    Blower on delay for better humidity control?

    What are your thoughts about delaying the blower turn on for about 30 seconds so the A-coil has a chance to get cold? Would this result in significantly lower humidity during part load conditions?

  2. #2
    Join Date
    Jan 2011
    Location
    Washington, D.C.
    Posts
    58
    Post Likes
    If the CFM is set correctly for the appropriate btu and the chagre is set according to proper conditions, would it make a difference in humidty contol if the blower has a 30 sec delay seeing that the system has been commisioned for optimal effeciency? I belive that a properly commissioned A/C system will remove humidty and perform much better under any load condition.

  3. #3
    Join Date
    May 2000
    Location
    Indianapolis, IN, USA
    Posts
    42,886
    Post Likes
    Seems to me ICP used to do it that way. Or some variable speed systems offer slow start as one of their dehum profiles.

  4. #4
    Join Date
    Jun 2003
    Location
    Madison, WI/Cape Coral, FL
    Posts
    12,042
    Post Likes
    A 30 sec delay makes a very minor differecnce in the amount of mositure the ac removes. It's more important to have a very cold coil to remove moisture from the air. The length of cooling cycle is also very important. The cooling cycle must be long enough to saturate the cooling coil and pan and allow a significant amount of moisture to go down the drain. It takes 20-40 mins for moisture to start to drip to the drain. Coils hold +1lb. of moistue per ton before they start dripping to the drain. At the end of cycle, all the moisture on the coil evaporates back into the home. So time delays are a few drops. When the outdoor dew points are +55^F without significant cooling loads, a good dehumidifier is important for good humidifier is important.
    Regards TB
    Bear Rules: Keep our home <50% RH summer, controls mites/mold and very comfortable.
    Provide 60-100 cfm of fresh air when occupied to purge indoor pollutants and keep window dry during cold weather. T-stat setup/setback +8 hrs. saves energy
    Use +Merv 10 air filter. -Don't forget the "Golden Rule"

  5. #5
    Join Date
    May 2000
    Location
    Indianapolis, IN, USA
    Posts
    42,886
    Post Likes
    I have a chart somewhere based on data given to me by the product manager of a major brand as high SEER (12-13 back then) came out. While an oldie might have said evap very cold after 5 minutes, a newer unit with big coil and higher suction may take 10 minutes. So more critical than ever not to oversize. We often suggest downsizing based on our calcs, our nearest competitor tends to want to go bigger.

  6. #6
    Join Date
    Dec 2002
    Location
    Houston,Texas
    Posts
    23,010
    Post Likes
    Quote Originally Posted by teddy bear View Post
    It takes 20-40 mins for moisture to start to drip to the drain..
    Were in Arizona? We installed a Ruud system with a N-coil on Monday, system had been down for 2 days, 10 minutes of start up was producing a lot of water running through the T, you could look down into the T with your flashlight and the T was half full it was moving so much water.
    __________________________________________________ _______________________
    “Experience is a hard teacher because she gives the test first, the lesson afterwards" ~ Vernon Law

    "It's what you learn after you know it all that counts." ~ John Wooden

    "When the teachers become unteachable we're all in trouble" ~ Mr. Bill

    "Remember "Pro" is only a name, it's not always a mindset determined to do everything correctly" ~ Mr. Bill




  7. #7
    Join Date
    Aug 2004
    Location
    Missouri
    Posts
    15
    Post Likes
    From what I've learned on time delays on cooling, they are on to remove moisture off of the coil, to help reduce the possibility of mold. That is what I was told from Carrier when I asked about their 5 ton RTU fan delay.

  8. #8
    Join Date
    Jun 2003
    Location
    Madison, WI/Cape Coral, FL
    Posts
    12,042
    Post Likes
    Quote Originally Posted by Mr Bill View Post
    We installed a Ruud system with a N-coil on Monday, system had been down for 2 days, 10 minutes of start up was producing a lot of water running through the T, you could look down into the T with your flashlight and the T was half full it was moving so much water.
    I tested several dry coils with 75^F, 50%RH with similar results. A/c down for two days in Huston is probably very high indoor %RH with result in much more moisture in the air removed than <50%RH where a controlled space is.
    Try a dry coil and the space 50%RH, report the time. I did a VS a/c on low speed last week, took 45 mins, to start dripping. The unit removed <3 lbs. per hour on low speed. At the end of the cooling cycle, the moisture evaporated back into the space. If the cooling cycle is <45min.,after re-evaporation back into the home, no net moisture will be removed from the home.
    Regards TB
    Bear Rules: Keep our home <50% RH summer, controls mites/mold and very comfortable.
    Provide 60-100 cfm of fresh air when occupied to purge indoor pollutants and keep window dry during cold weather. T-stat setup/setback +8 hrs. saves energy
    Use +Merv 10 air filter. -Don't forget the "Golden Rule"

  9. #9
    Join Date
    Dec 2002
    Location
    Houston,Texas
    Posts
    23,010
    Post Likes
    Quote Originally Posted by teddy bear View Post
    Try a dry coil and the space 50%RH, report the time..
    Yes I have to admit, it was 100° outside with probably a 80% RH.
    __________________________________________________ _______________________
    “Experience is a hard teacher because she gives the test first, the lesson afterwards" ~ Vernon Law

    "It's what you learn after you know it all that counts." ~ John Wooden

    "When the teachers become unteachable we're all in trouble" ~ Mr. Bill

    "Remember "Pro" is only a name, it's not always a mindset determined to do everything correctly" ~ Mr. Bill




  10. #10
    Join Date
    Dec 2008
    Location
    Ontario Canada
    Posts
    758
    Post Likes
    Quote Originally Posted by BaldLoonie View Post
    I have a chart somewhere based on data given to me by the product manager of a major brand as high SEER (12-13 back then) came out. While an oldie might have said evap very cold after 5 minutes, a newer unit with big coil and higher suction may take 10 minutes. So more critical than ever not to oversize. We often suggest downsizing based on our calcs, our nearest competitor tends to want to go bigger.
    I agree, I'm a big fan of under sizing, on the right job

  11. #11
    Join Date
    Jul 2011
    Posts
    117
    Post Likes
    wow all this high tech formula talk.. Make sure it has a txv, before even dreaming about a delay...



    I have seen some very retarded stuff the past year and a half...

  12. #12
    Join Date
    Dec 2011
    Location
    bedford ind
    Posts
    1,103
    Post Likes
    Under sizing or over sizing based on your load calcs?

    Aren't load calcs supposed to be accurate? Is there a calc for under sizing and one for over sizing?

    If so, why have one for correct sizing , if correct sizing is wrong, which would then be understood that the over and under size calcs are correct, even though they are wrong?

    Or do we just put in a system that is wrong according to the correct load calc?

    Is that right?

  13. #13
    Join Date
    Dec 2011
    Location
    bedford ind
    Posts
    1,103
    Post Likes
    Where's bunny? She would love this!

  14. #14
    Join Date
    Dec 2002
    Location
    in a house, Appomattox, Va.
    Posts
    5,598
    Post Likes
    some of the variable speed units have a dehumidify mode to drop the blower speed the entire run cycle- activated by a dehumidistat.

    my mom's house has a little control from Lennox- you set it for dryer and it kicks over a relay to drop to a lower blower speed- but you could use a regular dehumidistat and relay to get the same effect. drops a psc motor to the next lower speed.

    both of these increase dehum, but only when the unit is running. and a txv would be a better setup if the airflow is cut well back.

    won't work on a cool day when the a/c only runs 5 min/hr at a time. That's where a whole house dehum would come in.
    Last edited by billygoat22; 08-27-2012 at 09:18 PM. Reason: fat fingers
    Col 3:23


    questions asked, answers received, ignorance abated

  15. #15
    Join Date
    Dec 2002
    Location
    in a house, Appomattox, Va.
    Posts
    5,598
    Post Likes
    Didn't central city hvac do a custom setup yrs ago?
    Col 3:23


    questions asked, answers received, ignorance abated

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •