Results 1 to 13 of 13
Thread: Ice machine and walking cooler
-
08-21-2012, 03:08 AM #1
Regular Guest
- Join Date
- Aug 2010
- Location
- Riverside California
- Posts
- 22
Ice machine and walking cooler
Manitowoc 0605WQY Ice machine dumping water all the time replace dump valve same thing need help
I am working on walk in freezer R404A condesing unit ,it was short cycling for 5-10 seconds. The H.p was once 300psi, L.P was 0. upon playing W/ the dual pressure switch ,system would kick in, clean cond coil H.P drop to 200 Psi. Then I close liquid line service valve to pump down system it stops but when I open L.L service system dosent kick in. it only cycles for a few seconds. I changed start and the run capicator . which shorted out the start capicitor again L.P was 115# H.P was 200#.I lowered the S.P and changed the start capicator it still does the same thing. I put TXV bulb in ice cold water as box temp was over 80*. Any advice or assistance would be appreciated. thanks
I first posted on tech to tech chat follow the advice correct starting problem by changing s/c, r/c and potential relay unit ran but the problem was l.l solenoid valve replace w/new replace l.l filter dryer pull vacuum for 2 hrs now the box temp does'nt go lower than 65* h.p is 275#-300# s.p is25#-30# Amps are r6.5 s9.8 c10.2 there is a frost on outlet of txv, sight glass has bubbles it is responding to pump down. Now iam thinking of replacing or cleaning txv any thought .
-
08-21-2012, 08:16 AM #2
Professional Member*
- Join Date
- Jun 2009
- Location
- Owen Sound
- Posts
- 22
Not enough info. What is ambient temp around condenser? compression ratio is way down. are you just very low on charge? is there a low pressure switch causing the cycling? i'de almost bet your money that there is.
-
08-21-2012, 08:18 AM #3
Professional Member*
- Join Date
- Jun 2009
- Location
- Owen Sound
- Posts
- 22
-
08-21-2012, 08:20 AM #4
This is a bit confusing. Lets take it in chunks:
- at this point, the unit was attempting to cycle off - the low pressure switch should have shut it down. Either the liquid solenoid was closed, or a service valve was. Correct the LP side of the dual pressure switch.
Did it start up at all? If yes, I don't understand why you keep messing with the start components. The reason it is shutting back down is the suction is still to low.
Can you confirm that the LL solenoid opens and closes (can you pump down with the solenoid)?
You say the box is at 65* with these pressures? You still have a restriction. Make sure all your service valves are open. The TXV would be the next suspect. Why are you putting it in ice water? Not sure if you are trying to make it open or close? This is a freezer, if the proper head is on it, it will be full open at 32* the same as 80* (or very similar). Put the bulb back where it goes.
You are still under charged! No bubbles!
-
08-21-2012, 11:02 AM #5
Regular Guest
- Join Date
- Aug 2010
- Location
- Riverside California
- Posts
- 22
Walking freezer
-
08-21-2012, 11:09 AM #6
Regular Guest
- Join Date
- Aug 2010
- Location
- Riverside California
- Posts
- 22
ambient is 95* I have no problem w/cycling now
H.P 275-300# S.P 25-30#
-
08-21-2012, 11:11 AM #7
Regular Guest
- Join Date
- Aug 2010
- Location
- Riverside California
- Posts
- 22
Yes it is ice machine
-
08-21-2012, 12:03 PM #8
Step away from your families equipment! And call a pro!!!!
-
08-21-2012, 01:38 PM #9
New Guest
- Join Date
- Jan 2010
- Location
- Ft. Walton Beach, FL
- Posts
- 2
Ice Machine
Think your machine may be more like a QY0605W. If that's the case, the W may be your problem.
-
08-21-2012, 02:22 PM #10
Where does one purchase replacement legs for a walking cooler and do they come with gym shoes or are those extra?
Local 597 Service Fitter
Metal Trade Journeyman
PAY ME NOW OR PAY ME LATER
It was working when I left...
WWFD
-
08-21-2012, 07:10 PM #11
-
08-21-2012, 08:15 PM #12
-
08-21-2012, 09:40 PM #13
Regular Guest
- Join Date
- Aug 2010
- Location
- Riverside California
- Posts
- 22
I am making effort to become a pro an my family equipment


Reply With Quote