    So, after hearing lots of helpful advice here I decided to forego the Bryant or Weil Mclain quotes I received and get some estimates for a Buderus oil boiler.

    First guy gave me a quote for a Buderus G115ws-5, with Reillo burner, Logomatic control, and tank ST150. Obviously more expensive than Bryant/weil but not too bad.

    Second guy is a Buderus dealer but says he will not sell Buderus Logomatic controls because they are a service nightmare. He is recommending a Burnham MPO-IQ115. Price is similar to the Buderus package.


    So, which one do I go with and why?

  2. #2
    Join Date
    Nov 2011
    Location
    Long Island, NY
    Posts
    280
    The Logamatic is a fine control, does a lot of different things. But the outdoor reset curve does need to be "tuned" to the house for maximum comfort and savings. It is better to get the customer involved and understand the curve setting process. I happen to be partial to the Buderus, but there is probably nothing wrong with the Burnham unit.

    Why are we quoting a five section boiler? Has anyone done or estimated a heat loss?

  3. #3
    Join Date
    Aug 2012
    Posts
    53
    Tell you the truth, I am not sure whether anyone did a heat loss calculation. They at least asked for the square footage of the house. it is a stone house (thick stone walls), built in 1940, older windows with storm windows.

  4. #4
    Join Date
    Aug 2012
    Posts
    53
    should have also said 2400 sq ft.

  5. #5
    Join Date
    Nov 2011
    Location
    Long Island, NY
    Posts
    280
    What part of the country are you located?

  6. #6
    Join Date
    Aug 2012
    Posts
    53
    S.E. Pa. - just outside Philly.

  7. #7
    Join Date
    Nov 2011
    Location
    Long Island, NY
    Posts
    280
    I'll wager a g115/3 would heat the house fine. I have one in a 3000 sq ft McMansion on Long Island and it heats just fine. You do need to take into account the local conditions and some specifics like homes with a lot of glass and/or infiltration, pretty much what a heat loss tells you. Bigger is NOT better with boilers! It only leads to higher fuel consumption.
    Attached Images Attached Images  

  8. #8
    Join Date
    Aug 2012
    Posts
    53
    One guy told me that he would use a 5 section because I have older 2-2.5 inch pipes, and there is a lot of water in the system to heat. Does that make sense?

    BTW, do you have a logamitc control?

  9. #9
    Join Date
    Nov 2011
    Location
    Long Island, NY
    Posts
    280
    If you have a large volume of water in the system your supposed to pipe the boiler "primary-secondary piping" or some other type of boiler protection to combat condensation issues, boiler size really has nothing to do with it.

    I have the Logamatic in my own home, yes.

  10. #10
    Join Date
    Sep 2002
    Location
    Northeast Ohio
    Posts
    4,842
    We have several of the Burnham MPOs running in the field, no problems what so ever. And I agree on the primary secondary piping arrangement. 20 years ago hardly saw them at all, today, most of what we pipe is primary secondary.
    A good HVAC tech knows how, an educated HVAC tech knows why!

    DEM


  11. #11
    Join Date
    Oct 2009
    Location
    God's country - Shenandoah Valley, VA
    Posts
    362

    Make Them do a Load Calc.

    Quote Originally Posted by newlyn View Post
    One guy told me that he would use a 5 section because I have older 2-2.5 inch pipes, and there is a lot of water in the system to heat. Does that make sense?

    BTW, do you have a logamitc control?

    The size of the pipes does NOT determine the size of the boiler. You probably have a converted gravity flow system. This is not a problem and can actually be beneficial as the volume of water in the pipes serves as a buffer that will help prevent short cycling of the boiler.

    As others have stated, it should be piped primary/secondary.

    I agree with Ron that a three section G115 would probably be sufficient. The Buderus can be upfired by 10%.

    Both are good boilers. I would give the Buderus the edge with its flexible cast iron. I'm a dealer for both.


    Have you tried the contractor search on this forum? Heatinghelp.com also has one.

  12. #12
    Join Date
    Jan 2012
    Location
    Broomall, PA
    Posts
    398
    Concur with the others about getting a total heat loss. I'm in your area, about the same size house, MPO-115 w/ and indirect. But I'm very insulated.

  13. #13
    Join Date
    Oct 2009
    Location
    God's country - Shenandoah Valley, VA
    Posts
    362
    Quote Originally Posted by newlyn View Post
    S.E. Pa. - just outside Philly.
    I'd recommend that you contact STEVEusaPA.
    Bob Boan


    ​You can choose to do what you want, but you cannot choose the consequences.

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event