Results 1 to 13 of 29
    new jersey
    high head low back pressure
    Hi guys, I have a question for all the techs out there.
    Regular 1/3 hp self contain reach in
    134a txv system, 16 ounces charge
    Normal operation pressures H-110# L-14#
    My question is > what condition will make this unit run with head pressure 250# and a back pressure -25#?
    Jan 2010
    Ft. Walton Beach, FL
    Agree w/ jpsmith, either clogged filter or metering device, probably caked up coil too
    new jersey
    It is a TXV system not a cap system
    And it is 1 week old
    Oct 2011
    Chicagoland Area
    Doesn't matter how old. I've had new equipment not work from the factory. My advice to you is contact the mfg and find out how you should proceed. If they're paying for it, follow their instructions.
    new jersey
    I work for the factory, I design the the coolers and the refrigeration system. We had a call from a out of state end user saying our cooler wasn't working rigth , was dead on arrival. I call a service company to go look at it, the tech said he thinks was a restriction because he put the gauges on it and got 250# head pressure and -25# on back pressure .
    I try to duplicate those pressures in a identical unit in the shop, unit working normal, I close the king valve on the receiver to create the restriction, my back pressure drop to -20# and my head pressure drop from 110# to 90#. The head pressure drop didn't rise . Were the 250# come from?
    Jul 2009
    Columbia, MD
    from the unit being over charged because of low pressure.
    Jun 2009
    DFW, TX
    The ambient temp in the kitchen is 95*f while the one in your shop is 70*F? Just a SWAG...
    Oct 2011
    Chicagoland Area
    The guy looking at it added gas because he thought it was low. It didn't work. He called tech support.
    Jul 2009
    Columbia, MD
    the readings the tech saw is most likely due to a restricted metering device with an over charge. the unit is probably over charged because it wasn't working right at startup. so, what does every tech do with low pressures? they add refrigerant.....
    i would assume by you closing the king valve you made a restriction before your gauges which indicate low head. try over charging the unit and creating a restriction after the high side gauge.
    you engineer these units? where do i sign up for this job?
    new jersey
    My high gauge is before the king valve, and I try to over charge it , I put double the Freon and the high side gauge went up a couple # ( with the restriction in the king valve)
    California
    Quote Originally Posted by coolerman View Post
    Wait a minute here...
    You are asking US how to diagnose & repair a system that YOU designed??????
    new jersey
    I'm just asking a opinion, because doesn't make sense , maybe you guys know something that I don't. what I think is that teck is full of *****.