    TXV and Overloaded Evaporator
    How does a TXV handle an overloaded evaporator? Is there some type of "limit" to the amount of freon a TXV will allow to go through regardless of load conditions? Overloaded evaporators tend to happen during recovery from thermostat setback/high humidity etc.
    Nov 2007
    Mississippi
    It can only open to "wide open".
    Tallahassee, FL
    The suction pressure sensor (equalizer) force acts to close the valve.
    This is how hard shut off valves work.
    The maximum limit of a TXV is its rated capacity, and the power element in the case of a MOP rated valve. The capacity of a TXV shouldn't be significantly greater than the design cooling capacity of the system.