    Refrigerant leaks in eighteen RTU's - acidic condensate

    This has got to be an air quality issue:

    So we have a customer - a moving company - that owns an A/C storage warehouse with eighteen rtu's. Every one of them has refrigerant leaks. Most of the units are about eight years old, but refrigerant is leaking even in units that are 1-2 years old. There is a noticeable accelerated corrosion on the evaporator end plates and drain pans.

    We have just received results from water tests we did on the condensate, and the pH is between 4.3 and 4.8. Pretty low, right? Has anybody seen this before? What might cause it?

    The only lead I have is that I think they are running propane forklifts inside. Could the exhaust somehow make the condensate acidic?

    -Joshua

  2. #2
    Join Date
    Jul 2010
    Location
    nebraska
    Posts
    2,810
    Post Likes
    That's probably a good guess. I've seen the condensate from 90% furnaces eat through copper drain lines and etch 1/4" gouges in concrete.Also saw vtk's vented backwards so the exhaust sucked right back into the intake, rusted out heat exchangers in less than 3 years. Seems like tin end plates wouldn't stand a chance.

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •