tracer summitt version 17
I recently had an issue where my trane ahu discharge air sensor reading at the front end was out of range (ten degrees below actual) despite an acceptable ohm value at a given temp (i checked it with the charts for a 10k type 2 sensor), i even swapped it with the return discharge air sensor (same part#) i went into tracer summit anolog inputs and attempeted to offset sensor, and noticed no change at graphic, Do i need rover to make change? Fyi there is an mp580 on ahu.
-
09-03-2012, 11:45 PM #2
Professional Member
- Join Date
- Mar 2011
- Location
- North Carolina Piedmont Area
- Posts
- 293
Have you verified that the SAS is referencing the correct sensor. I would first go to the graphic editor, click on the sensor readout and confirm its reference is set correctly.
-
09-06-2012, 10:41 PM #3
Regular Guest
- Join Date
- Aug 2012
- Posts
- 6
ill check that out thanks