    Cold air down large staircases

    Hi, I have 1500 sq ft upstairs serviced by what should be an oversized 3 ton ac. It can't quite keep up when the temp is high 90s inside is over 80.
    There are two wide and open staircase going upstairs. Are they significantly contributing to the issue? How much of the cold air is "lost" to the other floor?

    Thanks. Steve

  2. #2
    Join Date
    Mar 2009
    Location
    Mount Holly, NC
    Posts
    9,064
    Post Likes
    the problem is threefold, one, you have cold air falling down the staircases, two, the warm air from down stairs is being pushed above it warming the air upstairs, and three, your attic is pummeling the ceiling with hot air, and radiant surface heating is occurring from the attic high temps as well.

    energy auditing is your friend.
    The TRUE highest cost system is the system not installed properly...

    Find a HVAC-Talk Contractor by clicking here

    Click below to BECOME a pro member
    https://hvac-talk.com/vbb/forumdispl...ip-Information

    Do you go to a boat repairman with a sinking boat, and tell him to put in a bigger motor when he tells you to fix the holes?

    I am yourmrfixit

  3. #3
    Join Date
    Apr 2012
    Location
    Princeton NJ
    Posts
    125
    Post Likes
    Thread Starter
    Ok but besides adding more insulation to the attic I wonder if there is anything else (1995 house well constructed)

    And that also means that the 4.1 cooling load for the 1st floor is too high for my new ac to be installed in 2 days! Any way to estimate the cooling contribution? Any other fixes? Some sort of cross floor air circulator?

  4. #4
    Join Date
    Dec 2010
    Location
    The Quad-Cities area (midwest).
    Posts
    2,927
    Post Likes
    Quote Originally Posted by central nj View Post
    Hi, I have 1500 sq ft upstairs serviced by what should be an oversized 3 ton ac. It can't quite keep up when the temp is high 90s inside is over 80.
    There are two wide and open staircase going upstairs. Are they significantly contributing to the issue? How much of the cold air is "lost" to the other floor?

    Thanks. Steve
    The way I read your post is that you have a 3 ton A/C just for the (1,500 s.f.) 2nd floor? Do you have a A/C system cooling the lower level?

  5. #5
    Join Date
    Dec 2004
    Location
    Grand Rapids, MI
    Posts
    670
    Post Likes
    were are the second floor returns ?
    luck dan

  6. #6
    Join Date
    Dec 2005
    Location
    Cincinnati, Oh
    Posts
    11,829
    Post Likes
    Quote Originally Posted by central nj View Post
    Ok but besides adding more insulation to the attic I wonder if there is anything else (1995 house well constructed)
    I just came from a "well constructed" 1999 home. Got up in the attic, There was a 10'x10' space that the insulators didn't blow celulose into, I guess because it was hard to get to. That, and half the attic only had 4" of celulose (which is worth about nothing).

    That, and the massive attic (enough to play football in) only had 5, 6" roof vents, so no attic ventilation. It's been about 85-90* for the last 3 days, and about 130* in the attic.

    Guess what? The second floor doesn't cool correctly.
    Thats todays standard of "well constructed".

    Energy audit.
    "Better tell the sandman to stay away, because we're gonna be workin on this one all night."

    "Dude, you need more than 2 wires to a condenser to run a 2 stage heatpump."

    "Just get it done son."

    Dad adjusted

  7. #7
    Join Date
    Jun 2001
    Location
    Moore, Oklahoma, United States
    Posts
    4,648
    Post Likes
    1st things I would check are the air filters and the condenser (outside part) to make they are clean. These are the 2 most common causes of poor cooling complaints.

  8. #8
    Join Date
    Oct 2010
    Location
    Anderson, South Carolina, United States
    Posts
    21,019
    Post Likes
    Just because a house was recently built doesn't mean it was built well

  9. #9
    Join Date
    Apr 2012
    Location
    Princeton NJ
    Posts
    125
    Post Likes
    Thread Starter
    Ok, thanks for the comments so far. 54regcag--had had the unit recently seviced, but it is 17 years old.

    Jtrammel, good point. Will have someone look into it.

    George2---yes. Two systems. Will be 4 tons downstairs. This great forum convinced me to literally beg the company to downsize from 5 to 4 tons for first floor. I had to sign a waiver. The load was 4.0-4.3.

    Mr. Hvacvegas sir (thanks for help on other posts!!!)--got your point. I will have it looked at, good point.

    Daniel Workbee—there are 5 low down near the floor, 16x10 return grills, one in each room, and one in the hall. 8 supplies in the ceiling (one in each room, bathrooms, 2 in the hall).

    Maybe make the kids close the doors to all rooms? Would that kind of trap the cold air up stairs?

    Regardless, how big of a cooling loss are the double open stairways? Will it mess up the load that was done for my downstairs unit?

    Thanks
    Steve

  10. #10
    Join Date
    Dec 2005
    Location
    Cincinnati, Oh
    Posts
    11,829
    Post Likes
    Quote Originally Posted by central nj View Post
    Ok, thanks for the comments so far. 54regcag--had had the unit recently seviced, but it is 17 years old.

    Jtrammel, good point. Will have someone look into it.

    George2---yes. Two systems. Will be 4 tons downstairs. This great forum convinced me to literally beg the company to downsize from 5 to 4 tons for first floor. I had to sign a waiver. The load was 4.0-4.3.

    Mr. Hvacvegas sir (thanks for help on other posts!!!)--got your point. I will have it looked at, good point.

    Daniel Workbee—there are 5 low down near the floor, 16x10 return grills, one in each room, and one in the hall. 8 supplies in the ceiling (one in each room, bathrooms, 2 in the hall).

    Maybe make the kids close the doors to all rooms? Would that kind of trap the cold air up stairs?

    Regardless, how big of a cooling loss are the double open stairways? Will it mess up the load that was done for my downstairs unit?

    Thanks
    Steve
    It's called "stack effect". Look up in wikipedia for more information. Learn alot about it for air sealing your home.

    Your thinking the other way around though. If it's comfortable downstairs, but not upstairs, then keeping it open would help suck the heat downstairs. Heat always moves to cold, more so than "heat rises".

    Unless I'm just tired and thinking backwards.
    "Better tell the sandman to stay away, because we're gonna be workin on this one all night."

    "Dude, you need more than 2 wires to a condenser to run a 2 stage heatpump."

    "Just get it done son."

    Dad adjusted

  11. #11
    Join Date
    May 2004
    Location
    south louisiana
    Posts
    3,790
    Post Likes
    besides adding more insulation to the attic I wonder if there is anything else

    lots of anything elses...adding insulation over air leaks is wasting money.
    air sealing goes a long way to allowing insulation to perform.
    air moving through insulation reduces insulation values.

    living space walls that are shared with attic space have lots
    of heat gain from hot attics. insulation alone doesn't do much
    to solve these issues. if you insulate and then air seal the wall
    with foam sheathing boards, then the living space is easier
    to cool. and heat in winter time.

    I'm not hearing good things about nj clean energy free audits.
    it may be a starting point, but hiring an indpendent rater/auditor
    would give you unbiased information that could save you much
    more than minimal savings through utility sponsored audits.

    best of luck.
    The cure of the part should not be attempted without the cure of the whole. ~Plato

  12. #12
    Join Date
    Jan 2009
    Location
    SE Iowa
    Posts
    5,577
    Post Likes
    Quote Originally Posted by jtrammel View Post
    Just because a house was recently built doesn't mean it was built well
    Very sad and very true.

    What hasn't been mentioned, is that much of the air movement down the stairs is partly due to reverse stack effect. Air leaks upstairs and cause warm humid air in the summer to leak in, and conditioned air leak out downstairs. The flow is reversed in winter.

    The layout plays a major role, but I have a very wide open stairwell and there is cool air rolling down the stairs, but overall the upstairs is mostly isolated from the downstairs.

    I would focus on attic insulation and air leaks (can lights, bath fans, ceiling fixtures) and attic venting.

  13. #13
    Join Date
    Jul 2005
    Posts
    7,834
    Post Likes
    It's premature to blame the capacity issue on infiltration. Have the unit checked out, then take it from there. There are several different issues that can result in low capacity.

  14. #14
    Join Date
    Aug 2003
    Location
    Fort Worth, TX
    Posts
    11,847
    Post Likes
    Quote Originally Posted by hvacrmedic View Post
    It's premature to blame the capacity issue on infiltration. Have the unit checked out, then take it from there. There are several different issues that can result in low capacity.
    This. As much as I appreciate building science, the first question I would be compelled to ask the OP is if the upstairs system NEVER kept that area comfortable. If the answer is no, it once did keep things comfy, even on hot days, the system needs attention. If the answer is yes, it never has made things comfy, ever, the solution may lie between HVAC system design and the building envelope.
    Psychrometrics: the very foundation of HVAC. A comfort troubleshooter's best friend.

  15. #15
    Join Date
    Apr 2012
    Location
    Princeton NJ
    Posts
    125
    Post Likes
    Thread Starter
    Hi, thanks. Lived in the house 2 years so don't know more than that, and i was told the unit is fine.

    I just went through the trauma of having inadequate returns downstairs-- very inadequate (different post)

    The 5 return registers are wall/between stud jobs, 4x14, supplying 180 cfm by tables i looked at, so 900 cfm total. I need 3 tons (1200 cfm). I'm guessing it is close enough? If not is there a test to know if the return are is adequate?

  16. #16
    Join Date
    Jan 2009
    Location
    SE Iowa
    Posts
    5,577
    Post Likes
    No "Test" really needed. Just a tape measure and a calculator. For a return plenum you want to be under 700 feet per minute velocity, 500 even better. SO you calculate the square foot cross sectional area, then divide the nominal CFM by the area.

    Now, to know exactly what is being delivered, you'll have to measure static pressure across the blower and use a table that shows the performance data of the blower... which is included in the installation manual or data sheets. IN your case, newer limber is not full dimension, so the wall avity I think would be 14-1/2 x 3-1/2. SO that's 51sqin and divided by 144 is 0.354 sqft. 5 of those are 1.77sqft. SO 1200/1.77 = 678 fpm. Not too bad. 1 more retrun would be better. The next question would be the size of the main retrun trunk.

  17. #17
    Join Date
    Aug 2003
    Location
    Fort Worth, TX
    Posts
    11,847
    Post Likes
    Quote Originally Posted by motoguy128 View Post
    No "Test" really needed. Just a tape measure and a calculator. For a return plenum you want to be under 700 feet per minute velocity, 500 even better. SO you calculate the square foot cross sectional area, then divide the nominal CFM by the area.

    Now, to know exactly what is being delivered, you'll have to measure static pressure across the blower and use a table that shows the performance data of the blower... which is included in the installation manual or data sheets. IN your case, newer limber is not full dimension, so the wall avity I think would be 14-1/2 x 3-1/2. SO that's 51sqin and divided by 144 is 0.354 sqft. 5 of those are 1.77sqft. SO 1200/1.77 = 678 fpm. Not too bad. 1 more retrun would be better. The next question would be the size of the main retrun trunk.
    That would not include the aK of the grill or filter grill, of course. Take that and then see how well each stud cavity draws. Not to mention what else a stud cavity introduces into the return air stream. And what that does to the pressurization of the house.

    Stud cavities and/or panned joists used as supply or return air paths should be against code, period. Doesn't mean nobody will still do it, but regardless.

    There have been numerous threads concerning multi-story homes and unacceptable temperature variances between floors. Many with one system serving two floors. The OP's house in this thread has two systems, one per floor, and comfort is still a problem. As in other threads with a similar topic, stud cavity based return paths are involved. I'm confident these aren't the sole culprit, as the only way to really get a grip what's going on is to be at the house and take note of everything in sight relevant to the HVAC and building enclosure. That said, give me a hot day, an infrared camera, a digital psychrometer, a gauge manifold, a flow hood, and a few hours and I'd love to be in a house like that to get data on what's really going on.

    Therefore the pros who have suggested an energy audit may be giving the OP the best advice, coupled together with having a competent HVAC pro thoroughly go through the systems to catch any performance robbing problems.
    Psychrometrics: the very foundation of HVAC. A comfort troubleshooter's best friend.

  18. #18
    Join Date
    Apr 2012
    Location
    Princeton NJ
    Posts
    125
    Post Likes
    Thread Starter
    Mr. Motoguy128—you are the best! Thanks for the very specific help.

    The plenum is I believe silvery fiber board (or wrapped duct?) 17x12 inches (or take 1 inch off if some is insulation at 16x11). That works out to 983 – 845 fpm. There is ?5 inch media filter at 16x15 (kind of 444 fpm) just before the furnace

    If I have my duct guy expand the plenum to 16x15, and make whatever branches are adequate, would I see substantial improvement in cooling?

  19. #19
    Join Date
    Apr 2012
    Location
    Princeton NJ
    Posts
    125
    Post Likes
    Thread Starter
    I'm thrilled! I was just up in the attic:

    The returns are on a long (t) duct, 14x14, but three on one side, and two on the other. So Mr. Motoguy's fpm are under 600.

    Well, they used a three foot section of 12 inch flex duct (fpm 1667?) to connect to the run to the furnace!

    So, if I just change the 10 foot or so run up to the attic (to 16x25) and replace the flex with something big (like 14x25) shouldn't that make a big difference. Or am I just being hopeful?


    P.S. Shophound—there are bare spots up there, some of the can lights aren't covered. When the ducts are fixed i'll definitely have someone pad things up. Thanks for the comment (as depressing as it was). Steve

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •