+ Reply to Thread
Page 2 of 3 FirstFirst 123 LastLast
Results 21 to 40 of 45

Thread: flushing linesets

  1. #21
    Join Date
    Feb 2005
    Location
    L.I. NY
    Posts
    129
    Post Likes
    Anyone remember the R12 to 134 conversion days? Recomendation was less than 2% of original mineral oil remaining and requiring mutiple oil changes to get it there. After a few years that number started to climb and the automotive guys stoped removing the old oil. They just added a few OZ of poly oil to the system and let it rip.

    I think I would rather have a used lineset from a clean system than one that has been flushed with the new flushes that are avaiabe today. Can I have my R-11 back, that stuff worked great as a flush.

  2. #22
    Join Date
    Jul 2011
    Posts
    117
    Post Likes
    lol nothing like trying to braze a lineset that has had r22 running thru it for decades without a flush by the way, I love how the FLAMES just like to try and tickle my nose from my torches!!!


    Anyone that has any experience in HVAC know's what I am talking about...

  3. #23
    Join Date
    Dec 2002
    Location
    Arizona
    Posts
    4,480
    Post Likes
    You need to revisit refrigerant recovery laws if your having those problems. LOL
    Make your expertise uniquely valuable.

    Make your influence uniquely far-reaching.

  4. #24
    Join Date
    Jul 2011
    Posts
    117
    Post Likes
    ah the lab default.. Nah I am speaking for us men in the field...

  5. #25
    Join Date
    Dec 2002
    Location
    Arizona
    Posts
    4,480
    Post Likes
    LOL You have no idea!
    Make your expertise uniquely valuable.

    Make your influence uniquely far-reaching.

  6. #26
    Join Date
    Jul 2011
    Posts
    117
    Post Likes
    Well seems I met the 1st troll here on hvac-talk... Flushing the lineset has turned into a pissing match over who is more over the top... Good luck on preaching your beleif's on what is ok and right in the field.. Not to flush or to flush whatever, If your best is just a nitro purge so be it, if it is a r11 flush with a nitro purge so be it... If it is nothing then so be it.. As far as this gorilla bull crap your trying to smear all over this guys question so be it.. You do not sound professional you sound like someone trying to say not cleaning linesets is ok, when its not and is not doing your best for your customer client etc.. If it was my house i would flush it, just as I would if I had control over it for my customers..

    Go to the labs, the experiments in your controlled rooms and make excuses for not doing the best for your customers to relieve your guilt, I don't care, and I am done trying to reason with ignorance.....

    I am just glad people like you have proven to me I am doing the best for my clients and customers thank you so much...

    for proving to me I am one of the best...

  7. #27
    Join Date
    Feb 2009
    Location
    Tallahassee, FL
    Posts
    6,217
    Post Likes
    X2 jimj

    You are in the minority of "us in the field" danae

    You seem to be the one being the most defensively. Jimj has been around and seen most of it all and is well respected among

    You will do well to listen and let your mind be opened to what others say.

  8. #28
    Join Date
    Dec 2002
    Location
    Arizona
    Posts
    4,480
    Post Likes
    Quote Originally Posted by Danae12 View Post
    Go to the labs, the experiments in your controlled rooms and make excuses for not doing the best for your customers to relieve your guilt, I don't care, and I am done trying to reason with ignorance.....

    I am just glad people like you have proven to me I am doing the best for my clients and customers thank you so much...

    for proving to me I am one of the best...
    If you can support ANY of your arguments with any kind of written information by any manufactures ( other than the people that sell flush) I would love to see it. I unlike you have an open mind.
    Make your expertise uniquely valuable.

    Make your influence uniquely far-reaching.

  9. #29
    Join Date
    Dec 2005
    Location
    Cincinnati, Oh
    Posts
    11,829
    Post Likes
    Quote Originally Posted by Danae12 View Post
    Well seems I met the 1st troll here on hvac-talk... Flushing the lineset has turned into a pissing match over who is more over the top... Good luck on preaching your beleif's on what is ok and right in the field.. Not to flush or to flush whatever, If your best is just a nitro purge so be it, if it is a r11 flush with a nitro purge so be it... If it is nothing then so be it.. As far as this gorilla bull crap your trying to smear all over this guys question so be it.. You do not sound professional you sound like someone trying to say not cleaning linesets is ok, when its not and is not doing your best for your customer client etc.. If it was my house i would flush it, just as I would if I had control over it for my customers..

    Go to the labs, the experiments in your controlled rooms and make excuses for not doing the best for your customers to relieve your guilt, I don't care, and I am done trying to reason with ignorance.....

    I am just glad people like you have proven to me I am doing the best for my clients and customers thank you so much...

    for proving to me I am one of the best...
    Based on that last post, if I was judging only on professionalism...

    We flush, but not with rx11. We use a nitro/cleaning mixture, similar (but greater volumes) to a acid cleanup injector.
    Seems like it works so far. Haven't had any real compressor issues. The nitro really sprays that stuff out of there. I doubt anything remains when correctly done.
    But, thats in the rarity that we can't replace a lineset.

    In reality though, I'd rather hit them with nitro alone.
    As mentioned earlier, there's only 2 things that belong in a system. Refrigerant and oil.

    keep in mind, if the crap hits the fan with flushing linesets (5 years down the road it eats up windings), I doubt your manufacturer will stand behind those warranty claims. Especially if they've said not to use flushing agents.
    "Better tell the sandman to stay away, because we're gonna be workin on this one all night."

    "Dude, you need more than 2 wires to a condenser to run a 2 stage heatpump."

    "Just get it done son."

    Dad adjusted

  10. #30
    Join Date
    Jul 2006
    Location
    Prata di Pordenone Italy
    Posts
    8,069
    Post Likes
    I say do what you feel comfortable with .although you can go wrong with replacing the line set

  11. #31
    Join Date
    Aug 2010
    Posts
    4,338
    Post Likes
    "I've been doing it this way for a long time..."
    doesn't mean you've been doing it THE ONLY RIGHT WAY though.Experience is of value but not a gospel.

    Supposedly glass bottles are better for water bottle because it doesn't leach anything. You could chose to use glass water bottle for on the field and on the beach. It's safe as long as its not broken. Here the unquestionable risk exceeds questionable benefits, so unless you're a veggie organic hippie freak the prudent choice is plastic bottle.

    For a one man show working on flat rate you have a lot of discretion in what you do.
    If you're a business owner where the expense of techs affect your bottom line, procedures that take considerable payable tech time with questionable merit (return on investment) shouldn't be done just because its always been done and works good based on anecdotal evidence.

    If it adds an hour to each install but merits are moot, that's one hour of payroll expense.

  12. #32
    Join Date
    Jun 2004
    Posts
    946
    Post Likes
    I don't use any chemical to flush the system
    Just plain nitro.
    Flush is bad news for your system

    I have to agree with jimj

    The only reason they wanted only a small amount mineral oil
    Was the parrafen wax
    That was dissolve on older semi hermetic compressor.
    The wax is not messible with poly oil
    So the minute it hit a colder spot like txv
    It will separate and plug it up.

    They stop using this wax in mid 80s.


    Even if you don't purge with nitro it should be okay
    As long as its not a burn out.

    You are doing more harm if u use rx11
    And can't get all out

  13. #33
    Join Date
    Jun 2004
    Posts
    946
    Post Likes
    Parrafen wax is wax that was used for motor winding insulation
    It get dissolve by meniral oil

  14. #34
    Join Date
    Jun 2009
    Location
    Pompano Bch, S Fla
    Posts
    57
    Post Likes
    Thanks Jim. Good to see some actual literature on the subject. The company I work for tells us to flush with only nitro (and vacuum of course) so this makes me feel much better about it. How do you get those bulletins?

  15. #35
    Join Date
    Jul 2009
    Location
    South Carolina
    Posts
    14,412
    Post Likes
    I don't see the reason for any argument here. The fact is most of us are doing what we have been taught , told, researched or experienced what works the best. I don't know about the rest here but I've only been installing 410a systems for about 4 years. That's hardly enough time to get any long term data on the best line cleaning procedures. I've done it both ways but stopped using the flush in the early goings. I haven't had any problems yet that I know of so I'll stick with the plain nitro purge until I find any definitive evidence that it is not sufficient. It looks like even the manufacturers don't all agree what is the best way to clean an old line set. The majority of them seem to think R22 is the best to clean the lines with but with the price of R22 now it doesn't seem very practical. In another 5 or 10 years we'll have a lot more data to compare but for now I say do whatever you're comfortable with as long as you don't leave anything in the lines that wasn't there before.
    Gary
    -----------
    http://www.oceanhvac.com
    The best things in life are free but not everyone is willing to pay the price.
    When you appreciate what you have, you have a lot more.

  16. #36
    Join Date
    May 2011
    Location
    tallahassee,fl
    Posts
    380
    Post Likes
    Got about 15 systems right now that every time I hook up to service I can smell straight flush.

  17. #37
    Join Date
    Aug 2010
    Posts
    4,338
    Post Likes
    Quote Originally Posted by garyed View Post
    R22 is the best to clean the lines with but with the price of R22 now it doesn't seem very practical.
    It shouldn't be really relevant, at least its not to the point where de minimis loss makes it any costlier than anything else. Closed loop liquid refrigerant flush is a feature found on many automotive A/C service equipment.

    Open loop flushing using refrigerant is illegal anyways.

    As far as the instructions given by companies, the tech, you, are the most expensive expense. Every second you're there, the company is expending on your payroll.

    What you'd do as a one man job is different from. If you do things your own way and it takes you an hour more you're not actually losing money unless there's a direct opportunity cost (i.e. had to turn another job down) but if he's paid by the company by the hour, its an hour of labor that they have to pay you.

  18. #38
    Join Date
    Feb 2009
    Location
    Tallahassee, FL
    Posts
    6,217
    Post Likes

    its goona take some time to see what happens to units with flush circ

    When the coils get dirty and/or cond fan quits - that is when the discharge temps are goona start causing flush components to break down and form acids.

  19. #39
    Join Date
    Jul 2009
    Location
    South Carolina
    Posts
    14,412
    Post Likes
    Quote Originally Posted by ICanHas View Post
    It shouldn't be really relevant, at least its not to the point where de minimis loss makes it any costlier than anything else. Closed loop liquid refrigerant flush is a feature found on many automotive A/C service equipment.

    Open loop flushing using refrigerant is illegal anyways. ............................
    Here's a twister.
    Whether you illegally flush with R-22 & blow it to the atmosphere or do it legally closed loop you're still going to waste it all unless you illegally reuse what you legally used.
    Gary
    -----------
    http://www.oceanhvac.com
    The best things in life are free but not everyone is willing to pay the price.
    When you appreciate what you have, you have a lot more.

  20. #40
    Join Date
    Aug 2010
    Posts
    4,338
    Post Likes
    Quote Originally Posted by garyed View Post
    Here's a twister.
    Whether you illegally flush with R-22 & blow it to the atmosphere or do it legally closed loop you're still going to waste it all unless you illegally reuse what you legally used.
    It is illegal to charge a system with recovered refrigerant unless the refrigerant originated from the same owner, but there is no specific language saying you can not HCFC-22 formerly used for refrigerant for closed loop cleaning.

    In closed loop system, the solvent (HCFC-22 in this case) is recycled and the only loss is through connecting/disconnecting.

+ Reply to Thread
Page 2 of 3 FirstFirst 123 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •