So before you had no A/C coil? That's a 24" furnace if I remember right. They likely put a narrow coil above it and really blocking airflow. What capacity A/C?
-
09-05-2012, 04:47 PM #15
Regular Guest
- Join Date
- Sep 2012
- Posts
- 14
A/C coil was put in in May. It seems that the old blower was able to move air better somehow though. For the few cool mornings we had in May after installation, the heat was fine. So problems didn't crop up untl now.
It is a 4 ton Gibson.
-
09-05-2012, 04:57 PM #16
So they changed out the motor without determining what was causing the problem?
The blower wheel blades & the A-Coil are two of the first things you check when there is low airflow & blower motors overheating.
A lint blocked A-Coil will cause the blower wheel to unload & that plus the lack of airflow over the motor will cause it to overheat & quit running.
This situation appears to be a mismatched application...Last edited by udarrell; 09-05-2012 at 05:23 PM. Reason: mismatched application...
AOP Forum Rules:
Rules for Posting
Rules For Equipment Owners
Equipment Owners Find a Contractor HERE!
udarrell
-
09-05-2012, 05:04 PM #17
Nordyne makes a 24" wide 4 ton coil. Just adding a coil to a system shouldn't cut airflow enough that you can't use it. Unless they used a 17" coil over the 24" furnace but if it is a matched coil, there isn't a 17" wide 4 ton from Nordyne.
There's still something fishy. 1/2 horse when it should be a 3/4 horse?
Can you take any pictures?
-
09-05-2012, 06:07 PM #18
Regular Guest
- Join Date
- Sep 2012
- Posts
- 14
Yeah...likely a mismatched application.
So matching with a proper furnace is an answer?
I confirmed the motor is 3/4 horse. I can take pictures...you mean of the inside of the A/C plenum?
-
09-05-2012, 07:39 PM #19
Professional Member*
- Join Date
- Jul 2006
- Location
- Virginia
- Posts
- 3,716
The contractor that installed the coil should fix it
The governent can not give anything to someone that it has not first taken from someone else
-
09-05-2012, 08:08 PM #20
Take a picture of the furnace and plenum above it.
-
09-05-2012, 08:45 PM #21
Regular Guest
- Join Date
- Sep 2012
- Posts
- 14
-
09-05-2012, 08:49 PM #22
Regular Guest
- Join Date
- Sep 2012
- Posts
- 14
Agree...I'll be trying to work it through with him. I think he's thinking the only way to fix it is to right size the furnace.
-
09-05-2012, 09:18 PM #23
wow....ductwork looks like a problem. cant tell because im not there but i suspect it is. i also see a barometric damper on the furnace. there may be a chance that someone who was properly trained in combustion installed it and tuned that furnace.
-
09-05-2012, 09:38 PM #24
Ductwork looks like a problem, can you post a pic of duct coming off of coil
-
09-05-2012, 10:15 PM #25
Professional Member*
- Join Date
- Jul 2006
- Location
- Virginia
- Posts
- 3,716
I wonder if they landed the y wire on the terminal strip or just wire nuted the y wires together causing the blower to run in low speed
The governent can not give anything to someone that it has not first taken from someone else
-
09-06-2012, 06:39 AM #26
Regular Guest
- Join Date
- Sep 2012
- Posts
- 14


Reply With Quote