+ Reply to Thread
Results 1 to 9 of 9

Thread: CFM Recommendations for Spray Tanning Room

  1. #1
    Join Date
    Jun 2011
    Location
    Seattle WA
    Posts
    1,253
    Post Likes

    CFM Recommendations for Spray Tanning Room

    Hi guys, I went on a call for a salon that is complaining that the spray tan room does not ventilate well enough. They have 2 6" exhaust fans that do not work worth a crap. The room is about 6'x17' and they use some sort of air compressor contraption that sprays this nasty orange spray tan stuff. What do you think would be the right fan to remove this stuff from the air. I would also need make up air as well, the room is pretty tight. Also, the existing fans are 120v run off of a 20a circuit, I would like to be able to re-use the circuits, 1 for the exhaust and 1 for the make up air. Depending on the CFM for the fan I may not need a makeup air fan, an electric dampered combustion air doohickey might work. Opinions?
    America; first we fight for our freedom,
    then we make laws to take it away.

    -Alfred E Newman

  2. #2
    Join Date
    Aug 2012
    Location
    Ocala, FL
    Posts
    330
    Post Likes
    How many CFM of supply/return/exhaust air do you currently have? You want the room to be net negative on airflow so the odors don't escape the room. Makeup air would be at least partially supplied by your supply if there is enough of it and as you say the room is tight. if you don't have plenty of supply it will end up as a makeup air temp room.

    If you are treating it as a spray booth (like for painting cars) the requirements can be found in NFPA 33. You would need 100 linear feet per minute of exh. air flow and "Makeup air shall be provided at a rate approximately equal to the rate that air is exhausted by the hazardous exhaust system" according to IMC 510.5.5

    Not suggesting you need a spray tan room with an industrial spray booth setup, but the solution lies between there and your existing fart fan.


    Sent from my iPad using Tapatalk HD

  3. #3
    Join Date
    Jun 2011
    Location
    Seattle WA
    Posts
    1,253
    Post Likes
    Thread Starter
    Thanks for the reply. It wont need paint booth exhaust for sure. I was thinking around 400CFM but I'm just not sure.
    America; first we fight for our freedom,
    then we make laws to take it away.

    -Alfred E Newman

  4. #4
    Join Date
    Aug 2012
    Location
    Ocala, FL
    Posts
    330
    Post Likes
    I would be looking at Loren Cook AC type fans. They are centrifuge type fans and can go through the wall or roof. If you get one a bit larger than the 400cfm and set it up with a potentiometer you can dial it up or back based on their needs.

  5. #5
    Join Date
    May 2005
    Location
    Lubbock Texas
    Posts
    778
    Post Likes
    I did one many moons ago and dropped a return in the space with a merv 13 filter I think I was running about 500cfm. For whats its worth its been operating like that for over 12 years with no issues.
    The premise of ventilation is that the OA is clean or of sufficient quality to be used for dilution. Traditional ventilation is somewhat being threatened by the fact that the EPA is changing the requirements for outdoor air quality which is creating non-attainment zones in what is now becoming a significant portion of the country. That means that buildings in those areas will need to clean up the OA before they bring it into the building.
    www.genesisair.com
    Genesis Air Inc.

  6. #6
    Join Date
    Jun 2011
    Location
    Seattle WA
    Posts
    1,253
    Post Likes
    Thread Starter
    Quote Originally Posted by Pete838 View Post
    I would be looking at Loren Cook AC type fans. They are centrifuge type fans and can go through the wall or roof. If you get one a bit larger than the 400cfm and set it up with a potentiometer you can dial it up or back based on their needs.
    Thanks, any ideas for make up air?
    America; first we fight for our freedom,
    then we make laws to take it away.

    -Alfred E Newman

  7. #7
    Join Date
    Aug 2012
    Location
    Ocala, FL
    Posts
    330
    Post Likes
    Quote Originally Posted by LibertyTree View Post
    Thanks, any ideas for make up air?
    Can you dump conditioned air into it on the opposite end of the long space? A straight OA makeup fan is going to make that room really uncomfortable 10 months out of the year. The air would be outside temp unless you were to condition it, and that's big $ for such a small project..unless your client has deep pockets and wants to do it "right". Chances are if the building is big enough and not extremely tight you're getting enough OA infiltration anyway.


    Sent from my iPad using Tapatalk HD

  8. #8
    Join Date
    Jun 2011
    Location
    Seattle WA
    Posts
    1,253
    Post Likes
    Thread Starter
    Quote Originally Posted by Pete838 View Post
    Can you dump conditioned air into it on the opposite end of the long space? A straight OA makeup fan is going to make that room really uncomfortable 10 months out of the year. The air would be outside temp unless you were to condition it, and that's big $ for such a small project..unless your client has deep pockets and wants to do it "right". Chances are if the building is big enough and not extremely tight you're getting enough OA infiltration anyway.


    Sent from my iPad using Tapatalk HD
    Thanks for the reply. The building is a pile of crap. The owner is willing to spend a reasonable amount but I'm certain there wont be an HRV or anything of the sort going in... I think there is a floor register in the room but I'm sure its putting out 150CFM at best so it wont match the new fan at all. It is pretty tight too. Plus what happens if the furnace doesn't happen to be running when the fan turns on. There is certainly a dilemma here. I wonder if I could run a wire to the G terminal on the furnace from an electronic make up air damper that would force the furnace fan on when the damper opens? 150cfm might be better than nothing.
    America; first we fight for our freedom,
    then we make laws to take it away.

    -Alfred E Newman

  9. #9
    Join Date
    Aug 2012
    Location
    Ocala, FL
    Posts
    330
    Post Likes
    The simpler solution might be to just switch the thermostat to FAN-ON during occupied hours... Assuming you can dump enough supply air in there.
    interlocking the blower fan with the exh. fan (or the opposite) would ensure nobody tampered with the T-stat.

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •