  1. #14
    So far i haven't brought it in since it won't but I am trying to using the BACnet IP not MS\TP. Again i have had success with many different vendors both brought in BACnet MS\TP and BACnet IP and this is the only vendor i have had any trouble with.

  2. #15
    Join Date
    May 2006
    Posts
    675
    Quote Originally Posted by sundodger4 View Post
    So far i haven't brought it in since it won't but I am trying to using the BACnet IP not MS\TP. Again i have had success with many different vendors both brought in BACnet MS\TP and BACnet IP and this is the only vendor i have had any trouble with.
    Did you add in the IP address into the BBMD of the NAE?? This is a direct link from the NAE to the device.

  3. #16
    Join Date
    May 2006
    Posts
    675
    http://www.chipkin.com/technical-res...cnet-explorer/

    If the above doesn't work - go to this site and download this tool. From your machine, you can scan the BACnet/IP and see if this device is even working.

  4. #17
    Join Date
    Nov 2005
    Location
    Shreveport, Louisiana
    Posts
    2,338
    Does the lutron panel and the NAE have the correct subent and gateway information????? Did you add it as a BBMD in the NAE?
    UA Local 141

  5. #18
    Join Date
    Dec 2011
    Location
    Charlotte, NC
    Posts
    47
    If the two devices are on the same subnet, and you can ping one but don't see anything w/ BACnet/IP, you may want to check the other device's (Lutron) subnet mask. The subnet mask is used to determine the broadcast address of the subnet, and BACnet/IP depends upon broadcast functionality. Depending on the subnet mask, you may be able to ping without issue, but the other device (Lutron) may not ever respond to your BACnet/IP discovery messages. If the subnet mask on the device is configured incorrectly, it will ignore those discovery messages, because from it's perspective, they are not being sent to the broadcast address.

  6. #19
    Quote Originally Posted by integrator View Post
    Did you add in the IP address into the BBMD of the NAE?? This is a direct link from the NAE to the device.
    That took care of the problem, I only had the Lutron panel in teh BBMD, when I did as you said, put the NAE IP in there also it fixed the problem, thanks

Page 2 of 2 FirstFirst 12

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event