    TXV Question

    Just curious on the newer style TXV"s and coils. If you use the internal port on the inside coil to connect the braze-less TXV, do you remove the schrader or can you leave it in? I ask this because I've always brazed the included extensions and they never came with schraders installed. Logically the internal sensor block would keep it depressed and take readings just fine, but we all know manufactures never seem to build equipment well thinking logically; lol.!

  2. #2
    Join Date
    Jul 2009
    Location
    Columbia, MD
    Posts
    4,483
    are you talking about an external equalizer line? if it has a shraider depressor in it then you can leave the shraider in. i always take them out.

  3. #3
    No, on the newer internal coils they have a port inside the case, I hear it's used for the factory to pressurize them with nitrogen. I've always purchased the braze style TXV, for residential heat-pump/fossil furnace setups 13seer and over. I got a newer screw on style TXV today and I left the schrader in, now I'm nervous it may cause issues with the TXV later on. It cycled fine and pressures were good. It was to cold outside to trim the superheat and get good head pressure readings. I've never had to adjust any factory matched set before so I let them used the system until I can come back on a warmer day. Now I'm slightly worried about the TXV, and I really don't want to pump it down again.

  4. #4
    Join Date
    Jul 2009
    Location
    Columbia, MD
    Posts
    4,483
    a indoor evaporator coil? well if it doesn;t have a shraider depressor in it then you will starve your evaporator coil. you will have really high superheat.

  5. #5
    Join Date
    Nov 2001
    Location
    East Texas
    Posts
    949
    Should be fine,,,,,,,,no worries.

  6. #6
    Join Date
    Dec 2010
    Location
    Virginia
    Posts
    355
    ok, so you are saying the valves I am dealing with are internally equalized? If so what does the bleed port do?

  7. #7
    Join Date
    Jan 2008
    Location
    In the work truck
    Posts
    3,076
    I dont know what kind of valve your working on. Is there a 1/4" tube you braze into the suction line? IF so the Valve is externally equalized.
    The bleed port is a hole in the valve that allows refrigerant to bypass the valve in the off cycle.
    Did you start reading on Sporlan's site yet? Bulletin 10-9 and 10-10 will answer your questions. Take the time to read and understand them. If you need help ask the question. We will help.
    Gotta have the right tool for the job!

    Where is all the stuff MADE IN THE USA?

    "Thats what we do Troy. Incredible, Invisible, Imbelivable things. We are an Unseen, Unknown, Unvincible fraternity of craftsman.."

  8. #8
    Join Date
    Dec 2010
    Location
    Virginia
    Posts
    355
    The valve that I am talking about replaced a valve that had a very small tube brazed into the suction line, that I thought was the external equalizer, and was replaced with a valve that had the same tube with a female flare and came with a 90 degree short piece of suction tube with the male threaded flare connection for, what I thought was the new equalization tube.

  9. #9
    Join Date
    Feb 2006
    Location
    Phoenix,AZ
    Posts
    2,895
    Quote Originally Posted by millertime77 View Post
    The valve that I am talking about replaced a valve that had a very small tube brazed into the suction line, that I thought was the external equalizer, and was replaced with a valve that had the same tube with a female flare and came with a 90 degree short piece of suction tube with the male threaded flare connection for, what I thought was the new equalization tube.
    That is the external eq line. But it doesn't dump refrigerant from the high side to the low side during the off cycle. A bleed valve does that instead. Did you read the PDF?

  10. #10
    Join Date
    Feb 2006
    Location
    Phoenix,AZ
    Posts
    2,895
    Quote Originally Posted by millertime77 View Post
    ok, so you are saying the valves I am dealing with are internally equalized? If so what does the bleed port do?
    internal eq. valves are found on small evaps such as reach-in coolers with little pressure drop!!! Here's a pdf from parker thats a little better than the one i posted earlier. http://www.parker.com/literature/Aft...V%20Theory.pdf

  11. #11
    Join Date
    Oct 2010
    Location
    Anderson, South Carolina, United States
    Posts
    7,778
    I've never seen one with a valve core depressor on it so I always take the valve stem out. All the York's don't have a stem in it it comes with the outdoor unit packaged with the piston

  12. #12
    Join Date
    Jun 2011
    Location
    Detroit vicinity, Michigan
    Posts
    79
    Yeah, if you don't pull the schrader........you're gonna have a bad time!

  13. #13
    Join Date
    Aug 2001
    Location
    Pavilion, NY
    Posts
    2,198
    I think he is referring to a situation such as a goodman Evap. When you install the external txv and they send you stubs, he is referring to using the Schrader factory installed on the suction line of the unit. The flare connection has a depressor on the end.
    ...

Page 1 of 3 123 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event