New Evaporator and condenser installed . R-22
Hi guys. I just change out a evaporator and a condenser for a w/in ref. I notice the txv outlet is frosting where the spider going to coil. I running R-22 and my pressure is 50psi suction and 260 high side. Site glass is clear and temperature is 40- 38 F. It was running good for a week and the evaporator ice up. I deice coil and everything looks ok except frosting coming out the txv. Is this normal for r-22 ? Thanks Eric
-
08-15-2012, 06:27 AM #2
Professional Member
- Join Date
- Jun 2009
- Location
- Garland, TX
- Posts
- 349
-
08-15-2012, 10:15 AM #3
Professional Member*
- Join Date
- May 2008
- Location
- Myrtle Creek. Oregon
- Posts
- 182
Put a defrost clock on it!
a stupid question is a question you wont to ask, but don't
-
08-15-2012, 10:57 AM #4
Check the box for infiltration. Warm moist air will suck into the box through any opening and freeze on the coil. Check door gaskets and penetrations for line sets and electrical. Also check door closure and latch that they close and hold door sealed. Usually don't need defrost on coolers however if your box is beat up and full of gaps it may be the most cost effective solution as long as it makes set point. Oh ya and tell them not to prop door open.
-
08-15-2012, 11:11 AM #5Bear Rules: Keep our home <50% RH summer, controls mites/mold and very comfortable.
Provide 60-100 cfm of fresh air when occupied to purge indoor pollutants and keep window dry during cold weather. T-stat setup/setback +8 hrs. saves energy
Use +Merv 10 air filter. -Don't forget the "Golden Rule"
-
08-15-2012, 11:11 AM #6
Regular Guest
- Join Date
- Jun 2010
- Location
- Miami
- Posts
- 249
Wouldn't hurt to check evap superheat. Might need to open up the txv a bit.
-
08-16-2012, 02:08 AM #7
Regular Guest
- Join Date
- Aug 2012
- Posts
- 7
I notice some r-22 meduim temp system some sweat coming out the txv and some frost. I know r-12 doesnt frost.
-
08-16-2012, 02:10 AM #8
Regular Guest
- Join Date
- Aug 2012
- Posts
- 7
-
08-16-2012, 05:23 PM #9
-
08-16-2012, 10:39 PM #10
-
08-17-2012, 10:53 PM #11
I agree. I service 2 walk in coolers and 2 walk in freezers. Two run r12 and two r22. All have defrost timers. If the cooler was installed charged and left alone it probably would be fine. As soon as you add people into the mix it is over. They can't seem to close the doors! Not to mention plastic and all sorts of other trash that gets on the coil.
-
08-17-2012, 11:54 PM #12
Regular Guest
- Join Date
- Aug 2012
- Posts
- 7
How many defrost time you put per day and how long ?
-
08-18-2012, 10:58 AM #13
Professional Member
- Join Date
- Jul 2010
- Location
- So-Cal
- Posts
- 526
I usually put it for 15min 3 times during the day and 30-35 min about 2:00am.
I work for a fast food company that is not open 24hrs they leave around mid night so the 30-35min at that time is ok because no one is opening the door.
Never iced up again.