Thread: Cant get bubbles out of sight glass

  1. #41
    Join Date
    May 2011
    Location
    tallahassee,fl
    Posts
    380
    Post Likes
    Quote Originally Posted by WhiteSoxFan View Post
    ^
    X3

    FWIW, I had a similar job a month ago. SC was where it was supposed to be but the SG was not clear... I was told a TXV needed a full column of liquid to work properly so I kept adding juice. I couldn't clear the SG to save my life... After way overshhoting the SC and still seeing bubbles, I decided to forget about the SG and just focus on the SC.

    Hope that helps...
    Yep, had a unit early in my career that I charged by site glass, operated great when I left it, next day call for no cool, go back 30* sc, sh&@! Set sc at 10* and no call back. DO NOT CHARGE BY SG, period!!!

  2. #42
    Join Date
    Dec 2010
    Location
    Virginia
    Posts
    360
    Post Likes
    Thread Starter
    Thanks for all of your guys help. Experience says that airconditioning should always have a solid column of liquid, and refrigeration, in low ambient, is the only time you should see bubbles. I think it could be a problem with the piston(in backwards, or moving around a little, like someone mentioned), and probably a few other possibilities, but what are you going to do. If it isn't broke don't fix it. By the way I have checked the evap coil, and it isn't dirty, and I changed the filter. I think the sight glasses should be used in medium and low temp applications only, not air conditioning. Thanks to all.

  3. #43
    Join Date
    Feb 2009
    Location
    Tallahassee, FL
    Posts
    6,217
    Post Likes
    A sight glass is a useful tool on any system regardless of low temp or high temp. IMHO. Its function does not change because it is on a ac unit.

    Its a nice tool meant used in conjunction with (not in leiu of) all the others.

  4. #44
    Join Date
    Jul 2002
    Posts
    1,790
    Post Likes
    Sightglasses are for TXV systems ONLY. Take it our or tape it up!

  5. #45
    Join Date
    Sep 2012
    Posts
    4
    Post Likes
    I agree. Sight glasses can be useful on TXV systems but are worthless on fixed bore metering devices. Never use a sight glass on any refrigeration, ac, or heat pump with a fixed bore. Get back to basics and check superheat based upon the inddor dry bulb temp and the outdoor ambient temp.

  6. #46
    Join Date
    Sep 2012
    Posts
    4
    Post Likes
    Sorry. I meant to say indoor WET bulb and outdoor ambient

  7. #47
    Join Date
    Jun 2004
    Posts
    946
    Post Likes
    Txv or fixed orifice
    Sight glass should not be used to determine the charge on small resi equipment.

    Its not true that only on low ambient condition will cause bubbles on sight glass
    High indoor loads will cause bubbles too
    Dirty condenser
    extreme outdoor temp
    Long liquid line on the roof (flash gas)
    Long vertical liquid line (pressure drop)
    Non condensable
    Blend refrigerant high temperature glide.
    Restriction upstream of sight glass
    Wide txv hunting
    Unseated orifice
    Gas heater is running the same time

    Sorry that's all I could think off right now.

  8. #48
    Join Date
    Jul 2011
    Posts
    21
    Post Likes
    Quote Originally Posted by shaka View Post
    High indoor loads will cause bubbles too
    Please explain how. Not that I disagree, I just want to understand why.

  9. #49
    Join Date
    Jul 2008
    Location
    Mid Michigan
    Posts
    321
    Post Likes
    Quote Originally Posted by WhiteSoxFan View Post
    Please explain how. Not that I disagree, I just want to understand why.
    With more heat to reject at the condensor there will be less liquid building up in the condensor the hot gas will take longer to change state to liquid.
    Waddya mean don't thaw out the frig with a knive?

+ Reply to Thread
Page 3 of 3 FirstFirst 123

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •