    How does a TXV handle an overloaded evaporator? Is there some type of "limit" to the amount of freon a TXV will allow to go through regardless of load conditions? Overloaded evaporators tend to happen during recovery from thermostat setback/high humidity etc.

  2. #2
    Join Date
    Nov 2007
    Location
    Mississippi
    Posts
    1,423
    Post Likes
    It can only open to "wide open".

  3. #3
    Join Date
    Feb 2009
    Location
    Tallahassee, FL
    Posts
    6,055
    Post Likes
    The suction pressure sensor (equalizer) force acts to close the valve.

    This is how hard shut off valves work.

  4. #4
    Join Date
    Aug 2012
    Posts
    39
    Post Likes
    Quote Originally Posted by 54regcab View Post
    How does a TXV handle an overloaded evaporator? Is there some type of "limit" to the amount of freon a TXV will allow to go through regardless of load conditions? Overloaded evaporators tend to happen during recovery from thermostat setback/high humidity etc.
    The maximum limit of a TXV is its rated capacity, and the power element in the case of a MOP rated valve. The capacity of a TXV shouldn't be significantly greater than the design cooling capacity of the system.