Thread: JCI/Metasys System N2

  1. #21
    Join Date
    Apr 2006
    Location
    Columbus, Ohio
    Posts
    1,575
    Post Likes
    Thread Starter
    Quote Originally Posted by klrogers View Post
    Not if you have N2 devices, you have never told us exactly what devices you are connecting to.

    Kevin
    I will have that list tomorrow. I was tied up all day today on a job. I will let you know. Thanks alot.
    J. King

  2. #22
    Join Date
    May 2006
    Location
    Greater Atlanta Area
    Posts
    614
    Post Likes
    Once you determine what you need have the customer purchase the tools from JCI since they are the system owner (even if you fund it).

  3. #23
    Join Date
    Apr 2006
    Location
    Columbus, Ohio
    Posts
    1,575
    Post Likes
    Thread Starter
    I went out to the job site today and found that all of the vavs are on a n2 bus and have a VMA hardware type. The RTUs on this job reside on the LON network. They just use ccn to Lon cards for this. All of this is tied to a NAE55. So what software do I need to have to see the logic inside of the NAE55?

  4. #24
    Join Date
    Mar 2007
    Posts
    554
    Post Likes
    Quote Originally Posted by apprentice3 View Post
    So what software do I need to have to see the logic inside of the NAE55?
    Internet Explorer and Java.

  5. #25
    Join Date
    Mar 2007
    Posts
    554
    Post Likes
    Honestly if I were you, if it is working and you don't currently have any issues with the controls, I would just leave it alone until you have issues at this point.

  6. #26
    Join Date
    Apr 2006
    Location
    Columbus, Ohio
    Posts
    1,575
    Post Likes
    Thread Starter
    Quote Originally Posted by noskilltech View Post
    Honestly if I were you, if it is working and you don't currently have any issues with the controls, I would just leave it alone until you have issues at this point.
    The thing is they are having issues. Apparently this NAE55 is expected to control the Carrier Z series RTUs through LON. I need to see if there is any logic for certain control sequences that need to be done on these units. Apparently the 3 105 ton Carrier units feed into a common duct. They are having tons of trip outs when the units go unoccupied, and when the lead lag program takes affect. All of the units are controled internally to the maintain duct static pressure. Currently they are all referecing there built in duct static pressure sensor. All three of the sensors are reading different causing the fan speeds to be all over the place. Sometimes one unit will kick on and its fan will only ramp up to like 20 hz, and the unit doesn't have enough airflow for the 1st stage of cooling. Typically on these set ups I have seen the control system sync the fan speeds between the three units in the common ducted system. I need to get into this NAE55 for this reason. Is there a way that I can view the internal logic? I also want to see the logic that is writing the NVIs. Can this be done through internet explorer too? Or do you need some sort of software to see this part? I was on the system through internet explorer today, and I couldn't see anyway to access the internal programming.

    Thanks!
    J. King

  7. #27
    Join Date
    Mar 2007
    Posts
    554
    Post Likes
    All the programming in the NAE is viewed through internet exploded. I'm not exactly familiar with the Z series with the lon, but I would assume that all they are doing is reading data and commanding some setpoints. I would highly doubt with all the OEM equipment I've dealt with in the past that you will be able to control the VFD output once you do get into the NAE.

    I know in the past what I've done on your type of situation is use my own DP sensor and sent my own signal to the RTU controller. Your factory transducers will be your run of the mill "economically priced" transducer that we all can buy from Kele, ACI, etc. They should have a 4-20ma, 0-5vdc or 0-10vdc signal going back to the carrier control board. What I would do is take the factory transducer out of the unit, install it in your common duct work and run that to your own programmable controller. Then take 3 seperate AO's out of your controller back to the input on the RTU controller. You can program your controller or three controllers with logic so that all three units are getting the same exact static signal all the time. You'll have less labor doing that than beating your head against the wall trying to get the factory controller to do it.

  8. #28
    Join Date
    Apr 2006
    Location
    Columbus, Ohio
    Posts
    1,575
    Post Likes
    Thread Starter
    Quote Originally Posted by noskilltech View Post
    All the programming in the NAE is viewed through internet exploded. I'm not exactly familiar with the Z series with the lon, but I would assume that all they are doing is reading data and commanding some setpoints. I would highly doubt with all the OEM equipment I've dealt with in the past that you will be able to control the VFD output once you do get into the NAE.

    I know in the past what I've done on your type of situation is use my own DP sensor and sent my own signal to the RTU controller. Your factory transducers will be your run of the mill "economically priced" transducer that we all can buy from Kele, ACI, etc. They should have a 4-20ma, 0-5vdc or 0-10vdc signal going back to the carrier control board. What I would do is take the factory transducer out of the unit, install it in your common duct work and run that to your own programmable controller. Then take 3 seperate AO's out of your controller back to the input on the RTU controller. You can program your controller or three controllers with logic so that all three units are getting the same exact static signal all the time. You'll have less labor doing that than beating your head against the wall trying to get the factory controller to do it.
    Yeah I thought about doing something like that, but I just wanted to make sure that nothing was inside of the NAE that was doing this. There current JCI tech had told him that this sequence exists, but I cannot see anyway that they are currently even doing this. Maybe I will set up a Carrier controller to take control of some of these sequences if all the NAE is doing is monitoring and writing setpoints. If I wanted to log into the NAE through internet explorer would I just have to have the IP address of the controller, and the metasys user name and password?

    Thanks!
    J. King

  9. #29
    Join Date
    Nov 2005
    Location
    Shreveport, Louisiana
    Posts
    2,338
    Post Likes
    Go to Johnson Controls website In the search bar at the top right hand corner type in Product literature. In that type in or look for NAE Commisioning and or technical bulletin. This will go into more detail. Up front you need internet explorer. Also there is an IP address of the NAE.... You open IE(not firefox) Type in http://IP address/metasys or http://hostname/metasys The building staff can provide this. Also they can provide a user name and password. If you find the NAE commisioning guide you will find the factory password in it also. Again you will find lots of information in the product literature and with more information you can get further help on here. The first time you get on there go to the "help" tab at the top of the browser and find the metasys revision. It will be a number like 1.1 all the way up to 5.2.. It will prove helpful in the future. And look on the computer you are using onsite and see if the is a program called SCT, system configuration tool, It is used to do offline program and archiving of the NAE. And of you can get a back up of the NAE other here can help you further.
    UA Local 141

  10. #30
    Join Date
    Mar 2011
    Location
    Long Beach, CA
    Posts
    492
    Post Likes
    Are you sure that the 3 RTU's are feeding the same supply air duct. I guess this can be done but this is not that common. What kind of building is it. Is it office space, individual tenants, or open areas. How many floor does this building have?
    Have you verified actual duct static pressure with a magnehelic gauge, down stream of the duct work and also at the static pressure transducers. And if so what static pressure are you trying to maintain.

    Have you tried running the units in test mode or stand alone through the use of it own schedule. How about checking the the set up of the VFD whether it is set up as unit control or external control. Have you checked the ramp up time for the three VFD's.

  11. #31
    Join Date
    Apr 2006
    Location
    Columbus, Ohio
    Posts
    1,575
    Post Likes
    Thread Starter
    I will check into that information. Thanks a lot. As far as the SCT software goes the customer doesn't have that. Where can I get that at? Do I need that software to view all of the internal logic? Or can everything still be done in Internet explorer?

  12. #32
    Join Date
    Apr 2006
    Location
    Columbus, Ohio
    Posts
    1,575
    Post Likes
    Thread Starter
    Yes all 3 RTUs do feed into a common duct. Trust me I know that it is not typical. This is a office building with VAVs on the RTUs

  13. #33
    Join Date
    Apr 2006
    Location
    Columbus, Ohio
    Posts
    1,575
    Post Likes
    Thread Starter
    [QUOTE=alcomech;14046341]Are you sure that the 3 RTU's are feeding the same supply air duct. I guess this can be done but this is not that common. What kind of building is it. Is it office space, individual tenants, or open areas. How many floor does this building have?
    Have you verified actual duct static pressure with a magnehelic gauge, down stream of the duct work and also at the static pressure transducers. And if so what static pressure are you trying to maintain.

    The building has 6 floors. I have verified the actual duct pressure with a magnahelic. The static pressure they are trying to maintain is 1.5" w.c. Typically on these type of systems I have noticed that all of the units should reference the same static pressure pick up. At this building they are referencing the internal sensors to the unit. 2 of them a reading pretty close to the actual pressure in the duct. One of them is about 1.2 " w.c. low. I have already made recommendations to fix this problem.

    The ramp up time on the three VFDs is identical. The VFD is also currently being controlled internal to the unit as well.

    Thanks!
    J. King

  14. #34
    Join Date
    Mar 2011
    Location
    Long Beach, CA
    Posts
    492
    Post Likes
    Sounds like you are on to something here. Have you checked the maximum static pressure set point which will put the unit in alarm.
    And if so what is the set point.

    Also were is the static pressure transducer/ or velocity pick up located at. It should be located 2/3 down stream of the unit so that it will maintain true static to the last VAV's

  15. #35
    Join Date
    Mar 2011
    Location
    Long Beach, CA
    Posts
    492
    Post Likes
    I wonder if your actual static pressure set point is set too low at the Carrier control panel. At 1.5' W.C. there may not be enough pressure in the duct to the last and final 1st floor. Check the static at you last VAV to verify this. In addition you can get the required velocity set point by using the equal friction method

    In addition you will want to balance out a couple of the VMA VAV controllers so that you know what they are doing.
    You will need to use the VMA balancing tool through the use of HVAC Pro software or with the use of the VBT VAV balancing tool. If you have gotten into the front end it is possible to verify air flow and static there. But each VMA should have been balanced at start up along with its actual CFM out put and Pick-up gain/coefficient value

    Equal Friction Method:
    Area (Sq Ft.) = CFM divided by velocity FPM
    where as: area = 15000 CFM divided by 1500 FPM = 10 Sq
    10 Sq. Ft x 144 (Sq. Inches per Sq. Ft)/24" = 60"
    Therefore, select 60"x24" supply duct


    5400 CFM ÷ 1700 FPM velocity = 3.18 Sq Ft. Duct Area


    Aspect Ratio = 48/12= 4
    Aspect Ratio 4 = 144%
    Round duct = 66%
    Differance = 78%

    Velocity FPM = airflow CFM/ area in Ft Squared

    Velocity x Area = CFM

    To Figure CFM by known Sq Ft area and Static Pressure.

    External Static Pressure Method:
    This called total external static Pressure.
    A differential manamoter is used to measure the air pressure at the inlet and outlet of the blower assembly. This pressure is the same pressure a balloon has pushing against its internal walls. Air Blowers have the same type of pressure at the inlets and outlets. The measured air is compared to design charts provided by the equipment manufacture to determine how much air volume is flowing in cubic feet per minute. (CFM).

  16. #36
    Join Date
    Apr 2006
    Location
    Columbus, Ohio
    Posts
    1,575
    Post Likes
    Thread Starter
    Quote Originally Posted by alcomech View Post
    Sounds like you are on to something here. Have you checked the maximum static pressure set point which will put the unit in alarm.
    And if so what is the set point.

    Also were is the static pressure transducer/ or velocity pick up located at. It should be located 2/3 down stream of the unit so that it will maintain true static to the last VAV's
    The maximum static pressure setpoint that will put the unit into alarm is 3" w.c.

    The location of the static pressure pick ups are definitely problems. It is right off the discharge of each unit. So basically each unit has its own pick up. I know that this is definitely a problem. I told the customer yesterday about installing one pick up 2/3 down the duct and referencing that one value back up to all 3 units.
    J. King

  17. #37
    Join Date
    Apr 2006
    Location
    Columbus, Ohio
    Posts
    1,575
    Post Likes
    Thread Starter
    Quote Originally Posted by alcomech View Post
    I wonder if your actual static pressure set point is set too low at the Carrier control panel. At 1.5' W.C. there may not be enough pressure in the duct to the last and final 1st floor. Check the static at you last VAV to verify this. In addition you can get the required velocity set point by using the equal friction method

    In addition you will want to balance out a couple of the VMA VAV controllers so that you know what they are doing.
    You will need to use the VMA balancing tool through the use of HVAC Pro software or with the use of the VBT VAV balancing tool. If you have gotten into the front end it is possible to verify air flow and static there. But each VMA should have been balanced at start up along with its actual CFM out put and Pick-up gain/coefficient value

    Equal Friction Method:
    Area (Sq Ft.) = CFM divided by velocity FPM
    where as: area = 15000 CFM divided by 1500 FPM = 10 Sq
    10 Sq. Ft x 144 (Sq. Inches per Sq. Ft)/24" = 60"
    Therefore, select 60"x24" supply duct


    5400 CFM ÷ 1700 FPM velocity = 3.18 Sq Ft. Duct Area


    Aspect Ratio = 48/12= 4
    Aspect Ratio 4 = 144%
    Round duct = 66%
    Differance = 78%

    Velocity FPM = airflow CFM/ area in Ft Squared

    Velocity x Area = CFM

    To Figure CFM by known Sq Ft area and Static Pressure.

    External Static Pressure Method:
    This called total external static Pressure.
    A differential manamoter is used to measure the air pressure at the inlet and outlet of the blower assembly. This pressure is the same pressure a balloon has pushing against its internal walls. Air Blowers have the same type of pressure at the inlets and outlets. The measured air is compared to design charts provided by the equipment manufacture to determine how much air volume is flowing in cubic feet per minute. (CFM).
    Wow this is a lot of information. Thanks for all of you help. Next week I will get into the VAVs and review some of there setpoints. I was also looking into this SCT software on JCIs website. Is that software absolutely necessary to view the logic? Would JCI typically leave that on the end users main computer?
    J. King

  18. #38
    Join Date
    Jan 2012
    Location
    Ohio
    Posts
    29
    Post Likes
    Quote Originally Posted by apprentice3 View Post
    I have more of a service controls background. I have worked on a lot of different systems out there. I have only done some mild programming. I usually catch on pretty quick once I get going though. So I think some sort of training would be good. I have thought about upgrading this system to a Tridium system. My company hasn't got into Tridium yet, but I have been on them for a few years now letting them know how big of a player Tridium is in the controls market. They are strongly considering sending a few of there programmers, and myself to AX training. I agree this would definitely be the best solution to the problem. On this job there is some pretty custom logic that the JCI system doesn't contain that I would have to put into the Tridium. Do they have a lot of different programming blocks for most applications?
    apprentice3... if you want some assistance, please send me a private message. I am in the Columbus, OH area and can help you with whatever you need... figuring out what you have, where you need to go, accessing your current site, etc...



    Tommy C...

  19. #39
    Join Date
    Jul 2008
    Location
    Melbourne
    Posts
    1,611
    Post Likes
    http://IP address/sct or http://hostname/sct
    u:metasyssysagent
    p:XMG3-Rel.1
    http://cgproducts.johnsoncontrols.co...DF/1201519.PDF

    and if he stuffs it up then somebody from JCI will get a call
    ...and if he doesnt then ... well, thats the way it should be.
    1 + 1 = 3 ( *** for very large values of 1)

    ...everybody wants a box of chocolates and long stemmed rose

    Be brave. You cannot get eaten by an imaginary tiger.

  20. #40
    Join Date
    Jun 2012
    Location
    Tampa
    Posts
    1
    Post Likes

    Cool The Last Resort.

    Quote Originally Posted by Cagey57 View Post
    OP,
    This assumes you will find "Legacy N2" devices; AHU's, VMA's, VAV's, UNT and DX-9100's at the job.

    The S4 gizmo is trick, the S2 Converter is pretty slick but I already had the B&B 485SD9TB that connect to a 9pin serial port otherwise I would have bought the S2 box. If you do not have a serial port get the B&B converter and a Digi Edgeport/1 to adapt it to a USB port. Least brain damage in the long run.

    The software is MW-MTOOL-0 for a new copy (with the CBT) or for about 1/2 the price you should order the MW-MTOOL-6 (no CBT). The AS-CVTPRO300-1 is very pricey. I recommend one of the 2 converters (S2 or the B&B Electroincs) mentioned above. Your best bet will be to locate your local independant Johnson Controls ABCS dealer to order/purchase the M-Tools Software.

    You mentioned "Custom Programming", if it's NOT an NAE you will have to decifer the N30 logic or, if its NCM/PMI you will have to get either the JCB source files or the GPL files. Hopefully off of the existing Workstation.

    As mentioned above the FX-60/70 is likely your best solution if you don't have a long term plan.

    Good Luck.


    You purchase the sioftware and hire an ex-jci tech to train you.

+ Reply to Thread
Page 2 of 3 FirstFirst 123 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •