I have a carrier chiller that has had a ongoing issues with low load surging and they will also not load up. Both machines run between 5% and 15% guide vane position.
I adjusted T1 and P1 so the unit is always in HGBP mode to keep to machine on line.(2 machines).
Any advise would be appreciated.
This is my current operating conditions-
M#19XVR3032256BGS64
CwSetpt- 46
Condenser water - 74.6 / 77.3
Evap water - 52.4 / 50.5
Refrig - 81 / 48.2
Inlet guide vane- 5%
Motor- full speed @ 55% amps
Sent from my DROID Pro using Tapatalk 2
-
08-29-2012, 07:26 PM #2
Better Log?
I assume the mini log you posted was in the HGBP mode. I would be interested in seeing a log in LWT mode.
Both chillers doing the same thing? Exactly? If not, I know in my case I would have a better shot at helping if we look at them individually. Otherwise, if they really are doing the same thing or pretty close, then, I would be inclined to review the set-up menu closely.
Is this a new plant for you? Do you have old logs? Do the logs indicate it ran a-lot in HGBP back then as well?
Can you get a log under a heavy load?
What are the run hours?
When was the last time the float was inspected/serviced? These machines have a habit of the float sticking. You will get this mystery low refrigerant temp condition & sometimes it will alarm, then, the next day(s) it will run fine. They can surge in this condition as well.
Lastly: I personally never use HGBP unless I have no other option & even then its usually temporary. Especially in your case, if you have operating inverters, there is no need to pour money down the drain.All my leon freaked out!
-
08-29-2012, 08:18 PM #3
Professional Member*
- Join Date
- Jan 2008
- Location
- Dallas ,Texas
- Posts
- 3,507
Why not just run one chiller?
-
08-29-2012, 11:05 PM #4
Professional Member*
- Join Date
- Dec 2008
- Location
- Dixiana, AL
- Posts
- 2,487
-
08-29-2012, 11:43 PM #5
Professional Member*
- Join Date
- Jan 2008
- Location
- Dallas ,Texas
- Posts
- 3,507
-
08-30-2012, 12:32 AM #6
-
08-31-2012, 07:08 AM #7
Regular Guest
- Join Date
- May 2008
- Location
- Northern Virginia
- Posts
- 15
1- we have been working @ this site for 2 years. The T1/P1 has been set low from the beginning. T1/P1 was changed to factory setting after 3 consecutive 100degree days in the beginning of the summer because the chillers were not loading up. I also am not the primary tech for this site, but I feel these chillers should run better.
2- both chiller have similar issues.
3- the float has not been inspected
4- I also think one chiller should be able to handle the load, but it does not keep the load, because of the minimal guide vane position.
Sent from my DROID Pro using Tapatalk 2
-
08-31-2012, 07:22 AM #8
Professional Member*
- Join Date
- Jan 2008
- Location
- Dallas ,Texas
- Posts
- 3,507
Are the VFD's running 100% on both chillers?
-
08-31-2012, 07:34 AM #9
Regular Guest
- Join Date
- May 2008
- Location
- Northern Virginia
- Posts
- 15
Yes both are running 100% VFD.
I also left out that both chillers are running 24/7 in a 24/7 occupied space.
Sent from my DROID Pro using Tapatalk 2
-
08-31-2012, 09:11 AM #10
Professional Member*
- Join Date
- Aug 2009
- Location
- Prattville,Alabama
- Posts
- 1,102
You have a 1.9 F split on the evaporator. I would look into this first. It can be surprising what happens when you take care of a seemingly unrelated issue....
-
08-31-2012, 09:08 PM #11
Regular Guest
- Join Date
- Oct 2011
- Location
- South Georgia
- Posts
- 45
If i am reading your numbers correctly you have condensor and cooler approach a little too wide. Check the machine's original design sheets and compare to actual. Are your transducers accurate? How about tube cleanliness?
-
08-31-2012, 11:00 PM #12
Regular Guest
- Join Date
- Aug 2012
- Location
- FL
- Posts
- 18
Fix first why the chiller does not load. Look inside the panels there should be a sticker with the original setup of the chiller. Make sure it is correct on the setup screens. Those numbers are what the chiller ran at factory. Once the chiller loads and unloads check for proper pressure drops on the vessels, it could be that there is not enough water flow on the evaporator and the setup was changed to keep the chillers online.