Are mismatched evap coil and compressor sizes a bad idea?
Hi all, I posted earlier about some estimates we got. We got another one on a Trane today but this contractor is suggesting a 2 ton outdoor unit (max our electrical system can handle) paired with a 2.5 ton coil. He says this would cool better. Until the current coil failed on our 25 year old 2 ton Ruud, we didn't have any trouble keeping the house at 80 which is fine for us while we're home. (we live in the DC suburbs, so summers aren't particularly brutal, just humid) Does it make any sense to mismatch like this? None of the other contractors suggested this. What would the benefits to this be? Possible drawbacks?
-
08-21-2012, 09:56 AM #2
I believe if and old Indian Chief had a say today in this business, he would say, "much advise causes much confusion". This is why the more folks tire kick, the more confused they will be. I think it's great to get a couple/three bids, but everyone will have a different opinion and price. Back in the old school days, the 1/2 ton larger evaporator coil was very common, but this is a new age with newer technology, the best advise I can give you and I would hope most pro's here would agree is to, go strictly with what the mfg. of your equipment says is the best/perfect match, that way if down the line you encounter any issues and a mfg. rep. has to come out, your covered on your end.
“I am glad that I paid so little attention to good advice; had I abided by it I might have been saved from some of my most valuable mistakes.” - Edna St. Vincent Millay
The critic is a prisoner to his own experiences and perspectives, erroneously believing his limited experiences are the sum of all truth.
No Guns…No Freedom…Know Guns…Know Freedom.
-
08-21-2012, 10:58 AM #3
Professional Member*
- Join Date
- Dec 2010
- Location
- The Quad-Cities area (midwest).
- Posts
- 1,756
If you're only looking for a low SEER, you can match the coil size to the condenser.
If a higher SEER is desired, then normally a larger coil is necessary. A larger coil will not dehumidify the home as well, however.
It just depends on your goal.
-
08-21-2012, 12:02 PM #4
Regular Guest
- Join Date
- Aug 2012
- Posts
- 6
We're way more concerned about humidity than temperature. We run a dehumidifier downstairs frequently to combat the sticky air. Can I make sure I'm understanding correctly? Larger coil means more cooling surface area which would mean more cold air in a shorter amount of time, right? So the AC wouldn't run as much. But that would also mean the big coil wouldn't ever get as cold or stay cold as long which wouldn't let it suck as much moisture out of the air as if it was running colder and longer. Is that the general logic behind it? That makes sense to me if so, and then I think I'd rather the smaller coil. Our energy bills are not high with our 25 year old unit so increasing the efficiency isn't a giant priority for us.
-
08-21-2012, 12:10 PM #5
Professional Member*
- Join Date
- Aug 2007
- Location
- Northern VA 38 degrees N by 76 degrees W
- Posts
- 3,251
Ask them to do a Manual J load calculation, this will let you know what your homes latent load and sensible load is. From this the correct coil can be determined. There is no set combination that is right for your home without determining the type of load that needs to be dealt with.
Most contractors will attempt to sell you the highest SEER possible but if installed in the wrong application it will cost you more money to attempt to accomplish what is needed.
-
08-21-2012, 12:15 PM #6
Putting the 2 ton Trane on a 2 ton coil gives 23,000 BTUs. On a 2.5 ton coil (031) gives 23,000 BTUs. Ask him how that cools better? All it did is skew a few hundred BTU off latent (humidity removal) and move toward sensible. OK, he could say that cools better but could add a point or 2 to RH%.
Larger coil has more cooling area, means warmer coil which is why the larger coil drops humidity removal a hair.
-
08-21-2012, 12:56 PM #7
Regular Guest
- Join Date
- Aug 2012
- Posts
- 6
Ok, thanks so much. I don't see how the bigger coil would make sense for us. I think he oversized the furnace too. He didn't do any real load calculation, just kind of asked about our use and how things were with the units we had. He wrote up for the same size furnace as our current one, and the 2 guys who did measurements and spent a long time doing calculations on what we needed both came up with far lower outputs. I think we will pick between them. It seems like they were more by the book in terms of coming up with products for us.
-
08-21-2012, 06:42 PM #8
Professional Member*
- Join Date
- Dec 2010
- Location
- The Quad-Cities area (midwest).
- Posts
- 1,756
-
08-21-2012, 07:52 PM #9
Professional Member*
- Join Date
- Nov 2004
- Location
- SW FL
- Posts
- 5,260
Designer Dan
It's Not Rocket Science, But It is SCIENCE with "Some Art".

Define the Building Envelope and Perform a Detailed Load Calc: It's ALL About Windows and Make-up Air Requirements. Know Your Equipment Capabilities
-
08-21-2012, 08:35 PM #10
Professional Member*
- Join Date
- Jul 2006
- Location
- Virginia
- Posts
- 3,713
Is guy proposing the larger furnace and coil cheaper ?
-