View Post
    The valve that I am talking about replaced a valve that had a very small tube brazed into the suction line, that I thought was the external equalizer, and was replaced with a valve that had the same tube with a female flare and came with a 90 degree short piece of suction tube with the male threaded flare connection for, what I thought was the new equalization tube.
    That is the external eq line. But it doesn't dump refrigerant from the high side to the low side during the off cycle. A bleed valve does that instead. Did you read the PDF?

  3. #23
    Join Date
    Jul 2009
    Location
    Damascus MD
    Posts
    6,160
    Post Likes
    the equalizer tube sees the suction pressure of the evaporator.

    it takes the suction pressure and forces it on the spring of the diaphragm or bulb pressure.

    if the equalizer tube were blocked there would be no pressure against the spring and the valve would be forced close which would give you a high superheat.

  4. #24
    Join Date
    Feb 2009
    Location
    Tallahassee, FL
    Posts
    6,217
    Post Likes
    Think that's backwards

  5. #25
    Join Date
    Oct 2011
    Location
    between here and over there
    Posts
    453
    Post Likes
    Quote Originally Posted by dachipsta View Post
    I wouldnt leave a valve core in for something like that because anytime it would need to be taken off the system will be empty of gas anyways. If not and for some reason the system is slow to equalize, you will wind up with compressor starting issues if the cycles are close together, sometimes even when they arent. Not as much if you have start componants but why go thru the hassle. Take out the core.
    understand that its all based on what the equipment manufacture designed it for. Trane heatpump air handler coils come with the core in but you must remove it before you install the TXV. the equalizer cap tube with the flare end, is not equipped with a depressor. if you leave the core in and install the TXV and start the unit it will not equalize the TXV in respect to the evap coil causing problems with the performance of the TXV and overall system. I would follow the manufactures instructions. every one is different.
    ®

  6. #26
    Join Date
    Dec 2010
    Location
    Virginia
    Posts
    360
    Post Likes
    Read most of the PDF, a good one indeed, and figured out that it is 2 oppossing forces that control the flow of refrigerant, the charge in the bulb against the back pressure leaving the evaporator. So I guess I was wrong in my thinking that pressures equalize in a txv system, they don't? They do though equalize in a system using a piston as a metering device?

  7. #27
    Join Date
    Jul 2009
    Location
    Damascus MD
    Posts
    6,160
    Post Likes
    im pretty sure by looking at the design of the valve. the equalizer tube(suction pressure) puts pressure on spring which is driven by the bulb pressure. if the equalizer was blocked the valve would shut down.

    maybe someone else can chime in. im not at my computer.

  8. #28
    Join Date
    Jul 2009
    Location
    Damascus MD
    Posts
    6,160
    Post Likes
    ok found it.....this should clear it all up

    http://www.sporlanonline.com/10-37.pdf

  9. #29
    Join Date
    Jan 2008
    Location
    In the work truck
    Posts
    3,275
    Post Likes
    THere is only one opening force on a TEV. That is the bulb which is pushing down on the needle. Warmer bulb, Valve throttles open.
    THe Closing force is evaporator pressure and spring pressure.

    In regards to the PDF Gravity posted I am pretty sure when they are talking about high superheat/ low suction being a blocked equalizer they are referring to the seal around the pushrods leaking. This gas cannot escape because of the blockage and pushes up on the diaphragm. This counteracts the opening force of the valve..
    Gotta have the right tool for the job!

    Where is all the stuff MADE IN THE USA?

    "Thats what we do Troy. Incredible, Invisible, Imbelivable things. We are an Unseen, Unknown, Unvincible fraternity of craftsman.."

  10. #30
    Join Date
    Jan 2008
    Location
    In the work truck
    Posts
    3,275
    Post Likes
    Quote Originally Posted by millertime77 View Post
    Read most of the PDF, a good one indeed, and figured out that it is 2 oppossing forces that control the flow of refrigerant, the charge in the bulb against the back pressure leaving the evaporator. So I guess I was wrong in my thinking that pressures equalize in a txv system, they don't? They do though equalize in a system using a piston as a metering device?
    Yes many TEV's do equalize. However they do it in a manner differently then you first thought. Basically there is hole drilled in the valve body. They are different sizes and Sporlan stamps the size of the port next to "BP" on the side of the valve.
    York for example on residential systems do not have this so the pressures dont equalize.

    OF course on captubes or orifices the pressure does equalize.
    Gotta have the right tool for the job!

    Where is all the stuff MADE IN THE USA?

    "Thats what we do Troy. Incredible, Invisible, Imbelivable things. We are an Unseen, Unknown, Unvincible fraternity of craftsman.."

  11. #31
    Join Date
    Jun 2012
    Location
    East tx
    Posts
    164
    Post Likes
    Should be fine. I've installed a few and the equalizer line had a schrader depressor. Zero issues with many a mile on them.

  12. Likes VanUllandHVAC liked this post.
  13. #32
    Join Date
    Feb 2009
    Location
    Tallahassee, FL
    Posts
    6,217
    Post Likes
    Quote Originally Posted by gravity View Post
    im pretty sure by looking at the design of the valve. the equalizer tube(suction pressure) puts pressure on spring which is driven by the bulb pressure. if the equalizer was blocked the valve would shut down.

    maybe someone else can chime in. im not at my computer.
    I understand what you are saying but how does a non bleed valve work? I though with the rising suction pressure forces valve closed. With lower suction pressure ie 0 and warm bulb shouldn't valve tend to open.

  14. #33
    Join Date
    Feb 2009
    Location
    Tallahassee, FL
    Posts
    6,217
    Post Likes
    Also non bleed valves are a good thing as long as recip compressor has start component.

    Huge efficiency gains as well as increased dehum due to warm refrigerant not being able to warm up evap. Cycling losses

  15. #34
    Join Date
    Jul 2009
    Location
    Damascus MD
    Posts
    6,160
    Post Likes
    i found another pdf.

    it also shows high superheat/ low suction is a cause of a plugged external equalizer tube

    http://www.hintech-electric.com/cata...lp%20guide.pdf

    scroll to bottom for troubleshooting

  16. #35
    Join Date
    Feb 2009
    Location
    Tallahassee, FL
    Posts
    6,217
    Post Likes
    Quote Originally Posted by gravity View Post
    i found another pdf.

    it also shows high superheat/ low suction is a cause of a plugged external equalizer tube

    http://www.hintech-electric.com/cata...lp%20guide.pdf

    scroll to bottom for troubleshooting
    Plugged to me is different than not connected. If plugged it would read higher than normal evap press.

    If the evap pressure force acts in the closing direction and it is non existing due to no schrader depress wouldn't you assume valve would stay wide open.

    That is a neat pdf and it will be kept. I appreciate it.

  17. #36
    Join Date
    Jul 2005
    Posts
    7,834
    Post Likes
    Quote Originally Posted by SBKold View Post
    I understand what you are saying but how does a non bleed valve work? I though with the rising suction pressure forces valve closed. With lower suction pressure ie 0 and warm bulb shouldn't valve tend to open.
    When the compressor shuts down the low side pressure will begin to rise, increasing the closing force. The valve closes.

  18. #37
    Join Date
    Jul 2009
    Location
    Damascus MD
    Posts
    6,160
    Post Likes
    if its plugged it would be the same as not connected

  19. #38
    Join Date
    Jul 2009
    Location
    Damascus MD
    Posts
    6,160
    Post Likes
    ive never witnessed a clogged or capped off tube. but going by the troubleshooting guide i linked it saids a plugged tube would have low suction and high superheat

  20. #39
    Join Date
    Feb 2009
    Location
    Tallahassee, FL
    Posts
    6,217
    Post Likes
    What I believe happens is very small amount of pressure from the high side enters into chamber where it never enters the low side. Hence keeping higher than normal closing force.

    Now if the equalizer were never connected would be the only way to have wide open valve.

  21. #40
    Join Date
    Jul 2009
    Location
    Damascus MD
    Posts
    6,160
    Post Likes
    are you talking about if the stem were leaking?

+ Reply to Thread
Page 2 of 3 FirstFirst 123 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •