Page 2 of 4 FirstFirst 1234 LastLast
Results 14 to 26 of 41

Thread: Walk in freezer

  1. #14
    Join Date
    Feb 2008
    Location
    California
    Posts
    1,920
    egads man!

    what establishment can make due without their walk-in freezer? it's pushing a month now.

    Give us more info to fix this thing.

  2. #15
    Join Date
    Mar 2009
    Location
    Mid-Mo
    Posts
    2,526
    Slow an steady wins the race phase. Lol.

  3. #16
    Join Date
    Sep 2011
    Location
    Fayetteville, NC
    Posts
    122
    I bought that book refer for hvac techs. Pretty good information there.

    Slow and steady will keep the calls backing up and you will never get home

  4. #17
    Join Date
    Aug 2010
    Location
    Riverside California
    Posts
    22
    You are right . ,this unit was not working they were using 3 door reach-in. When i start they do not want the same guy working who change out the compressor a year ago. like i said box went down to20*F after getting info. from all the experties from hvactalk. I did accomlish a lot working on this unit. There is lot lot to be learned I will keep u updated I am going back tomorrow. I still believe system there is something wrong.

  5. #18
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    2,848
    There must be. Box should run 0 to -10
    Local 597 Service Fitter
    Metal Trade Journeyman

    PAY ME NOW OR PAY ME LATER

    It was working when I left...
    WWFD

  6. #19
    Join Date
    Aug 2010
    Location
    Riverside California
    Posts
    22
    Quote Originally Posted by 2sac View Post
    There must be. Box should run 0 to -10
    That's what iam trying to achieve

  7. #20
    Join Date
    Aug 2010
    Location
    Riverside California
    Posts
    22
    Quote Originally Posted by Phase Loss View Post
    egads man!

    what establishment can make due without their walk-in freezer? it's pushing a month now.

    Give us more info to fix this thing.
    You are right . ,this unit was not working at they were using 3 door reach-in. When i started they do not want the same guy working who change out the compressor a year ago. like i said box went down to20*F after getting info. from all the experties from hvactalk. I did accomlish a lot working on this unit,and still there is lot lot to be learned I will keep u updated I am going back tomorrow. I still believe the system is not running to it's full capacity

  8. #21
    Join Date
    May 2011
    Location
    Eastern Washington State
    Posts
    7
    not gonna lie I installed a pump down valve backwards once....we all know what that would cause..........needless to say that got fixed...

  9. #22
    2Sac nailed it on the head. Quit touching our equipment you hack.

  10. #23
    Join Date
    Oct 2012
    Location
    CA
    Posts
    218
    Quote Originally Posted by traviscmatthews View Post
    2Sac nailed it on the head. Quit touching our equipment you hack.
    Do you need a hug ?

  11. #24
    Join Date
    Jan 2006
    Location
    DFW Metroplex
    Posts
    4,910
    Quote Originally Posted by Qamar View Post
    check txv screen it's clean turn off avap.fan to see flow of refrigerant , frost was building all across evap coil follow sporlan instructions to adjust SH left unit running all night chk next morning box temp went down to 20*F. 1/4 turn stem to chk if it goes down further. I am debating if there is a mismatch. I have collected all the info.will do a serious anylisis.
    Obviously I'm a little behind the curve on replying here, but if you adjusted SH via Sporlan instructions - what did your final superheat reading come in at?

    Furthermore, when you started working on the unit the outside ambient was ~100F and head pressure was 350 psig - giving you an almost 30F condenser TD......which ain't right.

    After changing the LL solenoid valve, you stated the head pressure was reading 225 psig. What was the outside ambient?

    A guy shouldn't be horkin' around with the TXV until he's darn sure he has enough gas in the system....
    "The problem is the average person isn’t tuned in to lifelong learning, or going to seminars and so forth. If the information is not on television, and it’s not in the movies they watch, and it’s not in the few books that they buy, they don’t get it" - Jack Canfield

  12. #25
    Join Date
    Oct 2012
    Location
    Sandy, Utah
    Posts
    86
    If what you are describing is what I think you are. 1-very low suction pressure yet head pressure is normal or maybe a bit high? It sounds like you've done a good job cleaning up the system. Evacuating and putting the proper charge in. You've replaced the drier and the liquid line solenoid, correct?
    I would suspect that possibility that the power head assembly has lost it's charge which would shut off the expansion valve. Just a thought. I've had many powerhead's lose their bulb charge and it has some of the symptoms you've described. Also you can have a wax build-up that can plug up the txv. But again, you've cleaned up the system which should have taken care of that possible problem.
    Hope this might help.
    Mark

  13. #26
    Join Date
    Aug 2010
    Location
    Riverside California
    Posts
    22
    I almost gave up but next day i went back turned off the evap fan i see frost building up which gives me idea that that evap was not flashing gas because of fan running so i try looking for DTFD it was fried ireplaced DTFD unit went down to -5* so that was the problem thanks

Page 2 of 4 FirstFirst 1234 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •