    What happens if the refrigerant flows backwards through a liquid line filter-drier, that is, opposite the arrows printed on it? Is this a no-no?

  2. #2
    Join Date
    Oct 2004
    Posts
    3,400
    Usually nothing, if there isn't any debris in the system.
    If there is, then it's more likely to develop a restriction.

    The fine screen is on the wrong end of the drier.

    The dessicant doesn't really care which direction the moisture comes from.

    Maybe they need to put a little picture of a house on the outlet.

  3. #3
    Join Date
    Dec 2005
    Location
    Ohio
    Posts
    42
    Thanks for the reply.

  4. #4
    Join Date
    Jul 2002
    Posts
    897
    It can matter. Why do you think there is an arrow?
    There is an internal spring for compression of the dessicant beads that works with the filter flow. When installed backwards this reduces the spring tension and the beads can grind and turn to dust.


    http://www.emersonclimate.com/images...ter%20drier%22

  5. #5
    Join Date
    May 2003
    Location
    Dixie
    Posts
    1,344
    unless it's a heat pump with the proper dryer....bi-flow drier