Results 14 to 22 of 22
Thread: RH Humidity Problems - Help!
-
09-04-2012, 05:12 PM #14
Regular Guest
- Join Date
- Jun 2006
- Posts
- 96
Thanks Motoguy (and everyone else taking the time to try and help). The 3T unit has a properly sized 3T condenser (I'm told). The 1.5T unit is new (Rheem) and I saw them install a new Rheem condenser. I'd be shocked if they mis sized it again. This is a bit maddening. Outdoor air temp is 23C today. At my office, when I arrived, indoor air temp is 23C/RH = 38%. When I left home the house was 22.5C/RH=59%. Both systems were cooling to the same exterior conditions and I used the same hygrometer to take the measurements. Not a professional tool though - a $20.00 unit from Home Depot.
-
09-04-2012, 05:19 PM #15
Regular Guest
- Join Date
- Jun 2006
- Posts
- 96
Udarrell,
I don't disagree with you. Sizing is a large piece of the puzzle. Prior to installation, I asked the HVAC company to do a Manual J and a Manual D. They had the wholesaler do the calculations, who told the HVAC company that 2 x 3T was needed. How a 4T air handler got installed, I don't know. After allot of time and discussion, it was revealed taht the wholesaler and misrepresented the tonnage needed and said the Manual J calls for 4.2T. So they put in the correct air handler (3T) to match the compressor for the LR unit and changed the bedroom wing to 1.5T. It was +28C when I got home from the lake this weekend and the house was +22C and the RH was 61%. It seems to me that the setup is wrong (air handler speed, cycles per hour, etc.) or I still have way too much cooling. This is a maddening process.
-
09-04-2012, 05:24 PM #16
Regular Guest
- Join Date
- Jun 2006
- Posts
- 96
If we increase the cycle time and decrease the coil temperature to improve dehumidification, won't we supply colder air to the room and shut the thermostat off from the cold air entering the room? In other words, how to you get increased run times with the existing equipment without over cooling the room? Is the suggestion that we still have too much capacity?
-
09-04-2012, 06:56 PM #17
Well, what don't U agree with?
First, they set the CPH wrong, U want it to run with as few cycles as possible; air flow with a TXV metering device should be a low as it will safely operate.
My home setup proves U don't need as much tonnage as U think or, sometimes even what the J calc says; I'd wouldn't use the additives in your climate area.
Vancouver, in British Columbia; 2.5% summer design is 77F & 66F wet bulb or, around 63% RH. Victoria is only 73F & 62F wet bulb.
Madison, WI is 88F & 73F wet bulb or around 49% RH. My area may be even closer to 90F design. The higher outdoor temp in SW WI means more grains of moisture per lb of dry air...
I believe they may be able to make your units work, if not downsize until they do work.
However, also remember that U have to have enough furnace air flow capacity for heating requirements in your area.Last edited by udarrell; 09-04-2012 at 06:57 PM. Reason: Typo...
AOP Forum Rules:
Rules for Posting
Rules For Equipment Owners
Equipment Owners Find a Contractor HERE!
udarrell
-
09-06-2012, 11:44 AM #18
Regular Guest
- Join Date
- Jun 2006
- Posts
- 96
Airflow for heat isn't a problem. the house is heated with a hydronic system (baseboard radiant heat) that operates independently of the AC system. It sounds like the consensus is that I either have too much cooling, or mismatched equipment (still??). In addition, setting the 1.5T unit to cycle more is not helping the situation.
lately the house has been comfortable with 51% RH. I have the windows open and the AC off. The overnight temps are 16C so the house cools down nicely. I'd like to get the problems sorted out for next year though.
-
09-14-2012, 10:51 AM #19
New Guest
- Join Date
- Sep 2012
- Posts
- 4
ECM constant fan
This is the Ask Our Pro's forum. In order to post a response here, you must have verified qualifications and have been approved by the AOP Committee. You may ask a question by starting a new thread.
You can find the rules for posting and qualifications here.
Additional infractions may result in loss of posting privileges.
Last edited by jpsmith1cm; 09-14-2012 at 05:56 PM. Reason: non AOP member
-
09-14-2012, 11:36 AM #20
ECM motor will only help if a thermostat with dehumidification capability is connected and wired to the Air Handler control board to slow the blower for more latent capacity. ECM motor, at proper static pressures use less energy at all speeds, and use dramatically less energy at low speeds and static pressures. However, with undersized ductwork, they can actually use the same or even more energy than a PSC motor.
-
09-14-2012, 01:47 PM #21
Constant fan across the coil does not give superior dehumidification. Being able to slow the fan to the ideal air flow to provide a very cold coil without freezing gives better dehumidification.
When the t-stat is satisfied, the moisture that remains on the coil, usually about 1 lb. per ton of capacity re-evaporates back into the home. If the fan is off or "auto" cycle, this may take 1.5 hours. With fan "on" low speed drying the coil takes 45 mins.
When the outdoor dew points are +50^F, expect to need supplemental dehumidification to maintain <50%RH during low/no cooling loads.
Regards TBBear Rules: Keep our home <50% RH summer, controls mites/mold and very comfortable.
Provide 60-100 cfm of fresh air when occupied to purge indoor pollutants and keep window dry during cold weather. T-stat setup/setback +8 hrs. saves energy
Use +Merv 10 air filter. -Don't forget the "Golden Rule"
-