    RH Humidity Problems - Help!

    I'll try to keep this as short as possible.

    I have a 3,000 sq ft ranch style home in western Canada. We had new AC system installed 5 years ago, including ductwork in the attic of our home. 2 AC units were installed, (both 3 ton). One provides cooling for the LR/DR/Hallways and Den and the second does the bedroom wing. From day one we got extremely cold air and excessive cycling. In addition, the RH was never lower than 62%. After some discussion with the contractor, it was discovered that the manual J called for 4.2 tons (Supplier of the equipment did the manual J but didn't provide it to the contractor, just the recommendation for 6 tons) . The contractor discovered that the air handler for the LR unit was sized for a 4 Ton unit as was the duct work. The bedroom air handler was for a 3 ton and the ductwork was also sized for a 3 ton.

    After a meeting last month the contractor said the following was the fix:

    1. Remove the bedroom 3 ton unit and replace with a 1.5 ton unit and matching 1.5 ton air handler;
    2. Remove the 4 Ton air handler from the LR unit and discard. Use the 3 Ton air handler (from the bedroom unit) connecting to the 3 ton outdoor unit - existing (this set up will give 4.5 ton of cooling capacity);
    3. Balance air flow and adjust ECM air handlers to optimum speed.

    With this new setup, cooling comfort has improved. Airflow has been reduced significantly and we no longer feel blasts of cool air (the "meat locker" effect). There was some discussion during the recent installation that we might not have enough "static pressure" with the new setup given that the ductwork was 3 ton for a now 1.5 unit compressor (bedrooms) and 4 ton for 3 ton compressor (LR/DR/Den). We had no further discussion on this.

    I had asked the contractor to make sure they sized the new units correctly and asked that they upgrade me to 2 stage units. I reasoned that in off peak running times, the Rheem units running in stage 1 would dehumidify without lowering the temperature much below the set point on the thermostat. They said the cost would be excessive as their remediation plan involved using some of the same equipment, wiring, setup, etc.

    I don't know where to turn at this point for a solution. I feel the RH of 63% when the outdoor is 60%RH (+28C) is too high. Crackers in our cupboards are soft and it just feels "wet" in the house.

    Anyone have ideas as to what is wrong with out setup and what it will take to correct it?

    Thanks,

    kayjh

  2. #2
    Join Date
    Oct 2011
    Location
    NJ
    Posts
    149
    Post Likes
    The humidity hasn't improved when the HVAC units were changed for the proper sizes? This should have allowed longer run times and better dehumidification.

  3. #3
    Join Date
    Jun 2006
    Posts
    96
    Post Likes
    Thread Starter
    Quote Originally Posted by vangoghsear View Post
    The humidity hasn't improved when the HVAC units were changed for the proper sizes? This should have allowed longer run times and better dehumidification.
    That is what I though.

  4. #4
    Join Date
    May 2000
    Location
    Indianapolis, IN, USA
    Posts
    42,886
    Post Likes
    Got model #s for the indoor & outdoor units?

    What controls (thermostat) do you have on these?

    Are both air handlers variable speed? Do you run the fan constantly?

    Is the humidity high on a hot day or just in mild weather and overnight when the units don't run much?

  5. #5
    Join Date
    Jun 2006
    Posts
    96
    Post Likes
    Thread Starter
    Quote Originally Posted by BaldLoonie View Post
    Got model #s for the indoor & outdoor units?

    What controls (thermostat) do you have on these?

    Are both air handlers variable speed? Do you run the fan constantly?

    Is the humidity high on a hot day or just in mild weather and overnight when the units don't run much?
    I don't have the model numbers for the inside and outside units. I can get them (when I get back to the lake), but a trip to the attic is required for the inside unit information and I believe they are now wrapped in 3 layers of insulation to help combat condensation.

    The air movers are ECM type. The 1.5T unit is matched to a Rheem air mover, while the 3 ton unit was matched to a non Rheem air handler (not sure why). THe fans do not run constantly. We find the humidity to be high even on hot days, although I think we are in the high 50's (% RH) under those conditions and 60 - 63% on cooler days when the units are running less.

    Any ideas?

  6. #6
    Join Date
    Nov 2004
    Location
    SW FL
    Posts
    13,328
    Post Likes

    Lightbulb

    Quote Originally Posted by kayjh View Post
    I'll try to keep this as short as possible.

    I have a 3,000 sq ft ranch style home in western Canada. We had new AC system installed 5 years ago, including ductwork in the attic of our home. 2 AC units were installed, (both 3 ton).

    One provides cooling for the LR/DR/Hallways and Den and the second does the bedroom wing. From day one we got extremely cold air and excessive cycling.

    In addition, the RH was never lower than 62%. After some discussion with the contractor, it was discovered that the manual J called for 4.2 tons (Supplier of the equipment did the manual J but didn't provide it to the contractor, just the recommendation for 6 tons) . The contractor discovered that the air handler for the LR unit was sized for a 4 Ton unit as was the duct work. The bedroom air handler was for a 3 ton and the ductwork was also sized for a 3 ton.

    After a meeting last month the contractor said the following was the fix:

    1. Remove the bedroom 3 ton unit and replace with a 1.5 ton unit and matching 1.5 ton air handler;
    2. Remove the 4 Ton air handler from the LR unit and discard. Use the 3 Ton air handler (from the bedroom unit) connecting to the 3 ton outdoor unit - existing (this set up will give 4.5 ton of cooling capacity);
    3. Balance air flow and adjust ECM air handlers to optimum speed.

    With this new setup, cooling comfort has improved. Airflow has been reduced significantly and we no longer feel blasts of cool air (the "meat locker" effect). There was some discussion during the recent installation that we might not have enough "static pressure" with the new setup given that the ductwork was 3 ton for a now 1.5 unit compressor (bedrooms) and 4 ton for 3 ton compressor (LR/DR/Den). We had no further discussion on this.

    I had asked the contractor to make sure they sized the new units correctly and asked that they upgrade me to 2 stage units. I reasoned that in off peak running times, the Rheem units running in stage 1 would dehumidify without lowering the temperature much below the set point on the thermostat. They said the cost would be excessive as their remediation plan involved using some of the same equipment, wiring, setup, etc.

    I don't know where to turn at this point for a solution. I feel the RH of 63% when the outdoor is 60%RH (+28C) is too high. Crackers in our cupboards are soft and it just feels "wet" in the house.

    Anyone have ideas as to what is wrong with out setup and what it will take to correct it?

    Without knowing what the exact set-up of the 3-ton and 1.5 ton units are currently.

    One might look elsewhere : i.e. amount of air leakage from outside
    1. Duct Blaster Test.
    2. House pressurization Test - Blower Door

    A/C should definitely provide < 45% R.H. when outside temperature is > 80'F/27'C.

    Electric billing would tell one a little about your run-times.

    http://www.energyconservatory.com/ap...lications1.htm
    Designer Dan __ It's Not Rocket Science, But It is SCIENCE with Some Art. _ _ KEEP IT SIMPLE & SINCERE ___ __ www.mysimplifiedhvac.com ___ __ Define the Building Envelope & Perform a Detailed Load Calc: It's ALL About Windows & Make-up Air Requirements. Know Your Equipment Capabilities

  7. #7
    Join Date
    Jun 2006
    Posts
    96
    Post Likes
    Thread Starter
    Quote Originally Posted by dan sw fl View Post
    Without knowing what the exact set-up of the 3-ton and 1.5 ton units are currently.

    One might look elsewhere : i.e. amount of air leakage from outside
    1. Duct Blaster Test.
    2. House pressurization Test - Blower Door

    A/C should definitely provide < 45% R.H. when outside temperature is > 80'F/27'C.

    Electric billing would tell one a little about your run-times.

    http://www.energyconservatory.com/ap...lications1.htm
    Thanks Dan,

    I'm not sure what he total run times are. I would have thought when it was 80F, the bedroom unit would have been running almost all day, but it doesn't, although the tech set it up to cycle 6 times/hour. I assume this is set to do this if there isn't the need to run for long periods of time due to heat load requirements. The LR unit cycles more than the bedroom unit does under high heat load.

    Overall, the cooling is very even, it is just the miserable humidity I need to get rid of. As to air infiltration, we don't have an energy sealed house, but this 1950's bungalow has older dual pane Pella windows in the bedroom wing and new Loewen triple pane windows in the LR/DR/den. We re insulated the attic 6 years ago when we installed the new AC duct work in the attic and before we insulated we had the attic spray foamed to seal all through the ceiling device boxes and the tops of the wall plates. I can't say for certain, but I don't think we have allot of leakage. The house isn't drafty in the winter.

  8. #8
    Join Date
    Nov 2004
    Location
    SW FL
    Posts
    13,328
    Post Likes
    Cycles per Hour should be = 2.

    You'll never get to a firm resolution without FACTS on Infiltration and condenser Performance.
    Designer Dan __ It's Not Rocket Science, But It is SCIENCE with Some Art. _ _ KEEP IT SIMPLE & SINCERE ___ __ www.mysimplifiedhvac.com ___ __ Define the Building Envelope & Perform a Detailed Load Calc: It's ALL About Windows & Make-up Air Requirements. Know Your Equipment Capabilities

  9. #9
    Join Date
    May 2000
    Location
    Indianapolis, IN, USA
    Posts
    42,886
    Post Likes
    The mismatch on the big one doesn't help. Also wonder if they reused the 3 ton air handler on the 1.5 ton unit. Coil too big and it the blower won't slow down enough.

    My 2 ton is oversized for my 1000 sq ft but I don't have a humidity problem despite being in a steamy climate. If it does climb into the upper 50s in cool, muggy weather, I use the dehumidify feature of my control and variable speed blower to drop it.

  10. #10
    Join Date
    Jul 2001
    Location
    Fairfield and NewHaven Counties in Commecticut
    Posts
    4,982
    Post Likes

    need to check CFM

    Quote Originally Posted by kayjh View Post
    I'll try to keep this as short as possible.

    I have a 3,000 sq ft ranch style home in western Canada. We had new AC system installed 5 years ago, including ductwork in the attic of our home. 2 AC units were installed, (both 3 ton). One provides cooling for the LR/DR/Hallways and Den and the second does the bedroom wing. From day one we got extremely cold air and excessive cycling. In addition, the RH was never lower than 62%. After some discussion with the contractor, it was discovered that the manual J called for 4.2 tons (Supplier of the equipment did the manual J but didn't provide it to the contractor, just the recommendation for 6 tons) . The contractor discovered that the air handler for the LR unit was sized for a 4 Ton unit as was the duct work. The bedroom air handler was for a 3 ton and the ductwork was also sized for a 3 ton.

    After a meeting last month the contractor said the following was the fix:

    1. Remove the bedroom 3 ton unit and replace with a 1.5 ton unit and matching 1.5 ton air handler;
    2. Remove the 4 Ton air handler from the LR unit and discard. Use the 3 Ton air handler (from the bedroom unit) connecting to the 3 ton outdoor unit - existing (this set up will give 4.5 ton of cooling capacity);
    3. Balance air flow and adjust ECM air handlers to optimum speed.

    With this new setup, cooling comfort has improved. Airflow has been reduced significantly and we no longer feel blasts of cool air (the "meat locker" effect). There was some discussion during the recent installation that we might not have enough "static pressure" with the new setup given that the ductwork was 3 ton for a now 1.5 unit compressor (bedrooms) and 4 ton for 3 ton compressor (LR/DR/Den). We had no further discussion on this.

    I had asked the contractor to make sure they sized the new units correctly and asked that they upgrade me to 2 stage units. I reasoned that in off peak running times, the Rheem units running in stage 1 would dehumidify without lowering the temperature much below the set point on the thermostat. They said the cost would be excessive as their remediation plan involved using some of the same equipment, wiring, setup, etc.

    I don't know where to turn at this point for a solution. I feel the RH of 63% when the outdoor is 60%RH (+28C) is too high. Crackers in our cupboards are soft and it just feels "wet" in the house.

    Anyone have ideas as to what is wrong with out setup and what it will take to correct it?

    Thanks,

    kayjh
    I would check to be sure you have matched equipment (AHRI) and the blower settings are correct for a humid climate. You need a contractor that can verify CFM, subcooling to verify the current equipment if doing what it is supposed to do. We need model numbers of indoor and outdoor units on bith systems and maybe someone can look up the AHRI here.
    Quality and Value Service and Repair

  11. #11
    Join Date
    Jun 2003
    Location
    Madison, WI/Cape Coral, FL
    Posts
    12,042
    Post Likes
    I am posting the data of a properly setup ac supply and the effect on the space as the ac cycle. The critical issues are the air flow and the length of the cooling cycles. It takes 20-30 mins. to load the a/c coil /pan and moisture to start driping to the drain. Also at the end of the cooling cycle, the moisture on the coil re-evaporates back to the home. Longer fewer cooling cycles helps. Colder coil helps.
    Keep in mind as the cooling load declines, do not expect the a/c to maintain <50%RH. Supplemental dehumidification from a dehumidifier is required when the outside dew points are near or above the desire inside dew point and there is note enough cooling load.
    Regards TB
    Family RM AC F Dew Pnt.pdf
    Attached Images Attached Images
    Bear Rules: Keep our home <50% RH summer, controls mites/mold and very comfortable.
    Provide 60-100 cfm of fresh air when occupied to purge indoor pollutants and keep window dry during cold weather. T-stat setup/setback +8 hrs. saves energy
    Use +Merv 10 air filter. -Don't forget the "Golden Rule"

  12. #12
    Join Date
    Jun 2006
    Posts
    96
    Post Likes
    Thread Starter
    Quote Originally Posted by teddy bear View Post
    I am posting the data of a properly setup ac supply and the effect on the space as the ac cycle. The critical issues are the air flow and the length of the cooling cycles. It takes 20-30 mins. to load the a/c coil /pan and moisture to start driping to the drain. Also at the end of the cooling cycle, the moisture on the coil re-evaporates back to the home. Longer fewer cooling cycles helps. Colder coil helps.
    Keep in mind as the cooling load declines, do not expect the a/c to maintain <50%RH. Supplemental dehumidification from a dehumidifier is required when the outside dew points are near or above the desire inside dew point and there is note enough cooling load.
    Regards TB
    Family RM AC F Dew Pnt.pdf
    If we increase the cycle time and decrease the coil temperature to improve dehumidification, won't we supply colder air to the room and shut the thermostat off from the cold air entering the room? In other words, how to you get increased run times with the existing equipment without over cooling the room? Is the suggestion that we still have too much capacity?

  13. #13
    Join Date
    Jan 2009
    Location
    SE Iowa
    Posts
    5,577
    Post Likes
    3000sqft in western canada. 4.5 tons combined capacity might still be on the big side. You should have seen some improvement however. But as mentioned, a 3 ton coil with a 1.5 ton condenser will result in a dry coil unless you really, really slow that blower down. I think a 2 ton coil is about as large as you want to go. I'd start by slowing the blower, but long term
    you may need to put in a properly sized, matching air handler.

    Also, 6CPH as mentioned is way too much. 2-3CPH is better for AC.

  14. #14
    Join Date
    Jun 2005
    Location
    SW Wisconsin
    Posts
    6,627
    Post Likes

    RIGHT SIZING Equipment to Control Humidity Problems

    Allow me to shock U concerning some sizing realities in your climate toward controlling humidity.

    I live in SW Wisconsin today 9/4/12 at 2-PM at Lancaster it was 90F & 54% RH; indoors it is 52% RH & 76F with good air circulation & totally comfortable.

    Lancaster, WI very close to me, at 3-PM on the hour updates, it was 91-F; 50% RH; Heat Index: 97-F. NOW at 3:26 PM it's 50% RH in here on my first floor area & 76-F; around 25-C.

    The indoor contains 45.7 gr/per/lb/air; outdoors 116 gr/per/lb/air; A/C has to remove 45.7 gr//per/lb/air to get to 52% humidity level indoors.

    This is a 1937 farm home loaded with 13 windows on 1st floor &, NO shade until very late in the afternoon; first floor area 620-sf have a Half-Ton window shaker with an adjustable floor fan positioned to move air through all the rooms & back to the A/C.

    Okay, 620-sf divided / by .5 (1/2-Ton) is 1240-sf per/ton of cooling.

    3000-sf home (however, your climate should be milder in western Canada than here in SW WI).
    3000-sf / 1240-sf per/ton of cooling is 2.4-Ton;

    Well, U would have duct losses, etc., however, your home is way, way better insulated & protected from radiant & convection heat transfer than my home!

    I have a Half-Ton on the 2nd floor which I only use in the evenings...

    These small units have kept me perfectly comfortable in 112-F Heat Index.

    How in the world could anyone 'initially' oversize equipment by that much?
    Your home's calc should not be near where they had figuring it; even now it's still oversized for effectively controlling humidity plus meeting the sensible load.

    I've never had a load calc performed on my home by me or anyone else; however, these light weight units do the job perfectly & use less wattage than most indoor blowers use!

    It is amazing how much U can effectively cool with small tonnage; my all electric home monthly bills would shock your shoes off!
    Last edited by udarrell; 09-04-2012 at 04:39 PM. Reason: Typo...

  15. #15
    Join Date
    Jun 2006
    Posts
    96
    Post Likes
    Thread Starter
    Quote Originally Posted by udarrell View Post
    Allow me to shock U concerning some sizing realities in your climate toward controlling humidity.

    I live in SW Wisconsin today 9/4/12 at 2-PM at Lancaster it was 90F & 54% RH; indoors it is 52% RH & 76F with good air circulation & totally comfortable.

    Lancaster, WI very close to me, at 3-PM on the hour updates, it was 91-F; 50% RH; Heat Index: 97-F. NOW at 3:26 PM it's 50% RH in here on my first floor area & 76-F; around 25-C.

    The indoor contains 45.7 gr/per/lb/air; outdoors 116 gr/per/lb/air; A/C has to remove 45.7 gr//per/lb/air to get to 52% humidity level indoors.

    This is a 1937 farm home loaded with 13 windows on 1st floor &, NO shade until very late in the afternoon; first floor area 620-sf have a Half-Ton window shaker with an adjustable floor fan positioned to move air through all the rooms & back to the A/C.

    Okay, 620-sf divided / by .5 (1/2-Ton) is 1240-sf per/ton of cooling.


    3000-sf / 1240-sf per/ton of cooling is 2.4-Ton;

    Well, U would have duct losses, etc., however, your home is way, way better insulated & protected from radiant & convection heat transfer than my home!

    I have a Half-Ton on the 2nd floor which I only use in the evenings...

    These small units have kept me perfectly comfortable in 112-F Heat Index.

    How in the world could anyone 'initially' oversize equipment by that much?
    Your home's calc should not be near where they had figuring it; even now it's still oversized for effectively controlling humidity plus meeting the sensible load.

    I've never had a load calc performed on my home by me or anyone else; however, these light weight units do the job perfectly & use less wattage than most indoor blowers use!

    It is amazing how much U can effectively cool with small tonnage; my all electric home monthly bills would shock your shoes off!
    Udarrell,

    I don't disagree with you. Sizing is a large piece of the puzzle. Prior to installation, I asked the HVAC company to do a Manual J and a Manual D. They had the wholesaler do the calculations, who told the HVAC company that 2 x 3T was needed. How a 4T air handler got installed, I don't know. After allot of time and discussion, it was revealed taht the wholesaler and misrepresented the tonnage needed and said the Manual J calls for 4.2T. So they put in the correct air handler (3T) to match the compressor for the LR unit and changed the bedroom wing to 1.5T. It was +28C when I got home from the lake this weekend and the house was +22C and the RH was 61%. It seems to me that the setup is wrong (air handler speed, cycles per hour, etc.) or I still have way too much cooling. This is a maddening process.

  16. #16
    Join Date
    Jun 2005
    Location
    SW Wisconsin
    Posts
    6,627
    Post Likes
    Quote Originally Posted by kayjh View Post
    Udarrell,
    I don't disagree with you.
    Sizing is a large piece of the puzzle. Prior to installation, I asked the HVAC company to do a Manual J and a Manual D. They had the wholesaler do the calculations, who told the HVAC company that 2 x 3T was needed. How a 4T air handler got installed, I don't know.

    After allot of time and discussion, it was revealed that the wholesaler and misrepresented the tonnage needed and said the Manual J calls for 4.2T. So they put in the correct air handler (3T) to match the compressor for the LR unit and changed the bedroom wing to 1.5T.

    It was +28C when I got home from the lake this weekend and the house was +22C and the RH was 61%. It seems to me that the setup is wrong (air handler speed, cycles per hour, etc.) or I still have way too much cooling.
    This is a maddening process.
    Well, what don't U agree with?

    First, they set the CPH wrong, U want it to run with as few cycles as possible; air flow with a TXV metering device should be a low as it will safely operate.

    My home setup proves U don't need as much tonnage as U think or, sometimes even what the J calc says; I'd wouldn't use the additives in your climate area.

    Vancouver, in British Columbia; 2.5% summer design is 77F & 66F wet bulb or, around 63% RH. Victoria is only 73F & 62F wet bulb.

    Madison, WI is 88F & 73F wet bulb or around 49% RH. My area may be even closer to 90F design. The higher outdoor temp in SW WI means more grains of moisture per lb of dry air...

    I believe they may be able to make your units work, if not downsize until they do work.

    However, also remember that U have to have enough furnace air flow capacity for heating requirements in your area.
    Last edited by udarrell; 09-04-2012 at 06:57 PM. Reason: Typo...

  17. #17
    Join Date
    Jun 2006
    Posts
    96
    Post Likes
    Thread Starter
    Quote Originally Posted by udarrell View Post
    Well, what don't U agree with?

    First, they set the CPH wrong, U want it to run with as few cycles as possible; air flow with a TXV metering device should be a low as it will safely operate.

    My home setup proves U don't need as much tonnage as U think or, sometimes even what the J calc says; I'd wouldn't use the additives in your climate area.

    Vancouver, in British Columbia; 2.5% summer design is 77F & 66F wet bulb or, around 63% RH. Victoria is only 73F & 62F wet bulb.

    Madison, WI is 88F & 73F wet bulb or around 49% RH. My area may be even closer to 90F design. The higher outdoor temp in SW WI means more grains of moisture per lb of dry air...

    I believe they may be able to make your units work, if not downsize until they do work.

    However, also remember that U have to have enough furnace air flow capacity for heating requirements in your area.
    Airflow for heat isn't a problem. the house is heated with a hydronic system (baseboard radiant heat) that operates independently of the AC system. It sounds like the consensus is that I either have too much cooling, or mismatched equipment (still??). In addition, setting the 1.5T unit to cycle more is not helping the situation.

    lately the house has been comfortable with 51% RH. I have the windows open and the AC off. The overnight temps are 16C so the house cools down nicely. I'd like to get the problems sorted out for next year though.

  18. #18
    Join Date
    Sep 2012
    Posts
    4
    Post Likes

    ECM constant fan

    This is the Ask Our Pro's forum. In order to post a response here, you must have verified qualifications and have been approved by the AOP Committee. You may ask a question by starting a new thread.

    You can find the rules for posting and qualifications here.

    Additional infractions may result in loss of posting privileges.
    Last edited by jpsmith1cm; 09-14-2012 at 05:56 PM. Reason: non AOP member

  19. #19
    Join Date
    Jan 2009
    Location
    SE Iowa
    Posts
    5,577
    Post Likes
    ECM motor will only help if a thermostat with dehumidification capability is connected and wired to the Air Handler control board to slow the blower for more latent capacity. ECM motor, at proper static pressures use less energy at all speeds, and use dramatically less energy at low speeds and static pressures. However, with undersized ductwork, they can actually use the same or even more energy than a PSC motor.

  20. #20
    Join Date
    Jun 2003
    Location
    Madison, WI/Cape Coral, FL
    Posts
    12,042
    Post Likes
    Quote Originally Posted by bant View Post
    I may be mistaken, I thought your information regarding the solution done by you contractor included air handlers with ECM motors.
    These motors were designed to give your home constant fan across the coil this should give you superior dehumidification with no more energy usage than your standard PSC motor in cycle mode. Even in the most humid climates, this option should work wonders on humidity.
    Constant fan across the coil does not give superior dehumidification. Being able to slow the fan to the ideal air flow to provide a very cold coil without freezing gives better dehumidification.
    When the t-stat is satisfied, the moisture that remains on the coil, usually about 1 lb. per ton of capacity re-evaporates back into the home. If the fan is off or "auto" cycle, this may take 1.5 hours. With fan "on" low speed drying the coil takes 45 mins.
    When the outdoor dew points are +50^F, expect to need supplemental dehumidification to maintain <50%RH during low/no cooling loads.
    Regards TB
    Bear Rules: Keep our home <50% RH summer, controls mites/mold and very comfortable.
    Provide 60-100 cfm of fresh air when occupied to purge indoor pollutants and keep window dry during cold weather. T-stat setup/setback +8 hrs. saves energy
    Use +Merv 10 air filter. -Don't forget the "Golden Rule"

Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •