    electric furnace no duct work

    I mounted a Coleman electric furnace in the basement of my camp to keep my pipes from freezing in
    the winter if the mini-split can't maintain 50 degrees.I am not using any ductwork as the basement is just one large area.
    Is there any thing I should do as far as setting the fan speed? Do I need to create static pressure because there is no ductwork?
    Any tips to optimizing this simple set up would be welcomed.

  2. #2
    Join Date
    Apr 2006
    Location
    Barrie Ontario
    Posts
    318
    Post Likes
    With no plenum isnt the strips exposed

  3. #3
    Join Date
    Sep 2012
    Posts
    9
    Post Likes
    Thread Starter
    Quote Originally Posted by turkey View Post
    With no plenum isnt the strips exposed
    Yes ,but they are 8ft. off the floor.I will add expanded metal to keep idiots out.

  4. #4
    Join Date
    Sep 2012
    Posts
    9
    Post Likes
    Thread Starter
    This is model Eb17b coleman furnace made for a house trailer.

  5. #5
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Its not approved for horizontal installation.

  6. #6
    Join Date
    Sep 2012
    Posts
    9
    Post Likes
    Thread Starter
    I changed the mounting so it is now a downflow unit .Is there anything else I should know?

  7. #7
    Join Date
    May 2012
    Location
    Upper Michigan
    Posts
    3,588
    Post Likes
    Quote Originally Posted by bobsat View Post
    Yes ,but they are 8ft. off the floor.I will add expanded metal to keep idiots out.
    How are you going to roast marshmallows at camp now?

  8. #8
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    I would probably run a trunk or make an ell to direct the air to the far end, so as to have a slightly better temp distribution.

  9. #9
    Join Date
    Sep 2012
    Posts
    9
    Post Likes
    Thread Starter
    Thanks for your reply.

  10. #10
    Join Date
    Jan 2009
    Location
    SE Iowa
    Posts
    5,577
    Post Likes
    Just curous, but for freeze protection, why not use something simplier, cheaper and with less moving parts like baseboard heaters or a wall mounted electric unit heater? You don;t need much if any airflwo just for freeze protection.

  11. #11
    Join Date
    Sep 2012
    Posts
    9
    Post Likes
    Thread Starter
    I only paid $150 for the furnace.Trying to keep the first floor, 896 sq. ft.,10 ft ceilings, poured concrete and the 2nd floor,stick built,which is very well insulated from freezing.I figured I need 40k btus.The first floor is in a flood zone so trying to keep every thing down there as high as possible.

  12. #12
    Join Date
    Jan 2009
    Location
    SE Iowa
    Posts
    5,577
    Post Likes
    Where are you at location wise? For just freeze protection, you BTU requirements can be roughly 1/2 that of comfort heating. You only need to keep it 35-40F. If most of that is a basement, where the ground temps are above 40F, then now it takes even less. You probably only need 10k BTU's. I just ran adjsuted the number for the basic laod calculation in my home and at 3500sqft and a lot of windows, it would only need 50k BTU's for freeze protection of 2 floors and a basement.

    ... but $150 is pretty cheap.

  13. #13
    Join Date
    Sep 2012
    Posts
    9
    Post Likes
    Thread Starter
    I am in central Pennsylvania.None of it is basement(underground).The first floor is poured concrete(8" thick R value about .8 to 2)The 2nd floor is 2x6 walls,no insulation between 1st and 2nd floor to allow heat from first floor to go to the 2nd floor.Electric furnace is in 1st floor.I understand what you are telling me needing less btu's to protect against freeze.The furnace presented itself and I went that direction.Thank's for your replies I appreciate the help as HVAC is not my forte.

  14. #14
    Join Date
    Oct 2010
    Location
    Anderson, South Carolina, United States
    Posts
    21,021
    Post Likes
    As stated above I would make an ell or tee to direct airflow in different directions other than that I see no problems other than high utility bill but that beats busted pipes. Check temp at furthest point when it gets cold and see how low you can set the temp to stay above freezing to keep your electric bill as low as possible

  15. #15
    Join Date
    Sep 2012
    Posts
    9
    Post Likes
    Thread Starter
    The electric furnace will only be an emergency back up to the mini-split heat pump system which the spec sheet says is good down to
    down to 0 degree f.It usually does'nt get to zero here very much and if it does it does'nt stay there long.The electric bill should not be too bad with the heat pump.

  16. #16
    Join Date
    Jan 2009
    Location
    SE Iowa
    Posts
    5,577
    Post Likes
    The minisplit will still function below 0F, but capacity will be greatly reduced, and it won't be a much more efficeint that heat strips depending on outdoor humidity levels... but likely enouhg capacity for freeze protection.

    However, having a reliable heat soruce for emergency back-up isn't a bad idea. Getting it for $150, makes it a simple choice, I can't disagree.

    Just make sure all electrical codes are followed in terms of proper wire size, breaker size, etc. A fire from improper electrical will do a LOT more damage than a busted water line. IF you're going ot be away for a period of time in winter, you can also just winterize the place using antifreeze in traps and draining the plumbing. You can do that in 20-30 minutes in most cases.

  17. #17
    Join Date
    Sep 2012
    Posts
    9
    Post Likes
    Thread Starter
    I will probably use the cabin every other week in the winter as it's only 14 miles from my home.The only part I dont like about winterizing is making sure the dishwasher,clotheswasher and icemaker in the fridge are done properly.
    I have been looking for remote temperature monitor for use with a pre-paid cell phone to keep tabs on things about $190 is as cheap as I have found.Of course it is fairly close so I can just drive down and check.
    Thanks again for all the helpful advice. Bob

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •