    Find the Problel 8/2012

    10 Ton Trane Pkg Gas Rooftop Install 208/230 V 3Phase
    Attached Images Attached Images  

  2. #2
    Join Date
    Feb 2006
    Location
    USA
    Posts
    4,381
    Post Likes
    Is that green wire a ground ?

    Sent from my SCH-I800 using Tapatalk 2

  3. #3
    Join Date
    Aug 2008
    Posts
    214
    Post Likes
    Hmm NO!

  4. #4
    Join Date
    Jul 2007
    Location
    Virginia
    Posts
    442
    Post Likes
    Looks like the line side wiring is undersized, in the pic it appears to be 10ga wire. Should have been at least 6ga wire going to that terminal block.
    When you do a job, Always make it easier for the next guy, because you may be the next guy working on it.

  5. #5
    Join Date
    Aug 2008
    Posts
    214
    Post Likes
    It is at least a 6 may be a 4.

  6. #6
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    5,355
    Post Likes
    That's what they call a single phase conversion. Attach the green wire to the terminal block and it becomes 3 phase.
    Officially, Down for the count

    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET

    I know enough to know, I don't know enough
    Liberalism-Ideas so good they mandate them

  7. #7
    Join Date
    May 2011
    Location
    Western, KY
    Posts
    3,294
    Post Likes
    There's a mess in the bottom left of the screen I cant make heads or tails of and it looks like one or more wires have the insulation tucked under the screw.

  8. #8
    Join Date
    Jul 2009
    Location
    Columbia, MD
    Posts
    4,860
    Post Likes
    its 208 volts and the tap on the transformer is at 230

    i was also seeing the insulation under the screw

  9. #9
    Join Date
    Sep 2010
    Location
    Western, MO
    Posts
    874
    Post Likes
    Not sure if the middle leg got pushed in all the way. And why are there jelly fish swimming just below the terminal block?

    jim
    Common sense isn't very common anymore.

  10. #10
    Join Date
    Aug 2008
    Posts
    214
    Post Likes
    10 ton 208/230 v 3 Phase Trane gas Pack. The Green wire is used as a HOT Leg of Power. And There is not a proper Ground to this unit. To top it off this is located on the "Former City Hall" Where the Inspectors office was at the time of install 10 years ago.

  11. #11
    Join Date
    Sep 2005
    Location
    Atlanta GA area
    Posts
    25,057
    Post Likes
    Quote Originally Posted by AC Shop View Post
    10 ton 208/230 v 3 Phase Trane gas Pack. The Green wire is used as a HOT Leg of Power. And There is not a proper Ground to this unit. To top it off this is located on the "Former City Hall" Where the Inspectors office was at the time of install 10 years ago.
    Classic!

    Inspectors are NOT about safety, they are about an easy income... Actually, to a degree they seem to have an entitlement mentality (like everyone else on the govt dole... payroll or non-working).
    GA-HVAC-Tech

    Quality work at a fair price with excellent customer service!

    Romans Ch's 5-6-7-8

    2 Chronicles 7:14

  12. #12
    Join Date
    Sep 2006
    Location
    Burnaby, BC
    Posts
    349
    Post Likes
    Got a little warm at one point, did it?


    ---------------------------------
    Please excuse me if my post looks like it was typed by a teenager. It was sent from my phone.
    I do three kinds of work.
    1 - Good - 2 - Fast - 3 - Cheap
    Pick two

  13. #13
    Join Date
    Oct 2011
    Location
    Cicero, IN.
    Posts
    61
    Post Likes
    Electricity does not care what color the wire is.