Results 14 to 20 of 20
    ottawa canada
    I just checked screwits attached drawing and its the auxillary contact in the AFD (5U2 ) that locks in the AFD after the momentary start signal from the starter module . I suspect this is your problem .
    Quote Originally Posted by Screwit View Post
    ...Hard to speed type with one finger
    which finger? oh wait....I know which one!
    A land down under
    Quote Originally Posted by jayguy View Post
    Yep, it is a bit of a multi-purpose tool
    Necessity is the mother of invention
    Quote Originally Posted by Michael demny View Post
    ...We are going to bypass the NC high pressure switch and verify the momentary power loss and phase reversal are still disabled and try again.
    that is a pretty expensive motor replacement to keep disabling safties like that.
    Aug 2009
    Prattville, Alabama
    I have increased the VFD's starting ramp time to make it an across the line inrush and the chiller will start and operate correctly.
    For how long? Will it fully load up? If not, how much will it load?
    Aug 2012
    The fastpack is configured for an AFDB starter with 1500:5 CT's. With this starter configuration we do not get the phase reversal option. We did bypass the High pressure switch and still no luck same phase loss at shutdown. I will look at the lock in wiring and see how it works with this VFD
    Aug 2012
    The chiller once started will operate until the stop signal is given. Loads to 100% and contols correctly. The VFD has the phase reversal, power monitoring over under voltage and phase loss built into its software. So the Trane Fastpak software is a redundant backup