Results 14 to 24 of 24
Thread: Need help ASAP
-
09-03-2012, 03:45 PM #14
If a compressor won't restart immediately following a brief power interruption (and there is no time delay protection either via the thermostat or at the unit itself), the compressor likely tripped its internal overload due to the system not having time to equalize prior to restarting the compressor.
To prevent this from happening again, you can either a)Get a thermostat with a built-in time delay for the compressor (will only hold the Y call when it senses power loss), or b) get a time delay (delay-on-break) installed in the condenser, or c) get a start-assist kit installed on the compressor, or d) don't run your system during thunderstorms (not always possible if a storm occurs when you're not home).
Bottom line sans any of the above: do not try to immediately restart your unit following a brief power loss."In this house we obey the laws of thermodynamics!"
- Homer Simpson
-
09-03-2012, 04:35 PM #15
-
09-03-2012, 04:38 PM #16
-
09-03-2012, 05:39 PM #17
-
09-04-2012, 06:37 AM #18
-
09-04-2012, 07:06 AM #19
Ahhh...I just don't know how relevant that info was.
Post model of outdoor unit. Didn't they change whole unit already once?
Scroll compressor can restrart right away.
-
09-04-2012, 08:03 AM #20
This did not escape me. In his case, however, his description had all the signs of a short cycled compressor, scroll or not. If there's a PTC and/or weak run cap involved, or reduced voltage supply (common during high demand times), I can see a scroll motor stalling due to the comp being quickly cycled off and on.
"In this house we obey the laws of thermodynamics!"
- Homer Simpson
-
09-04-2012, 08:05 AM #21
Professional Member*
- Join Date
- Mar 2009
- Location
- Mount Holly, NC
- Posts
- 1,614
I'd not recommend a supco start assist...
the kickstart is the least expensive I'd recommend, but the 521 is an excellent model. be sure they install the correct one for your size equipment. of course, the best is shutting off the ac during storms. keep in mind, many battery backed up digital stats do not keep the a/c on delay from a brief power outage...
a delay on break device will.The TRUE highest cost system is the system not installed properly...
The three big summer hearththrobs...
Mel Gibson
Dwane Johnson
The A/C repairman
-
09-04-2012, 08:07 AM #22
Professional Member*
- Join Date
- Mar 2009
- Location
- Mount Holly, NC
- Posts
- 1,614
also, the damage from short cycle is not the worst that can happen in a storm... lightning surge can fry the compressor completely even if the strike is miles away.
The TRUE highest cost system is the system not installed properly...
The three big summer hearththrobs...
Mel Gibson
Dwane Johnson
The A/C repairman
-
09-04-2012, 08:31 AM #23
He said entire od unit was dead. No fan. No compressor.
Post m# of your unit. It may already have short cycle protection.
-
09-04-2012, 09:34 AM #24
I will post this afternoon after work. Thx ahead. This website is the bomb


Reply With Quote