09-12-2012, 05:49 PM #40
It sounds more like a dirty evaporator coil or low air flow but I suspect dirty coil. It can still cool O.K. depending on how much demand there is in the conditioned space. A dirty coil won't necessarily show a low TD but will show low SH. I also agree with the others about no need to worry about bubbles in the sight glass, especially dealing with a piston system.
Gary
-----------
http://www.oceanhvac.com
An engineer designs what he would never work on.
A technician works on what he would never design.
-
09-12-2012, 05:53 PM #41
-
09-12-2012, 06:09 PM #42
Thanks for all of your guys help. Experience says that airconditioning should always have a solid column of liquid, and refrigeration, in low ambient, is the only time you should see bubbles. I think it could be a problem with the piston(in backwards, or moving around a little, like someone mentioned), and probably a few other possibilities, but what are you going to do. If it isn't broke don't fix it. By the way I have checked the evap coil, and it isn't dirty, and I changed the filter. I think the sight glasses should be used in medium and low temp applications only, not air conditioning. Thanks to all.
-
09-12-2012, 07:20 PM #43
A sight glass is a useful tool on any system regardless of low temp or high temp. IMHO. Its function does not change because it is on a ac unit.
Its a nice tool meant used in conjunction with (not in leiu of) all the others.
-
09-12-2012, 07:46 PM #44
Sightglasses are for TXV systems ONLY. Take it our or tape it up!
-
09-12-2012, 08:17 PM #45
New Guest
- Join Date
- Sep 2012
- Posts
- 4
I agree. Sight glasses can be useful on TXV systems but are worthless on fixed bore metering devices. Never use a sight glass on any refrigeration, ac, or heat pump with a fixed bore. Get back to basics and check superheat based upon the inddor dry bulb temp and the outdoor ambient temp.
-
09-12-2012, 08:19 PM #46
New Guest
- Join Date
- Sep 2012
- Posts
- 4
Sorry. I meant to say indoor WET bulb and outdoor ambient
-
09-13-2012, 01:06 AM #47
Txv or fixed orifice
Sight glass should not be used to determine the charge on small resi equipment.
Its not true that only on low ambient condition will cause bubbles on sight glass
High indoor loads will cause bubbles too
Dirty condenser
extreme outdoor temp
Long liquid line on the roof (flash gas)
Long vertical liquid line (pressure drop)
Non condensable
Blend refrigerant high temperature glide.
Restriction upstream of sight glass
Wide txv hunting
Unseated orifice
Gas heater is running the same time
Sorry that's all I could think off right now.
-