    If one wishes to use G61V blower in such a way as to not abuse it, what would you say is the max number of hours/day a blower should be running?

    House will be 54,000 cubic feet. HEPA-60 runs at 500cfm. It will take 108 minutes to filter inside air once. Would I be abusing blower or have a premature death of blower if I run it for extended period of time on a daily basis?

    Thanks for your help.

  2. #2
    Join Date
    Mar 2005
    Location
    burlington county n.j.
    Posts
    9,881
    Post Likes
    with v drive blower you could let it run 24-7. most of the strain on a motor is starting.

  3. #3
    Join Date
    Dec 2002
    Location
    Rochester, MN
    Posts
    5,307
    Post Likes
    You are better to leave the fan in "ON" at all times.. They motor is a variable speed DC motor, and runs very cheap vs the old standard motor. Also, the motor will last longer when it's running steady, than the stop and go.

    Only time you may want to put the fan in "AUTO" is in the summer. If the house feels muggy in the summer, switch it to auto.. otherwise, if you felt fine, then leave it on.

  4. #4
    Join Date
    Sep 2006
    Posts
    149
    Post Likes
    Thread Starter

    Smile

    Thanks for the replies

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •