Thread: Replaced my A/C this weekend, results of downsizing by 1/3.

  1. #1
    Join Date
    Jun 2001
    Location
    Moore, Oklahoma, United States
    Posts
    4,648
    Post Likes

    Replaced my A/C this weekend, results of downsizing by 1/3.

    Recently my 13 yr old Carrier A/C devolved a leak and I chose to replace the system rather than track down the leak and repair the coil. I had been reading about doing manual J calculations and how contractors are scared to death to undersize. I had been talking to co-workers about this and it's an uphill battle getting them to think different than 1 ton per 500sq ft. So I decided to take confidence in correct sizing and "put my money where my mouth is" and install a correctly sized A/C.

    House: 1587sq ft located in Oklahoma City, built 1999.
    OLD A/C: Carrier 3 ton 12SEER system original to the house.
    New Condenser: Thermalzone (Rebadged Rheem/Ruud 2 ton 14.5 SEER) 2 ton 14.5 SEER.
    New coil: 2 ton RFCL 13-16SEER with TXV http://www.rheem.com/documents/rcfl-...ication-sheets

    Results:
    Temperature the old unit cycled until it waswas above 105, clearly oversized for our area. New 2 ton unit can keep 76F inside with a 100 degree outdoor temperature, but runs continuously to do so.
    Humidity is HIGHER in the day with the new system even though it runs more. 45% vs. 40% for the old system. I've already reduced the 3 ton blower to it's lowest speed.
    As a test I've captured the condensate in a bucket to measure humidity removal. The 3 ton system with piston metering pulled more humidity by day, less by night. The new TXV system pulls more humidity at night than day. Both units keep humidity about 45% at night.
    Power Old unit consumed 3,000 to 3,500 watts depending on outside temperature. New unit consumes 1,800 to 2,500watts depending on outdoor temperature. Power use is on my in home wattmeter and includes blower consumption.
    Delta T Old unit got about 18 degrees most of the time, day or night. New unit gets 14 degrees in day, 18 degrees at night. Keep in mind the blower speed was lowered when the new A/C was installed.
    Cycle time Cycles were running about 6 minutes with the old unit, new unit runs about 8-10 minutes per cycle.
    Noise New unit is WAY quieter, both units have 8 pole motors. Scroll compressor can barely be heard compared to the recip compressor of the old unit. With the new unit you can barely hear the fan, very impressed. Neighbor still has his 3 ton builder unit with the 1125 RPM fan and it's twice as loud as my old unit.

    The coworker that helped me install it was impressed with how quiet the unit is and how much cooling it put out considering that it's only a 2 ton. He was a bit skeptical that the 2 ton could pull it off, but it's doing so with flying colors IMHO. So, believe the load calculations and don't fudge the input number to get the result you want. Yes they may seem low, but they DO work !!!

  2. #2
    Join Date
    Aug 2012
    Location
    Palmyra, Missouri, United States
    Posts
    224
    Post Likes
    new unit 14 degree split. sounds terrible.

  3. #3
    Join Date
    Jun 2001
    Location
    Moore, Oklahoma, United States
    Posts
    4,648
    Post Likes
    Thread Starter
    Quote Originally Posted by drife678 View Post
    new unit 14 degree split. sounds terrible.
    Split is measured return grille to supply, not across the coil itself. Don't know how much of a difference it makes.

  4. #4
    Join Date
    May 2000
    Location
    Indianapolis, IN, USA
    Posts
    42,886
    Post Likes
    Sounds like a lot of duct gain chewing up a good chunck of your capacity. I'd look into stopping that.

  5. #5
    Join Date
    Aug 2012
    Location
    Palmyra, Missouri, United States
    Posts
    224
    Post Likes
    Id like to see a minimum of 18 degree split

  6. #6
    Join Date
    Feb 2009
    Location
    Tallahassee, FL
    Posts
    6,217
    Post Likes
    Possibly why the humidity rises with the increased run times. Infiltration?

  7. #7
    Join Date
    Nov 2007
    Location
    Mississippi
    Posts
    1,571
    Post Likes
    14 degrees delta t could be on target. All acording on indoor dry bulb and wet bulb. There are charts for target delta t.

  8. #8
    Join Date
    Dec 2003
    Posts
    2,851
    Post Likes
    Maybe you are moving a little to much air? You said you lowered the fan speed, but it sounds like you have more air flow than ideal for 2 tons of cooling. Your rh is dependent on how cold you get the air. Maybe put in a more restrictive filter and see if the rh comes down.

  9. #9
    Join Date
    Jun 2001
    Location
    Moore, Oklahoma, United States
    Posts
    4,648
    Post Likes
    Thread Starter
    To be fair it was over 100 degrees when I took the daytime delta T reading, it's 5 degrees above design conditions for our area. I would think if I had duct leakage issues it would have affected the 3 ton units day/night offset also. I did notice the suction line felt warm when I took the daytime test on the new unit. I need to do a test with real thermometers across the coil, I question the accuracy of the infrared temperature gun. I'm thinking airflow is probably a little high even on the lowest speed, the 45% humidity is acceptable but I'm curious to see what happens when it's cool/rainy.

  10. #10
    Join Date
    Aug 2012
    Posts
    18
    Post Likes
    Yeah, I wouldn't trust an infrared to do a Delta T. They only measure the surface temp of what you point it at. You need the actual air temp.

  11. #11
    Join Date
    Jun 2003
    Location
    Madison, WI/Cape Coral, FL
    Posts
    12,042
    Post Likes
    Quote Originally Posted by 54regcab View Post
    To be fair it was over 100 degrees when I took the daytime delta T reading, it's 5 degrees above design conditions for our area. I would think if I had duct leakage issues it would have affected the 3 ton units day/night offset also. I did notice the suction line felt warm when I took the daytime test on the new unit. I need to do a test with real thermometers across the coil, I question the accuracy of the infrared temperature gun. I'm thinking airflow is probably a little high even on the lowest speed, the 45% humidity is acceptable but I'm curious to see what happens when it's cool/rainy.
    76^R, 45%RH equals a 52^F dew point. This equates to 45-47^F coil temp. This is very acceptable. Keep us posted on your %RH when the cooling loads decline with high outdoor dew points. Low/no cooling loads with +50^F outdoor dew points will raise the indoor %RH. How much moisture are you removing during a typical day or night? The amount of infiltrating/ventilation air with its moistue plus the moisture from the occupants equals the moisture removed by the a/c. If we know the number of occpants and the dew point outside/dewpoint inside, we estimate the amount of fresh air. Most homes do not get enough fresh during calm summer weather.
    If you want adequate fresh air throughout the +55^F dew point weather, you will need 25-50 lbs of moisture dehumidified from the house. Without a cooling load, a dehumidifier is ideal. For fresh filtered air, a whole house ventilating dehumidifier a good add-on.
    Regards TB
    Bear Rules: Keep our home <50% RH summer, controls mites/mold and very comfortable.
    Provide 60-100 cfm of fresh air when occupied to purge indoor pollutants and keep window dry during cold weather. T-stat setup/setback +8 hrs. saves energy
    Use +Merv 10 air filter. -Don't forget the "Golden Rule"

  12. #12
    Join Date
    Jun 2001
    Location
    Moore, Oklahoma, United States
    Posts
    4,648
    Post Likes
    Thread Starter
    The old 3ton A/C filled a 3.5 gallon bucket about every 24hrs. The new 2ton A/C takes about 36hours to fill the bucket. However the weather has been unusually dry lately. Low side pressure varies by outdoor temperature, but was 130 @ 90f outside when we started the system. Looks a lot like the 45-47 degree coil you mentioned.

    Calm doesn't exist in Oklahoma, there's almost always some breeze blowing. We have some of the highest average wind speeds in the nation. Outdoor dew points have been high 50's, which is low for this time of year. Very dry summer, dew points are more typically in the upper 60's.

  13. #13
    Join Date
    Aug 2012
    Location
    Palmyra, Missouri, United States
    Posts
    224
    Post Likes
    What is ur subcooling

  14. #14
    Join Date
    Jan 2009
    Location
    SE Iowa
    Posts
    5,577
    Post Likes
    You said it was in the attic? Air leakage in the ductwork could be a source. The air leakage may correlate more to runtime than to static pressure and total air flow.

    R22 system just seemd to dehumidify better. I think they just had less surface area and less total mass.

  15. #15
    Join Date
    Jun 2001
    Location
    Moore, Oklahoma, United States
    Posts
    4,648
    Post Likes
    Thread Starter
    The furnace/coil is in the garage, all the ductwork is in the attic. There may be some duct leakage, but it didn't seem to affect the larger A/C as much. The new A/C cools more at night, the old A/C was about the same no matter the temperature. Once temperatures get below 90 the new unit cools about as good as the older unit that was 50% larger. It's almost as the TXV is feeding more at lower outside temperatures, the piston on the old A/C seemed to feed LESS at lower outdoor temperatures. Humidity is holding steady in the mid 40's, even with the rain we had last night.

    No 410a was added, just used the factory charge, 25' lineset. It might be a little low but I don't hear any "flash gas" at the TXV. The guy helping me do the install seemed surprised at the size of he coil for begin a 2 ton. Lots of surface area, but it's a 2 row coil with 1/4" tubing instead of the standard 3 rows of 3/8" tubes for the freon. Coil "slab" was about 1/2 the thickness of the old 3 ton coil.

  16. #16
    Join Date
    Feb 2009
    Location
    Tallahassee, FL
    Posts
    6,217
    Post Likes
    What you stated about txv vs piston is precisely what you should notice between txv and piston.

    The cooler outside temps lowered head psi on old system which meant less refrigerant through hole.

    The txv opens up more to allow capacity at wider range of id/od temps. By far a superior device.

    Go ahead and take some readings next 100 afternoon.

    Accurate ll temp/pressure and ambient temp

    Record vapor line temp leaving indoor coil as well as condensor.

    Lets make sure valve has solid column under conditions.

  17. #17
    Join Date
    Feb 2009
    Location
    Tallahassee, FL
    Posts
    6,217
    Post Likes
    Not to mention the added efficiency and protection of compressor hard shut off txv offers

  18. #18
    Join Date
    Jun 2005
    Location
    Near Chicago, IL
    Posts
    3,372
    Post Likes
    Unsealed ductwork in an attic is a killer- it can wipe out 30% of your capacity.

    You should check your return temperature at a far room (in the room, next to the grille) and again at the unit. Do the same for the supply.

    Odds are, you will see high superheat with your gauges.

    The resi stuff I have worked with is all pre-charged for a 15' lineset, so if the OEM got it right, you are low on charge.

    Even builders level equipment needs to be charged properly, and higher SEER stuff is even more picky.

  19. #19
    Join Date
    Oct 2010
    Location
    Anderson, South Carolina, United States
    Posts
    21,021
    Post Likes
    If the duct was sized for 1200 cfm and now you have 800cfm the velocity is lower so the cooled air stays in the ducts longer and gains more heat from the attic, this could be the reason for the 14f drop vs 18f drop.

  20. #20
    Join Date
    Feb 2009
    Location
    Tallahassee, FL
    Posts
    6,217
    Post Likes
    Quote Originally Posted by jtrammel View Post
    If the duct was sized for 1200 cfm and now you have 800cfm the velocity is lower so the cooled air stays in the ducts longer and gains more heat from the attic, this could be the reason for the 14f drop vs 18f drop.
    Good point.

+ Reply to Thread
Page 1 of 6 123456 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •