    tracer summitt version 17

    I recently had an issue where my trane ahu discharge air sensor reading at the front end was out of range (ten degrees below actual) despite an acceptable ohm value at a given temp (i checked it with the charts for a 10k type 2 sensor), i even swapped it with the return discharge air sensor (same part#) i went into tracer summit anolog inputs and attempeted to offset sensor, and noticed no change at graphic, Do i need rover to make change? Fyi there is an mp580 on ahu.

  2. #2
    Join Date
    Mar 2011
    Location
    North Carolina Piedmont Area
    Posts
    452
    Have you verified that the SAS is referencing the correct sensor. I would first go to the graphic editor, click on the sensor readout and confirm its reference is set correctly.

  3. #3
    ill check that out thanks