Thread: TXV Question

  1. #14
    Join Date
    Feb 2006
    Location
    Phoenix,AZ
    Posts
    2,760
    Quote Originally Posted by Pascone10 View Post
    THats wrong. You should read up on the operation of the TEV...
    Yeah, he's confusing "Bleed" with equalize!!!

  2. #15
    Join Date
    Jan 2008
    Location
    In the work truck
    Posts
    2,942
    Mojo, If you hooked the 1/4" external equalizer line to a flare port with a schrader you need to go back and remedy your mistake. We all make mistakes and that is not a problem. However you need to step up and do what is right. Im glad to see you came here and asked the question. Good job.
    Gotta have the right tool for the job!

    Where is all the stuff MADE IN THE USA?

    "Thats what we do Troy. Incredible, Invisible, Imbelivable things. We are an Unseen, Unknown, Unvincible fraternity of craftsman.."

  3. #16
    Join Date
    Jan 2008
    Location
    In the work truck
    Posts
    2,942
    Quote Originally Posted by KB Cool View Post
    Yeah, he's confusing "Bleed" with equalize!!!
    Yea the "Bleed Port".. "equalizes". WHo would have thought that
    Its ok I know I thought that as well when I started in this trade.

    Honestly tho Im surprised how many never learned the complete way a TEV works. Once you learn it tho it makes life easy.
    Gotta have the right tool for the job!

    Where is all the stuff MADE IN THE USA?

    "Thats what we do Troy. Incredible, Invisible, Imbelivable things. We are an Unseen, Unknown, Unvincible fraternity of craftsman.."

  4. #17
    Join Date
    Dec 2010
    Location
    Virginia
    Posts
    353
    ok, so you are saying the valves I am dealing with are internally equalized? If so what does the bleed port do?

  5. #18
    Join Date
    Jan 2008
    Location
    In the work truck
    Posts
    2,942
    I dont know what kind of valve your working on. Is there a 1/4" tube you braze into the suction line? IF so the Valve is externally equalized.
    The bleed port is a hole in the valve that allows refrigerant to bypass the valve in the off cycle.
    Did you start reading on Sporlan's site yet? Bulletin 10-9 and 10-10 will answer your questions. Take the time to read and understand them. If you need help ask the question. We will help.
    Gotta have the right tool for the job!

    Where is all the stuff MADE IN THE USA?

    "Thats what we do Troy. Incredible, Invisible, Imbelivable things. We are an Unseen, Unknown, Unvincible fraternity of craftsman.."

  6. #19
    Join Date
    Feb 2006
    Location
    Phoenix,AZ
    Posts
    2,760
    Quote Originally Posted by millertime77 View Post
    ok, so you are saying the valves I am dealing with are internally equalized? If so what does the bleed port do?
    internal eq. valves are found on small evaps such as reach-in coolers with little pressure drop!!! Here's a pdf from parker thats a little better than the one i posted earlier. http://www.parker.com/literature/Aft...V%20Theory.pdf

  7. #20
    Join Date
    Dec 2010
    Location
    Virginia
    Posts
    353
    The valve that I am talking about replaced a valve that had a very small tube brazed into the suction line, that I thought was the external equalizer, and was replaced with a valve that had the same tube with a female flare and came with a 90 degree short piece of suction tube with the male threaded flare connection for, what I thought was the new equalization tube.

  8. #21
    Join Date
    Feb 2009
    Location
    Tallahassee, FL
    Posts
    5,821
    Go where you purchased the valve and have a look at the eq tube fitting. If it has no schrader depressor go back and remove tube. Add service tee with schrader depressor with eq tube connected to port with no schrader.

    Or just pump it down and remove it.

  9. #22
    Join Date
    Feb 2006
    Location
    Phoenix,AZ
    Posts
    2,760
    Quote Originally Posted by millertime77 View Post
    The valve that I am talking about replaced a valve that had a very small tube brazed into the suction line, that I thought was the external equalizer, and was replaced with a valve that had the same tube with a female flare and came with a 90 degree short piece of suction tube with the male threaded flare connection for, what I thought was the new equalization tube.
    That is the external eq line. But it doesn't dump refrigerant from the high side to the low side during the off cycle. A bleed valve does that instead. Did you read the PDF?

  10. #23
    Join Date
    Jul 2009
    Location
    Columbia, MD
    Posts
    3,379
    the equalizer tube sees the suction pressure of the evaporator.

    it takes the suction pressure and forces it on the spring of the diaphragm or bulb pressure.

    if the equalizer tube were blocked there would be no pressure against the spring and the valve would be forced close which would give you a high superheat.

  11. #24
    Join Date
    Feb 2009
    Location
    Tallahassee, FL
    Posts
    5,821
    Think that's backwards

  12. #25
    Join Date
    Oct 2011
    Location
    between here and over there
    Posts
    453
    Quote Originally Posted by dachipsta View Post
    I wouldnt leave a valve core in for something like that because anytime it would need to be taken off the system will be empty of gas anyways. If not and for some reason the system is slow to equalize, you will wind up with compressor starting issues if the cycles are close together, sometimes even when they arent. Not as much if you have start componants but why go thru the hassle. Take out the core.
    understand that its all based on what the equipment manufacture designed it for. Trane heatpump air handler coils come with the core in but you must remove it before you install the TXV. the equalizer cap tube with the flare end, is not equipped with a depressor. if you leave the core in and install the TXV and start the unit it will not equalize the TXV in respect to the evap coil causing problems with the performance of the TXV and overall system. I would follow the manufactures instructions. every one is different.

  13. #26
    Join Date
    Dec 2010
    Location
    Virginia
    Posts
    353
    Read most of the PDF, a good one indeed, and figured out that it is 2 oppossing forces that control the flow of refrigerant, the charge in the bulb against the back pressure leaving the evaporator. So I guess I was wrong in my thinking that pressures equalize in a txv system, they don't? They do though equalize in a system using a piston as a metering device?

Page 2 of 4 FirstFirst 1234 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event