    True prep table

    I've been working on older true prep table. The evaporator keeps freezing up. I've replaced the cap tube with same size and length and dryer. Ive brazed in access fittings on high and low it's a R134a system. The thermostat went bad on it also so I replaced it. Then I've replaced the evaporator fan too. At start my cabinet temp was 80 degrees. My ambient 95 degrees. My suction was 17 degrees and head 250. Any help would be appreciated!
    Knowledge comes with experience

  2. #2
    Join Date
    Jan 2010
    Posts
    45,370
    Post Likes
    Looks like a restriction with that hi of head pressure. Of course if your condenser is plugged you would get the same result.

  3. #3
    Join Date
    Mar 2006
    Location
    cincinnati, ohio
    Posts
    258
    Post Likes
    Thread Starter
    I overcharged it about 4-6oz to get suction up. I'm wondering if I need to shorten length of cap tube to raise suction pressure. It ran good for a week but now froze up again.
    Knowledge comes with experience

  4. #4
    Join Date
    Jan 2010
    Posts
    45,370
    Post Likes
    What's the nameplate charge say ?

  5. #5
    Join Date
    Mar 2006
    Location
    cincinnati, ohio
    Posts
    258
    Post Likes
    Thread Starter
    11oz. It's a True TSSU 48-12
    Knowledge comes with experience

  6. #6
    Join Date
    Jan 2010
    Posts
    45,370
    Post Likes
    Pull the charge and weigh in the exact amount. Your overcharged.

  7. #7
    Join Date
    Mar 2006
    Location
    cincinnati, ohio
    Posts
    258
    Post Likes
    Thread Starter
    When I first weighted it in my suction was at 3-4psi. That's why I overcharged. Shouldn't my suction on a refrigerator with 134 be around 25 psi?
    Knowledge comes with experience

  8. #8
    Join Date
    Jan 2010
    Posts
    45,370
    Post Likes
    Quote Originally Posted by nickellhead View Post
    Shouldn't my suction on a refrigerator with 134 be around 25 psi?
    Well at 26 psig your coil would be 30* add a 10* TD and your at 40* air temp.

  9. #9
    Join Date
    Jul 2011
    Location
    Lehigh Valley, PA
    Posts
    510
    Post Likes
    Quote Originally Posted by nickellhead View Post
    When I first weighted it in my suction was at 3-4psi. That's why I overcharged. Shouldn't my suction on a refrigerator with 134 be around 25 psi?
    BTDT. You keep charging until the suction comes up near 18psi and before you know it your head is at 250psi. Still a restriction or a new one in the cap tube.

  10. #10
    Join Date
    Jan 2010
    Posts
    45,370
    Post Likes
    On a hot pull down it can go low at first.

  11. #11
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    23,572
    Post Likes
    134a I like seeing 16-19psi on the suction side. Your head is way too high.
    Officially, Down for the count

    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET

    I know enough to know, I don't know enough
    Why is it that those who complain the most contribute the least?
    MONEY CAN'T BUY HAPPINESS. POVERTY CAN'T BUY ANYTHING

  12. #12
    Join Date
    Mar 2006
    Location
    cincinnati, ohio
    Posts
    258
    Post Likes
    Thread Starter
    When I weighted it in I let it cool down but suction pressure nor head changed. It stayed at 3-4&160ish. And it took cabinet forever to get down to 38 degrees. I just don't understand how it's freezing up when I have it overcharged? I'm wondering also if maybe new thermostat is acting up. The probe goes into a well inside middle of evaporator. I've always seen the probes clipped on outside of evaporator. Name:  ImageUploadedByTapatalk1346297324.052569.jpg
Views: 3136
Size:  34.5 KB here's a pic of the top of the evaporator.
    Knowledge comes with experience

  13. #13
    Join Date
    Jan 2010
    Posts
    45,370
    Post Likes
    What was the head pressure when you first weighed it in ? With a cap tube and no receiver the only place the extra refrigerant could go to was the condenser. This would reduce your condensing surface area. And yes the temp. control cap tube belongs in that well. Take a closer look at the condenser coil to be sure it is clean.

  14. #14
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    23,572
    Post Likes
    Does this unit have pans on top? If so, are they keeping pans in it overnight or just a cover? Need to keep pans in it.
    Officially, Down for the count

    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET

    I know enough to know, I don't know enough
    Why is it that those who complain the most contribute the least?
    MONEY CAN'T BUY HAPPINESS. POVERTY CAN'T BUY ANYTHING

  15. #15
    Join Date
    Mar 2006
    Location
    cincinnati, ohio
    Posts
    258
    Post Likes
    Thread Starter
    I think their taking the pans out at night. Why does it matter if pans are in there? I will check and clean Condensor tomorrow. Thanks for all your help!! If you think of anything else please let me know.
    Knowledge comes with experience

  16. #16
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    23,572
    Post Likes
    Pans need to stay in as an insulator. Box will not reach temp and compressor will not stop running. Similar to keeping a door open
    Officially, Down for the count

    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET

    I know enough to know, I don't know enough
    Why is it that those who complain the most contribute the least?
    MONEY CAN'T BUY HAPPINESS. POVERTY CAN'T BUY ANYTHING

  17. #17
    Join Date
    Mar 2006
    Location
    cincinnati, ohio
    Posts
    258
    Post Likes
    Thread Starter
    Thanks 2sac! That may be the problem. Because its lasted all week and then it sees to freeze up the day after they've been closed for two days. I'll definitely check that out!! I know my head pressure is high but just couldn't understand the week of running fine and then coming back after being closed for two days being froze up.
    Knowledge comes with experience

  18. #18
    Join Date
    Jun 2009
    Location
    DFW, TX
    Posts
    1,719
    Post Likes
    Its freezing up because it doesn't ever get the evaporator coil down to the 15*F that its looking for to cycle off, so it runs forever.

    Fix the refrigeration problem. Get cap tube specs from True. Replace it and use a C032CAPT drier or the C052-cap-tt-hh drier. Strap cap tube to suction line like OEM. Make sure clean condenser, clean evaporator, good airflow, all fan shrouds in place, etc.

    If a larger drier is used you may need to add a couple of ounces over nameplate to compensate.

    When you work on this unit, you put your temp probe in the coil and watch how fast coil pulls down. Also if you replaced the OEM evap fan which moves very slow, with a normal 9watt fan, it will move to much air and coil will run warm and can freeze the food.

    Good luck. True tech support is helpful and doesn't mind helping you troubleshoot. They know their products very well.

  19. #19
    Join Date
    Mar 2006
    Location
    cincinnati, ohio
    Posts
    258
    Post Likes
    Thread Starter
    Thanks everyone! I will go there this evening and check all of that. Why does cap tube have to be strapped to suction line?
    Knowledge comes with experience

  20. #20
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    23,572
    Post Likes
    To guarantee subcooled lquid is reaching the coil. Attach what you can to the suction line. This is a must. I usually use silver tape, then wrap it all with foam tape. If you have room, coil up the leftovers in the evaporator rather than the condenser section. I like to coil mine around my Maglite before installing it. looks neat and is compact.
    Officially, Down for the count

    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET

    I know enough to know, I don't know enough
    Why is it that those who complain the most contribute the least?
    MONEY CAN'T BUY HAPPINESS. POVERTY CAN'T BUY ANYTHING

+ Reply to Thread
Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •