Results 1 to 6 of 6
Thread: New install question..
09-04-2012, 11:09 AM #1
We're installing 2 new Trane split heat pumps. Twe090d 7-1/2 and twe120d 10 ton with matching indoor ahu's. I'm reading the install manual and noticed that Trane recommends 5/8 liquid for the 7-1/2 and 1/2" for the 10 ton. I can't see why they'd want a larger liquid line on the smaller capacity unit. Any thoughts??? TIA Fitz
Sent from my iPhone using TapatalkChaos equals cash$$$
09-05-2012, 10:03 PM #2
I think I'm going to just run 5/8 on both systems. Total line length is maybe 30'...
09-05-2012, 10:52 PM #3
Weird.. Im currently doin 3 10ton carriers, and according to there sizing chart they want 1/2" which to me seemed small, but i talked to carrier and they said 1/2, so i went with it. Im assuming this is 410
09-05-2012, 10:52 PM #4
5/8 will be fine tho
09-05-2012, 11:10 PM #5
- Mar 2011
- North Carolina Piedmont Area
- 291
Could it be a mistake in the spec. Is the suction also 1-3/8" for both? It doesn't make sense either way.
It is possible that they are concerned about the velocity and proper oil return.
I have a piping chart which is in Excel format. I will try to convert it and upload next post. If you want I can email it maybe.
09-06-2012, 09:00 PM #6
New 410 system. Yes both suctions are 1-3/8. Install is this weekend. I ordered 5/8 for both systems.