    High pressure switch
    What could cause a high pressure switch to trip when the unit hasn't run in 6 days. Unit was running fine for the whole summer. Homeowner says he shut it off 6 days ago. Turns it on today and the condenser wouldn't start. It's a ducane with a manual reset high pressure switch. Is it possible for it to trip if it's not running?
    Aug 2012
    MA
    Quote Originally Posted by BPToilman View Post
    So have you looked at the unit yet? If not I would ask, how does the home owner know its the switch? Also ditch the manual switch and hook em up with a auto one, they are cheap enough....
    Jul 2012
    Stratford
    I reset the switch. I looked at it this afternoon. Funny thing is, it hasn't been hot here. Not humid and I know the unit hasn't run.
    Houston,Tx.
    Quote Originally Posted by pecker head View Post
    Auto high pressure?
    Aug 2012
    Toronto, Canada
    Lol!! I second mr Bills post! Why not do one better and just bypass the hp switch!! That'll solve your problem.. It's only a safety ...
    You reset the switch and then wat??? What readings did you get??
    Jul 2012
    Phoenix, AZ
    Sounds like a DIY to me wrong page buddy.
    A couple things cn cause what your describing. Most likely it did run(for a few seconds), and then the HPS tripped.
    Need to take pressure nd temp readings to find out the cause of the high pressure.
    Jul 2012
    Stratford
    Not a do it yourself buddy. It was 9:30 at night. No pressure readings. Didn't know if it was possible for pressures to spike on the start like that after it had run fun and there wasn't a heavy load on the unit.
    They can, seen it on more then one.
    Jul 2012
    Stratford
    Looks like the txv is sticking. I had a high side pressure of 390 and a suction line pressure of 125. 80 degrees out here today. I couldnt see the pressures fluctuate at all.
    Jul 2009
    Columbia, MD
    dirty coil, over charged, oil logging in condenser, no fan.....
    Jul 2009
    Columbia, MD
    what do you mean txv is sticking? looks like r410a? those pressures look like the valve is open to me.
    80* ambient and 390 hi side???
    dirty coil or over charged
    Jul 2012
    Stratford
    I would think that with the pressure that high it would be closed, or stuck half way open? I know the coil is clean. It is 410