Thread: Walk in freezer

  1. #21
    Join Date
    May 2011
    Location
    Eastern Washington State
    Posts
    7
    Post Likes
    not gonna lie I installed a pump down valve backwards once....we all know what that would cause..........needless to say that got fixed...

  2. #22
    Join Date
    Sep 2012
    Posts
    15
    Post Likes
    2Sac nailed it on the head. Quit touching our equipment you hack.

  3. #23
    Join Date
    Oct 2012
    Location
    CA
    Posts
    781
    Post Likes
    Quote Originally Posted by traviscmatthews View Post
    2Sac nailed it on the head. Quit touching our equipment you hack.
    Do you need a hug ?

  4. #24
    Join Date
    Jan 2006
    Location
    DFW Metroplex
    Posts
    4,910
    Post Likes
    Quote Originally Posted by Qamar View Post
    check txv screen it's clean turn off avap.fan to see flow of refrigerant , frost was building all across evap coil follow sporlan instructions to adjust SH left unit running all night chk next morning box temp went down to 20*F. 1/4 turn stem to chk if it goes down further. I am debating if there is a mismatch. I have collected all the info.will do a serious anylisis.
    Obviously I'm a little behind the curve on replying here, but if you adjusted SH via Sporlan instructions - what did your final superheat reading come in at?

    Furthermore, when you started working on the unit the outside ambient was ~100F and head pressure was 350 psig - giving you an almost 30F condenser TD......which ain't right.

    After changing the LL solenoid valve, you stated the head pressure was reading 225 psig. What was the outside ambient?

    A guy shouldn't be horkin' around with the TXV until he's darn sure he has enough gas in the system....
    "The problem is the average person isn’t tuned in to lifelong learning, or going to seminars and so forth. If the information is not on television, and it’s not in the movies they watch, and it’s not in the few books that they buy, they don’t get it" - Jack Canfield

  5. #25
    Join Date
    Oct 2012
    Location
    Sandy, Utah
    Posts
    158
    Post Likes
    If what you are describing is what I think you are. 1-very low suction pressure yet head pressure is normal or maybe a bit high? It sounds like you've done a good job cleaning up the system. Evacuating and putting the proper charge in. You've replaced the drier and the liquid line solenoid, correct?
    I would suspect that possibility that the power head assembly has lost it's charge which would shut off the expansion valve. Just a thought. I've had many powerhead's lose their bulb charge and it has some of the symptoms you've described. Also you can have a wax build-up that can plug up the txv. But again, you've cleaned up the system which should have taken care of that possible problem.
    Hope this might help.
    Mark

  6. #26
    Join Date
    Aug 2010
    Location
    Riverside California
    Posts
    24
    Post Likes
    Thread Starter
    I almost gave up but next day i went back turned off the evap fan i see frost building up which gives me idea that that evap was not flashing gas because of fan running so i try looking for DTFD it was fried ireplaced DTFD unit went down to -5* so that was the problem thanks

  7. #27
    Join Date
    Jun 2004
    Posts
    946
    Post Likes
    Quote Originally Posted by Qamar View Post
    I almost gave up but next day i went back turned off the evap fan i see frost building up which gives me idea that that evap was not flashing gas because of fan running so i try looking for DTFD it was fried ireplaced DTFD unit went down to -5* so that was the problem thanks
    .?
    What..?
    I don't understand
    None of it make any sense to me.
    I think there is something you are not telling us.
    Box don't get cold enough but when you replace termination fan delay
    The box drop?

    When u turn off the fan you had an idea?
    It's not flashing gas?

    Qamar
    Let me guess
    You are working on your own equipment.
    You don't want to call the tech back ( too expensive)
    So you will fix it yourself.

  8. #28
    Join Date
    Aug 2009
    Location
    Maine
    Posts
    8,146
    Post Likes
    Defrost heaters on ?
    Replace enough parts and just maybe you will get lucky.

    Quote Originally Posted by shaka View Post
    .?
    What..?
    I don't understand
    None of it make any sense to me.
    I think there is something you are not telling us.
    Box don't get cold enough but when you replace termination fan delay
    The box drop?

    When u turn off the fan you had an idea?
    It's not flashing gas?

    Qamar
    Let me guess
    You are working on your own equipment.
    You don't want to call the tech back ( too expensive)
    So you will fix it yourself.

  9. #29
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    32,658
    Post Likes
    The evap should flash MORE gas with the fan running.

    I think that like a broken clock is right twice a day, you managed to stumble on a defective part, but you need to learn diagnostics.

    I have to agree that it is unlikely that you are a trained technician, because you seem to lack the fundamental knowledge which you SHOULD know....
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







  10. #30
    Join Date
    Feb 2007
    Location
    Fremont, Indiana
    Posts
    3,275
    Post Likes
    Quote Originally Posted by shaka View Post
    .?
    What..?
    I don't understand
    None of it make any sense to me.
    I think there is something you are not telling us.
    Box don't get cold enough but when you replace termination fan delay
    The box drop?

    When u turn off the fan you had an idea?
    It's not flashing gas?

    Qamar
    Let me guess
    You are working on your own equipment.
    You don't want to call the tech back ( too expensive)
    So you will fix it yourself.
    ^^^^^^^^
    I don't get it either!
    Still sounds like you're stumbling and fumbling!

    sent from my Samsung Galaxy Note
    Member of the "Work Exchange Program"
    "Will work for knowledge"

    "Everyone is a genius. But if you judge a fish on its ability to climb a tree, it will live its whole life believing that it is stupid"
    A Einstein

  11. #31
    Join Date
    Jun 2004
    Posts
    946
    Post Likes
    Quote Originally Posted by lytning View Post
    Defrost heaters on ?
    Replace enough parts and just maybe you will get lucky.

    Yes I think that's what he is doing
    Keep throwing parts untill it's the right one.
    Heater won't be on
    Not in the same circuit as TFD.

  12. #32
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    32,658
    Post Likes
    The defrost termination energizes a solenoid behind the time clock, and that circuit is backed up by a separate timer that stops the defrost after a set time, such as 40 minutes.

    Not the "same circuit," but several circuits, working together.
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







  13. #33
    Join Date
    Aug 2010
    Location
    Riverside California
    Posts
    24
    Post Likes
    Thread Starter

    Freezer Working

    I came this far after 32 or 33 threads I accumulated enough info to understand operation of Walking freezer .And this acquired knowledge help me to troubleshoot in systematic fashion which help to pinpoint the problem. W/20*F box temp i Did'nt see any frost on back wall of evap. after turning off fan i see frost building across the coil which led me to check defrost t/stat which was defective i replace it turn on the unit temprature start dropping. There are people in this wrld who value ur effort this cstmr is one of them.
    Will work for knowledge

  14. #34
    Join Date
    Feb 2007
    Location
    Fremont, Indiana
    Posts
    3,275
    Post Likes
    So heaters energized throughout defrost cycle until terminated by fail safe?
    This could have been easily determined during initial visit!
    Besides, fail safe should be set at only 25% over.

    sent from my Samsung Galaxy Note
    Member of the "Work Exchange Program"
    "Will work for knowledge"

    "Everyone is a genius. But if you judge a fish on its ability to climb a tree, it will live its whole life believing that it is stupid"
    A Einstein

  15. #35
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    23,572
    Post Likes
    3 pages and it's still walking. You'd think it would be tired by now...
    Officially, Down for the count

    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET

    I know enough to know, I don't know enough
    Why is it that those who complain the most contribute the least?
    MONEY CAN'T BUY HAPPINESS. POVERTY CAN'T BUY ANYTHING

  16. #36
    Join Date
    Jun 2004
    Posts
    946
    Post Likes
    Quote Originally Posted by 2sac View Post
    3 pages and it's still walking. You'd think it would be tired by now...


  17. #37
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    32,658
    Post Likes
    It seems we have a lot of walking boxes lately...

  18. #38
    Join Date
    Mar 2009
    Location
    Mid-Mo
    Posts
    3,600
    Post Likes
    Quote Originally Posted by timebuilder View Post
    It seems we have a lot of walking boxes lately...
    They are just trying to keep their New Years resolution of weight loss.

  19. #39
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    32,658
    Post Likes
    Quote Originally Posted by ryan1088 View Post
    They are just trying to keep their New Years resolution of weight loss.
    All they have to do is get warm inside. They'll lose weight real fast!

  20. #40
    Join Date
    Dec 2010
    Location
    Woodbridge Twp, NJ
    Posts
    1,309
    Post Likes
    Quote Originally Posted by 2sac View Post
    3 pages and it's still walking. You'd think it would be tired by now...
    must be on a chain and not going far.
    Every customer you take for granted today will be someone else's tomorrow.

+ Reply to Thread
Page 2 of 3 FirstFirst 123 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •