06-12-2012, 11:10 AM #1
York Chiller weird alarms
Model YTH1A4E1CNJ
Weird alarms coming in, chiller will not run it. appears that there is a problem with the diagnostic board. The faults that show up keep changing along with the dates of the faults. Then the fault history will clear and start over again. All of this happens without the chiller even running. Now I am back to my original theory that it caught a stray power surge caused by the storms that went through here over the weekend.
Any thoughts?
-
06-12-2012, 09:21 PM #2
Professional Member
- Join Date
- Jun 2012
- Location
- so cal
- Posts
- 21
check for short on a sensor or transducer. also check all ribbons and wire connections are pushed in. i just had a yt fail because of this.
-
06-14-2012, 12:53 PM #3
-
06-18-2012, 11:51 AM #4
Update... I did check all connections and everything went back to working great. I cant pin point which wire or connection, but i did find a few loose. I think that was it...Thanks for the tip!!
-
07-10-2012, 11:44 AM #5
Regular Guest
- Join Date
- Apr 2012
- Location
- So. Fl.
- Posts
- 55
Depending on York chiller type, there is an external box located over the cooler barrel,weather proof. Has all temp./safety wires in it,I have found rubbed/cut wiring inside giving false alarms,open it up and replace all wirenuts. Should make problems stop at once,
With severe weather could have become wet inside.
-
08-10-2012, 01:14 AM #6
New issues, The system ran great for a awhile than shut down. Power down and up , screen passes dia. but the unit will not run. I see the red light on MB CR18 failure. any ideas?
-
08-10-2012, 03:52 AM #7
Professional Member
- Join Date
- Jan 2011
- Posts
- 676
The red light doesn't necessarily mean anything. The manual tells of its function. I think almost every board I've seen has the red light illuminated. Let's get specific...from the M/N it should be an Optiview panel. Is it the original microboard 031-01730-xxx? What do the two lines on the top left of the Optiview home screen say?
-
08-14-2012, 03:30 PM #8
00000005.jpg00000001.jpg
check this out not sure of the last few numbers 000 or 040....
-
08-14-2012, 04:19 PM #9
Professional Member
- Join Date
- Jan 2011
- Posts
- 676
O.K., you have a 031-01730-000 board. According to the second photo you are in the local mode and service level and the system is stopped. What happens when you push the rocker switch on the panel to the start/run position? Does the system go into pre-lube? What does the screen (top two lines) say then. In the photo you've shown indicates the rocker switch is off.
-
08-15-2012, 09:45 AM #10
-
08-15-2012, 10:27 AM #11
Professional Member
- Join Date
- Jan 2011
- Posts
- 676
What have you done to troubleshoot the circuit from the 120 VAC on the terminal block to and through the rocker switch? Start there and follow that path until you find out why you aren't getting power to the point of initiating a run command.
-
08-15-2012, 11:11 AM #12
-
08-16-2012, 08:34 PM #13
Professional Member
- Join Date
- Jan 2011
- Posts
- 676


Reply With Quote