08-19-2012, 09:59 AM #1
Regular Guest
- Join Date
- Aug 2012
- Location
- Katy, TX
- Posts
- 45
LENNOX 3-ton marginal delta between return & register temps
I have a 5-yr old 1,600 s.f. (single story) townhome in Houston, built in 07. The builder-grade LENNOX A/C is a 3-ton unit that until recently had been working fine (conventional box/A-Coil w/TXV, not a slab). (R410A) A couple weeks ago we noticed it not cooling well & unable to achieve 75-degree set point (wife going through 'the change' so greenies pls don't lecture me). Before doing anything I checked the return air (80 deg) and register temp (72 deg) nearest the plenum. Outside temp 95. Obviously something wrong. Amprobe showing 9A which seemed about normal, perhaps a little low, data plate shows RLA is 14A.
We called the same co. we've used & trusted for years tho they's recently changed ownership. (they also come every spring and fall for seasonal inspection, media filter changes, etc). The tech says low refrigerant, performs leak check but initially finds nothing, later discovers small leak at needle valve where manifold gauges attach. He evacuates the system & replaces an o-ring seal, pumps it down & recharges, adding 2 lbs of coolant. However, only minimal improvement. 80 deg return, 68 at register. Tech says should be at least 15 deg w/18~20 optimum. (Amprobe now showing 12A). System pressure showing 400 psi high side and 140 low side (indoor temp 76). Tech trying to talk me into replacing the TXV with a piston. I think I'm ready for a second opinion. Thanks.
-
08-19-2012, 10:31 AM #2
Possible slight restriction before metering device?TXV. Did he change the liquid line filter drier when he fixed the leak.
-
08-19-2012, 10:46 AM #3
Regular Guest
- Join Date
- Aug 2012
- Location
- Katy, TX
- Posts
- 45
No, and I did ask. He said the drier was fine, tho dunno how he determined that. I'm a retired commercial broadcast engr, & former industrial electrician (John Deere) so I know just enuf about A/C to keep my hands in my pocket and watch.
The high side pressure seems awfully high to me tho and I'm not happy to see the substantial current increase. How likely is it that a TXV might go bad? If it does crap out would it be better to replace it with another TXV or put in a piston instead? Tech said if he put in a piston that I'd also need a hard-start kit.
-
08-19-2012, 10:48 AM #4
Okay, the mfg'ers data on a Goodman 13-SEER, 3-Ton, R-410A, 95-F ambient, 80F indoors:
At a high 1351-CFM of airflow; @67F Wet Bulb or around 50% indoor RH, temp-split is 18F; @71F WB or, 64% RH split is 15F.
At 1200-CFM 67-WB, split is 19F; @71F WB, or, 64% RH split is 15F.
Of course that 8-F indoor airflow temp-split is unacceptable.
Well, that is a 12-F split which might not be too far off if there was a very high indoor humidity; you have to know the indoor humidity & should also know the approximate airflow CFM.We called the same co. we've used & trusted for years tho they's recently changed ownership. (they also come every spring and fall for seasonal inspection, media filter changes, etc). The tech says low refrigerant, performs leak check but initially finds nothing, later discovers small leak at needle valve where manifold gauges attach. He evacuates the system & replaces an o-ring seal, pumps it down & recharges, adding 2 lbs of coolant. However, only minimal improvement. 80 deg return, 68 at register. Tech says should be at least 15 deg w/18~20 optimum. (Amprobe now showing 12A). System pressure showing 400 psi high side and 140 low side (indoor temp 76). Tech trying to talk me into replacing the TXV with a piston. I think I'm ready for a second opinion. Thanks.
A 400-psig is 117-F condenser discharge, @ 95F ambient, that is a fairly high 22F condenser temp-split; which could mean a high indoor humidity or drawing hot air into the Return-Air from somewhere, plus other causes...
Do NOT replace that TXV; he is missing some other important factors!Last edited by udarrell; 08-19-2012 at 11:03 AM. Reason: Left outother factors...
AOP Forum Rules:
Rules for Posting
Rules For Equipment Owners
Equipment Owners Find a Contractor HERE!
udarrell
-
08-19-2012, 11:03 AM #5“I am glad that I paid so little attention to good advice; had I abided by it I might have been saved from some of my most valuable mistakes.” - Edna St. Vincent Millay
The critic is a prisoner to his own experiences and perspectives, erroneously believing his limited experiences are the sum of all truth.
No Guns…No Freedom…Know Guns…Know Freedom.
-
08-19-2012, 11:07 AM #6“I am glad that I paid so little attention to good advice; had I abided by it I might have been saved from some of my most valuable mistakes.” - Edna St. Vincent Millay
The critic is a prisoner to his own experiences and perspectives, erroneously believing his limited experiences are the sum of all truth.
No Guns…No Freedom…Know Guns…Know Freedom.
-
08-19-2012, 11:08 AM #7
Regular Guest
- Join Date
- Aug 2012
- Location
- Katy, TX
- Posts
- 45
Thanks. That's something else he mentioned, possibly slowing down the blower but I nixed that idea because of the wife's hormone issues in my original post. I understand the fan speed logic, but it's worked fine for 4½ yrs so I'm reluctant to allow someone to alter the mfr's original design (swap TXV for piston). I also don't want to pay out the wazoo for someone to shotgun the system without knowing what the problem is. In this area there's no shortage of Bozos with a license but not a lot of experience. There's also 3 mo. remaining on the mfr. warranty, so maybe time to call someone else.
-
08-19-2012, 11:13 AM #8“I am glad that I paid so little attention to good advice; had I abided by it I might have been saved from some of my most valuable mistakes.” - Edna St. Vincent Millay
The critic is a prisoner to his own experiences and perspectives, erroneously believing his limited experiences are the sum of all truth.
No Guns…No Freedom…Know Guns…Know Freedom.
-
08-19-2012, 11:18 AM #9
Regular Guest
- Join Date
- Aug 2012
- Location
- Katy, TX
- Posts
- 45
I was not there at the time. He told me he pumped the system down to place a vacuum on the line, coil, etc. supposedly as part of his leak check, and held the vacuum for 30 mins w/no loss, eliminating suspicion of the coil. No obvious oil showing up anywhere.
The system also has an outside "fresh air" return but is electronically damper-controlled. I was there at the time he inspected the fresh-air damper. It was closed. Apparently the T-stat controls it, though I don't know under what circumstances it calls for fresh air. This fresh air thing was one of the "selling points" of the home, stating that it helped hold a positive air pressure and would thus help eliminate dust. ANyway it is closed and temporarily disconnected at the wire nut to ensure it stays closed.
There are two inside returns, a 20" line coming from a 20x30 return in the hallway (below the stat) and a 12" line coming from a 12 x 12 return in the ceiling of the MBR. Coincdentally the MBR is the farthest run but is historically the coldest room in the house.
-
08-19-2012, 11:26 AM #10“I am glad that I paid so little attention to good advice; had I abided by it I might have been saved from some of my most valuable mistakes.” - Edna St. Vincent Millay
The critic is a prisoner to his own experiences and perspectives, erroneously believing his limited experiences are the sum of all truth.
No Guns…No Freedom…Know Guns…Know Freedom.
-
08-19-2012, 11:27 AM #11
Regular Guest
- Join Date
- Aug 2012
- Location
- Katy, TX
- Posts
- 45
You may have hit on something here... We recently had an alarm guy in the attic adding glass-break sensors in 2 bedroom ceilings. I just wonder what the chances are he might have accidentally gotten tangled up in a return air line? I guess an easy way to check that would be to see if we have good suction at both return air registers (MBR ceiling and hallway)
-
08-19-2012, 11:28 AM #12
Professional Member*
- Join Date
- Dec 2005
- Posts
- 1,655
But the tech came out is not knowledgeable enough. Get another tech please.
You seem to have more common sense than the tech who recommend replacing the TXV with piston. It worked for 4.5 years AND IF it fail, then replace it. Don't just swap it out just because of "uncertainty" or "guessing".
-
08-19-2012, 11:31 AM #13“I am glad that I paid so little attention to good advice; had I abided by it I might have been saved from some of my most valuable mistakes.” - Edna St. Vincent Millay
The critic is a prisoner to his own experiences and perspectives, erroneously believing his limited experiences are the sum of all truth.
No Guns…No Freedom…Know Guns…Know Freedom.


Reply With Quote
I wonder why he did not just use an electronic leak detector like most do.