  1. #14
    Join Date
    Mar 2004
    Location
    ottawa canada
    Posts
    2,111
    I just checked screwits attached drawing and its the auxillary contact in the AFD (5U2 ) that locks in the AFD after the momentary start signal from the starter module . I suspect this is your problem .
    The toy chest is officially full ... I got a new toy..... 2007 Aston Martin V8 Vantage
    You bend em" I"ll mend em" !!!!!!!
    I"m not a service tech.. I"m a thermodynamic transfer analyst & strategic system sustainability specialist
    Best Austin Healey In Show twice in 2013 .....All those hrs paid off .

  2. #15
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    4,530
    Quote Originally Posted by Screwit View Post
    ...Hard to speed type with one finger
    which finger? oh wait....I know which one!
    "If you pull one more stunt like you just pulled with Tommy, you won't have to get on a plane because I will personally kick your ass from here to Korea!" - Best of the Best

  3. #16
    Join Date
    Sep 2008
    Location
    A land down under
    Posts
    315
    Quote Originally Posted by jayguy View Post
    which finger? oh wait....I know which one!
    Yep, it is a bit of a multi-purpose tool
    Necessity is the mother of invention

  4. #17
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    4,530
    Quote Originally Posted by Michael demny View Post
    ...We are going to bypass the NC high pressure switch and verify the momentary power loss and phase reversal are still disabled and try again.
    that is a pretty expensive motor replacement to keep disabling safties like that.
    "If you pull one more stunt like you just pulled with Tommy, you won't have to get on a plane because I will personally kick your ass from here to Korea!" - Best of the Best

  5. #18
    Join Date
    Aug 2009
    Location
    Prattville, Alabama
    Posts
    2,145
    Quote Originally Posted by Michael demny View Post
    I have increased the VFD's starting ramp time to make it an across the line inrush and the chiller will start and operate correctly.
    For how long? Will it fully load up? If not, how much will it load?

  6. #19
    The fastpack is configured for an AFDB starter with 1500:5 CT's. With this starter configuration we do not get the phase reversal option. We did bypass the High pressure switch and still no luck same phase loss at shutdown. I will look at the lock in wiring and see how it works with this VFD

  7. #20
    The chiller once started will operate until the stop signal is given. Loads to 100% and contols correctly. The VFD has the phase reversal, power monitoring over under voltage and phase loss built into its software. So the Trane Fastpak software is a redundant backup

Page 2 of 2 FirstFirst 12

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event