Results 1 to 2 of 2
  1. #1
    Join Date
    Sep 2007
    Posts
    9

    Refrigerant leaks in eighteen RTU's - acidic condensate

    This has got to be an air quality issue:

    So we have a customer - a moving company - that owns an A/C storage warehouse with eighteen rtu's. Every one of them has refrigerant leaks. Most of the units are about eight years old, but refrigerant is leaking even in units that are 1-2 years old. There is a noticeable accelerated corrosion on the evaporator end plates and drain pans.

    We have just received results from water tests we did on the condensate, and the pH is between 4.3 and 4.8. Pretty low, right? Has anybody seen this before? What might cause it?

    The only lead I have is that I think they are running propane forklifts inside. Could the exhaust somehow make the condensate acidic?

    -Joshua

  2. #2
    Join Date
    Jul 2010
    Location
    nebraska
    Posts
    1,163
    That's probably a good guess. I've seen the condensate from 90% furnaces eat through copper drain lines and etch 1/4" gouges in concrete.Also saw vtk's vented backwards so the exhaust sucked right back into the intake, rusted out heat exchangers in less than 3 years. Seems like tin end plates wouldn't stand a chance.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •