Results 1 to 9 of 9
Thread: yk motor caught on fire
-
09-05-2012, 02:29 AM #1
Professional Member
- Join Date
- Jun 2012
- Location
- so cal
- Posts
- 21
yk motor caught on fire
i recently had a 800 hp yk motor on a vsd catch fire has anyone had this happen
-
09-05-2012, 07:10 AM #2
not a motor but I did have a vfd on a 19xrv blow up and the pieces that landed was on fire. and I saw it all happen.
-
09-05-2012, 03:33 PM #3
Professional Member
- Join Date
- Jan 2011
- Posts
- 646
Please explain exactly what burned. What were your megger readings when you performed the last annual inspection? I have seen people start chillers with low megger readings and blow a hole in the windings and shoot a fireball out and leave molten pieces of windings everywhere, but I have never seen one actually catch on fire.
Originally Posted by chillersinc
-
09-05-2012, 05:00 PM #4
Awesome! I only get the boring stuff over temp on hi phase this and that. I had a six lead motor on a blue oval recently act strange but not on fire......Yet.
It takes courage to grow up and turn out to be who you really are.
- E.E. Cummings
-
09-05-2012, 09:21 PM #5
Professional Member
- Join Date
- Oct 2011
- Location
- La.
- Posts
- 211
Had a 2000 ton YK loose the bearings on the motor and this started a fire in the motor from the grease burning. Perhaps this is what happened.
-
09-05-2012, 09:48 PM #6
Professional Member
- Join Date
- Sep 2011
- Location
- Northwest Louisiana
- Posts
- 155
Ditto on bearing failure and all the extra grease pumped in to cover the bearing noise. Fire dept had to put out. Seen lots of windings blow but not go up in flames. Recently a new Trane CVHF had it's VFD catch fire and complely burn up every combustable in machine. Nothing left but copper buss and some wire. Recent York motors are on low end of quality, wouldnt surprise me if they flamed up.
A LITTLE BIT OF STUPID GOES A LONG WAY!
-
09-14-2012, 09:23 AM #7
Regular Guest
- Join Date
- Feb 2010
- Posts
- 81
Open drive york, sat idle for to long??, we have strapped heaters to motor belly, no motor likes moisture at windings??
-
09-14-2012, 03:43 PM #8
New Guest
- Join Date
- Dec 2011
- Location
- Ft Lauderdale, Fl
- Posts
- 3
We had same problem on a YK
Wrong greasing procedure used by in house service techs (Big pharmaceutical) wayyyyyy too much grease pumped into the bearings. The motor flamed up. We were not aware of cause of failure until we had the failure report from motor rebuild shop.
Its always a good idea to inspect with flashlight the rotor shaft for indication of grease from bearings. Also, If i remember correctly, York specifies Polyurea based grease such as Mobil Polyrex EM, any other grease is not worthy!!........They say.
I think I read SB on that, cant quite remember.
-
09-15-2012, 11:37 AM #9
Professional Member*
- Join Date
- Jan 2009
- Location
- Jersey
- Posts
- 119
had one of the newer ram motors flame up, one of the motor leads came loose internally, shorted out, motor ran with six foot flames shooting out of the air vents, made for a really interesting day.